On 7/6/13 2:39 PM, Mark C. Stephens wrote:
How Does that Work Robert?
I mean why out of phase?

Then the voltage on the secondary of the buck transformer is subtracted from the line voltage.

This is a very common thing commercially where you have what's called a "buck/boost" transformer to adjust the line voltage. Typically to boost it at the end of a long run where resistive drops make the voltage too low.

The low voltage secondary must be big enough to carry the entire load current, of course.



-----Original Message-----
From: time-nuts-boun...@febo.com [mailto:time-nuts-boun...@febo.com] On Behalf 
Of Robert Atkinson
Sent: Sunday, 7 July 2013 12:57 AM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] HP 5370B dropping mains voltage

Hi Marki,

Dropping the mains voltage is easy. Get a mains to low voltage transformer. 
Connect the primary across the mains and the secondary in series opposition 
(out of phase) with the mains supply. Foar example a 100VA 12V transformer will 
drop your mains to just under 238V with a maximum load of 8A (the current 
rating of the secondary).


HTH,
Robert G8RPI.


_______________________________________________
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Reply via email to