The reason that DC is used commercially to measure resistance is simple, if you 
use AC you may well get the reactive component as well as the resistance coming 
into play.

Such low resistance measurements commercially are normally only made on high 
current power distribution networks as part of a periodic test regime where you 
need to determine the quality/resistance of such things as bus bar 
joints/connections and loop resistance.

It is not a good idea to use copperslip around aluminium, there is an aluminium 
based version that should be used, but, be warned, just like copperslip it is 
an insulator, try putting your meter probes, set for resistance, into a tub of 
both, I have.  I do not know just why but the aluminium version is just like 
sand, it gets everywhere when you use it.

To check your joint I would use a four wire Kelvin set up using say 10 Amps 
from my constant current bench supply and then use my Keithly 616 digital  
electrometer to measure the voltage/s present across the joint, a simple 
application of Ohms law will then give the resistance.