On 04/24/2006 05:26 AM, Carlos Rodrigues wrote:
On 4/24/06, Peter Selinger <[EMAIL PROTECTED]> wrote:
Yes, here it is in the logs:
UPS status: 230.6 190.0 221.3 000 49.9 2.29 37.1 00000000
The voltage is reported as 2.29. Would be nice if the driver could
report the voltage at the same resolution. -- Peter
Done. The protocol actually says the voltage may have two decimals,
I've missed that part...
@lonely wolf: can you try now?
--
Carlos Rodrigues
Here we are, gentlemen:
[EMAIL PROTECTED] nut]# upsc [EMAIL PROTECTED]
battery.charge: 100.0
battery.voltage: 2.29
battery.voltage.nominal: 96.0
driver.name: megatec
driver.parameter.port: /dev/ttyS0
driver.version: 2.1.0
driver.version.internal: 1.4
input.frequency: 50.0
input.voltage: 232.4
input.voltage.fault: 190.0
input.voltage.maximum: 232.4
input.voltage.minimum: 232.4
output.voltage: 221.3
output.voltage.nominal: 220.0
ups.delay.shutdown: 2
ups.delay.start: 3
ups.load: 0.0
ups.mfr: Ablerex
ups.model: MS3000RT MS02035C
ups.serial: unknown
ups.status: OL
ups.temperature: 35.9
Excellent job. Thank you !
I have uploaded all updated info on my web site
(http://wdl.lug.ro/ablerex), in case anybody needs them.
Secondary question: as you can see at
http://wdl.lug.ro/ablerex/upsilon.status.screen (and
http://wdl.lug.ro/ablerex/upsilon.config.screen ), upsilon reports:
ACfail Shutdown Delay: 1440 Min
UPS Turn Off Delay : 10.0 Min
1440 min = a 24h (maximum allowed value) delay I have setup when
discharging the UPS, so that I can test nut while being sure upsilon
will not shutdown the computer used for tests.
Shouldn't these values be seen somewhere in upsc output ? How are they
related to "ups.delay.shutdown: 2" and "ups.delay.start: 3" ?
manuel
--
Manuel Wolfshant linux registered user #131416
IT manager NoBug Consulting Romania
http://www.brainbench.com/transcript.jsp?pid=40317
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser