An electrician would consider two GFCI’s in series unprofessional.  It does not 
provide any more protection, and in the even one of them trips, it is likely to 
cause confusion.

That said, there are DIN rail mount GFCI modules with no outlet just the test 
and reset buttons, you could wire one ahead of the terminal block in the L-Com 
enclosure.  Phoenix Contact makes them, I saw them at Allied for over $100.  I 
assume you don’t want to pay that.


From: Josh Luthman 
Sent: Friday, May 22, 2015 4:46 PM
To: af@afmug.com 
Subject: Re: [AFMUG] NEMA enclosure with GFCI outlet

Right the outlets.  Not inside the enclosure (at least mine).

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On May 22, 2015 5:43 PM, "Jaime Solorza" <losguyswirel...@gmail.com> wrote:

  All outlets here at well sites are GFCI period.    So u get used to it.  

  Jaime Solorza

  On May 22, 2015 2:36 PM, "George Skorup" <geo...@cbcast.com> wrote:

    NEC says you need one GFI device on a circuit. So tell them two is not 
code? :)


    On 5/22/2015 3:11 PM, Josh Luthman wrote:

      I'm using that enclosure now.  Need to dremel room for a GFCI. 

      I hate them as well.  They're doing a breaker, GFCI and that will go to 
the GFCI in the box.  That's what they want, so that's what I'm charging for.


      Josh Luthman
      Office: 937-552-2340
      Direct: 937-552-2343
      1100 Wayne St
      Suite 1337
      Troy, OH 45373

      On Fri, May 22, 2015 at 3:37 PM, Josh Reynolds <j...@spitwspots.com> 
wrote:

        
http://www.l-com.com/productfinder/finderresults.aspx?ftype=ENCLOSURES&finderid=5&steps=14x12x7+Inch%7c120+VAC%7cNone

        Find one you can adapt, swap the outlet for a GFCI.

Josh Reynolds
CIO, SPITwSPOTS
www.spitwspots.comOn 05/22/2015 11:33 AM, Josh Luthman wrote:

          Gotta have both (customer requirement).


          Josh Luthman
          Office: 937-552-2340
          Direct: 937-552-2343
          1100 Wayne St
          Suite 1337
          Troy, OH 45373

          On Fri, May 22, 2015 at 3:32 PM, Adam Moffett <dmmoff...@gmail.com> 
wrote:

            You could wire your box to the load side of a separate outdoor 
GFCI.  Then the GFCI can also act as a convenience outlet and disconnect 
switch.  Just a thought. 


            On 5/22/2015 3:29 PM, Josh Luthman wrote:

              Does such a thing exist?  My current plan is to take a small box 
with a normal outlet and replace it, but that requires a bit of dremel work and 