On Tue, Mar 5, 2013 at 2:17 AM, Samir Idris <[email protected]> wrote:

> Eric,
>
> Thanks for that.  Yeah found that :)
>
> How do I join ccie_dc group?  Just email there?
>
> Regards,
> Samir.
>
> On Tue, Mar 5, 2013 at 6:11 PM, Eric Day <[email protected]> wrote:
>
>>  Samir,  (for the record there is also a CCIE DC online list - 
>> [email protected]
>> )
>>
>> They are always redundant, and to my knowledge there is not a way to
>> change that.  Since the maximum capacity is fairly limited, it is easy to
>> project the largest power consumed configuration and plan for such.  Cisco
>> I believe has done just that, for the 5548's they used 750w power supplies
>> with 1:1 redundancy and for the 5596's used 1100w.  Output below, and you
>> can see if one more 16port module was added only an additional 90w would be
>> needed and chassis would be at capacity for modules with room still for a
>> failure of a power supply:
>>
>> xxxxxx-n5k-a# show env power
>>
>>
>> Power Supply:
>> Voltage: 12 Volts
>> ------------------------------
>> -----------------------------
>> PS  Model                Input Power       Power     Status
>>                          Type  (Watts)     (Amp)
>> -----------------------------------------------------------
>> 1   N55-PAC-1100W        AC    1050.00     87.50     ok
>> 2   N55-PAC-1100W        AC    1050.00     87.50     ok
>>
>>
>> Mod Model                   Power     Power       Power     Power
>> Status
>>                             Requested Requested   Allocated
>> Allocated
>>                             (Watts)   (Amp)       (Watts)
>> (Amp)
>> --- ----------------------  -------   ----------  --------- ----------
>> ----------
>> 1    N5K-C5596UP-SUP        648.00    54.00       648.00    54.00
>> powered-up
>> 2    N55-M160L3-V2          110.40    9.20        110.40    9.20
>> powered-up
>> 3    N55-M16UP              90.00     7.50        90.00     7.50
>> powered-up
>>
>>
>> Power Usage Summary:
>> --------------------
>> Power Supply redundancy mode:                 Redundant
>> Power Supply redundancy operational mode:     Redundant
>>
>> Total Power Capacity                             2100.00 W
>>
>> Power reserved for Supervisor(s)                  648.00 W
>> Power currently used by Modules                   200.40 W
>>
>>                                                 -------------
>> Total Power Available                            1251.60 W
>>                                                 -------------
>>
>>
>>  On Tue, Mar 5, 2013 at 1:03 AM, Samir Idris <[email protected]>wrote:
>>
>>>  Hello,
>>>
>>> Are the power supplies on a 5548 active-active?  how do we check that?
>>>
>>> Regards,
>>> --
>>> Samir Idris
>>>
>>> _______________________________________________
>>> For more information regarding industry leading CCIE Lab training,
>>> please visit www.ipexpert.com
>>>
>>> Are you a CCNP or CCIE and looking for a job? Check out
>>> www.PlatinumPlacement.com <http://www.platinumplacement.com/>
>>>
>>> http://onlinestudylist.com/mailman/listinfo/ccie_rs
>>>
>>
>>
>>
>> --
>> Eric Day
>> [email protected]
>>
>
>
>
> --
> Samir Idris




-- 
Eric Day
[email protected]
_______________________________________________
For more information regarding industry leading CCIE Lab training, please visit 
www.ipexpert.com

Are you a CCNP or CCIE and looking for a job? Check out 
www.PlatinumPlacement.com

http://onlinestudylist.com/mailman/listinfo/ccie_rs

Reply via email to