thanks :)

On Tue, Mar 5, 2013 at 6:21 PM, Eric Day <[email protected]> wrote:

> http://onlinestudylist.com/mailman/listinfo/ccie_dc
>
>
> On Tue, Mar 5, 2013 at 2:17 AM, Samir Idris <[email protected]> wrote:
>
>> Eric,
>>
>> Thanks for that.  Yeah found that :)
>>
>> How do I join ccie_dc group?  Just email there?
>>
>> Regards,
>> Samir.
>>
>> On Tue, Mar 5, 2013 at 6:11 PM, Eric Day <[email protected]> wrote:
>>
>>>  Samir,  (for the record there is also a CCIE DC online list - 
>>> [email protected]
>>> )
>>>
>>> They are always redundant, and to my knowledge there is not a way to
>>> change that.  Since the maximum capacity is fairly limited, it is easy to
>>> project the largest power consumed configuration and plan for such.  Cisco
>>> I believe has done just that, for the 5548's they used 750w power supplies
>>> with 1:1 redundancy and for the 5596's used 1100w.  Output below, and you
>>> can see if one more 16port module was added only an additional 90w would be
>>> needed and chassis would be at capacity for modules with room still for a
>>> failure of a power supply:
>>>
>>> xxxxxx-n5k-a# show env power
>>>
>>>
>>> Power Supply:
>>> Voltage: 12 Volts
>>> ------------------------------
>>> -----------------------------
>>> PS  Model                Input Power       Power     Status
>>>                          Type  (Watts)     (Amp)
>>> -----------------------------------------------------------
>>> 1   N55-PAC-1100W        AC    1050.00     87.50     ok
>>> 2   N55-PAC-1100W        AC    1050.00     87.50     ok
>>>
>>>
>>> Mod Model                   Power     Power       Power     Power
>>> Status
>>>                             Requested Requested   Allocated
>>> Allocated
>>>                             (Watts)   (Amp)       (Watts)
>>> (Amp)
>>> --- ----------------------  -------   ----------  --------- ----------
>>> ----------
>>> 1    N5K-C5596UP-SUP        648.00    54.00       648.00    54.00
>>> powered-up
>>> 2    N55-M160L3-V2          110.40    9.20        110.40    9.20
>>> powered-up
>>> 3    N55-M16UP              90.00     7.50        90.00     7.50
>>> powered-up
>>>
>>>
>>> Power Usage Summary:
>>> --------------------
>>> Power Supply redundancy mode:                 Redundant
>>> Power Supply redundancy operational mode:     Redundant
>>>
>>> Total Power Capacity                             2100.00 W
>>>
>>> Power reserved for Supervisor(s)                  648.00 W
>>> Power currently used by Modules                   200.40 W
>>>
>>>                                                 -------------
>>> Total Power Available                            1251.60 W
>>>                                                 -------------
>>>
>>>
>>>  On Tue, Mar 5, 2013 at 1:03 AM, Samir Idris <[email protected]>wrote:
>>>
>>>>  Hello,
>>>>
>>>> Are the power supplies on a 5548 active-active?  how do we check that?
>>>>
>>>> Regards,
>>>> --
>>>> Samir Idris
>>>>
>>>> _______________________________________________
>>>> For more information regarding industry leading CCIE Lab training,
>>>> please visit www.ipexpert.com
>>>>
>>>> Are you a CCNP or CCIE and looking for a job? Check out
>>>> www.PlatinumPlacement.com <http://www.platinumplacement.com/>
>>>>
>>>> http://onlinestudylist.com/mailman/listinfo/ccie_rs
>>>>
>>>
>>>
>>>
>>> --
>>> Eric Day
>>> [email protected]
>>>
>>
>>
>>
>> --
>> Samir Idris
>
>
>
>
> --
> Eric Day
> [email protected]
>



-- 
Samir Idris