> On Jul 17, 2025, at 10:41 AM, Jon Elson via cctalk <[email protected]> 
> wrote:
> 
> On 7/17/25 08:45, Paul Koning via cctalk wrote:
>> 
>>> On Jul 16, 2025, at 3:42 PM, Van Snyder via cctalk <[email protected]> 
>>> wrote:
>>> 
>>>> ...
>>> The Computer History Museum in Sunnyvale, CA has a working IBM 1401
>>> computer from Germany. It has ferroresonant power supplies. They bought
>>> a converter to supply 50 Hz power because they were certain it wouldn't
>>> work at 60 Hz. And it has motors in the card reader, card punch,
>>> printer, and tape drives, that would all run at the wrong speed using
>>> 60 Hz power.
>> I wonder about "they were certain it would not work".  That should be a 
>> question of fact, not belief.
>> 
>> As for the motors, that's an obvious issue (if they are induction motors 
>> rather than universal motors).  The modern solution is a VFC -- variable 
>> frequency motor controller.  Those are pretty cheap and work great with 
>> motors.  I've heard that they are not so good with power supply 
>> transformers, not sure if that has been experimentally confirmed.  For power 
>> supply transformers, 50 vs. 60 Hz is unlikely to matter.  People with CDC 
>> mainframes that want 400 Hz power do need a solution, with motor-generators 
>> as the traditional answer.  I wonder if a VFC would work for that, perhaps 
>> with post-VFC filtering to turn the waveform into something closer to a sine 
>> wave.
>> 
>> 
> 
> VFDs (variable frequency drives) produce ~340 V PWM "square" waves,  Given 
> enough inductance in the motor windings, this causes roughly sinusoidal 
> currents.  But, feed this into a transformer, and you will get high frequency 
> spikes.  Now, MAYBE, due to the way a "Sola" transformer works, it might 
> smooth out the square waves, but it is real hard to predict what will happen. 
>  Also, VFDs are usually designed for balanced 3-phase loads.

Yes, the question is whether the transformer could be made sufficiently happy.  
As for 3-phase: the CDC mainframes (6000 series) in fact use 3 phase 400 Hz 
power feeding their power supplies -- you're dealing with 3-phase transformers 
and 6-diode rectifiers behind them.

        paul


Reply via email to