Hi Etienne,

I think you can solve your problem in two ways. 
In all you need to pass down the length of the packet in total from the root 
type (which knows the length).
1) You keep on just reading bytes and parse in the protocol logic class (Like 
in the S7 driver or KNX)
2) You directly parse PlcValues (using "dataIo" types) 

I would prefer option 2 but 1 is simpler. The reason I'm doing 1) in S7 and KNX 
is that I need to know the type from the request to decode in the S7 case and 
in the KNX case I need to know the type from an external source in order to 
decode it.


Chris

Am 13.03.20, 14:45 schrieb "Etienne Robinet" <[email protected]>:

    Yes this is exactly what I need. If I get the remaining bytes, I can know 
the element numbers as I have their type!
    
    Etienne
    
    On 2020/03/13 13:40:09, Julian Feinauer <[email protected]> 
wrote: 
    > Hey,
    > 
    > there ist he possibility to get the remaining size oft he bytes of the 
message. Does that help?
    > Otherwise I misread your question.
    > 
    > Julian
    > 
    > Am 13.03.20, 14:37 schrieb "Etienne Robinet" <[email protected]>:
    > 
    >     Hi Julian,
    >     so how should I declare this field in the mspec if I can not get its 
size?
    >     Thank you,
    >     
    >     Etienne
    >     
    >     On 2020/03/13 13:35:52, Julian Feinauer 
<[email protected]> wrote: 
    >     > Hi Etienne,
    >     > 
    >     > first, Congratulations on your Progress!
    >     > To you question:
    >     > This is a common issue with many protocols.
    >     > We solve that in the protocol layer by keeping the request until we 
get the response (see for Example how we did it for S7).
    >     > So you cannot solve that in mpsec at compile time but have to 
decode the byte[] you get with the Information from the Request.
    >     > 
    >     > Hope that helps!
    >     > Julian
    >     > 
    >     > Am 13.03.20, 14:02 schrieb "Etienne Robinet" <[email protected]>:
    >     > 
    >     >     Hi Chris,
    >     >     I have yet another question. When sending a request for 
multiple elements (let's say 10 elements of an array), you get a response from 
the PLC with all the data at the end of the packet. The problem is, in the 
request there is the number of elements we want, but not in the response. So so 
the protocol knows how many elements there are in the response packet, but not 
the packet itself. This is quite a problem as for the parse, we need to know 
the length of the 'data' array containing the response data (for now it was 
only depending on the type, but I would need type*elements).
    >     >     
    >     >     I tested a bit by modifying the generated IO, and 1 way to do 
it is to get the remaining bytes and divide this by the datatype size. I just 
wanted to ask if someone would know how to declare this in the mspec, as I 
don't want to touch at the template. I also thought about having an attribute 
on the response, but I don't know how to put an attribute that won't get 
parsed/serialized. Hope I am clear enough, but this is  a code sample that 
worked (modifying generated sources):
    >     >     https://i.imgur.com/Xm6DxEZ.png (notice the error but this code 
works if I write it myself)
    >     >     And here is how I put it in the mspec: 
https://i.imgur.com/Ye1Kl9q.png (you can see the number of element is not 
present)
    >     >     
    >     >     Any help is welcome of course! :)
    >     >     Etienne
    >     >     
    >     >     
    >     >     
    >     >     
    >     >     
    >     >     On 2020/03/12 21:34:12, Christofer Dutz 
<[email protected]> wrote: 
    >     >     > Hi Etienne,
    >     >     > 
    >     >     > that's amazing news :-) ... congratulations :-)
    >     >     > 
    >     >     > Also had a look at your mspec and I think you have done a 
great job with that. I wasn't quite sure about the relation between CipRRData 
and CipExchange, but your solution looks rock-solid.
    >     >     > 
    >     >     > And now reading that you even managed to get something 
working, that makes me very happy.
    >     >     > 
    >     >     > Tomorrow I'll be a little consumed with signing the contract 
with the KNX foundation but I'll try to have a look at your fork.
    >     >     > 
    >     >     > Thanks for your great work :)
    >     >     > 
    >     >     > Chris
    >     >     > 
    >     >     > 
    >     >     > 
    >     >     > Am 12.03.20, 17:50 schrieb "Etienne Robinet" 
<[email protected]>:
    >     >     > 
    >     >     >     Hi all,
    >     >     >     again a productive day, I pushed to my branch and the 
driver support reading, multiple reading and the camel component works (in 
karaf) and takes a List of strings. Tested it on a different PLC and it also 
worked! Next I'm going to implement the array readings and then maybe writing 
(tests needs to be done too).
    >     >     >     
    >     >     >     Etienne
    >     >     >     
    >     >     >     On 2020/03/12 07:18:32, Etienne Robinet 
<[email protected]> wrote: 
    >     >     >     > Hi Chris,
    >     >     >     > yes that's what I thought so I managed to work around 
like this: 
    >     >     >     > 
    >     >     >     > 
https://github.com/etiennerobinet/plc4x/blob/eip/protocols/eip/src/main/resources/protocols/eip/eip.mspec
    >     >     >     > 
    >     >     >     > And this works for reading! I managed to make a quick 
test and read via the tag name. Now my question is: can I create sub-types that 
are also discriminated with sub-subtypes? That would allow to create the 
ReadRequest only, as the fields before are mainly constant/implicit.
    >     >     >     > Etienne
    >     >     >     > 
    >     >     >     > On 2020/03/11 20:24:14, Christofer Dutz 
<[email protected]> wrote: 
    >     >     >     > > Hi Etienne,
    >     >     >     > > 
    >     >     >     > > you are defining the type CipRRData twice ... once as 
one of the sub-types of EipPacket and once as a dedicated discriminated type.
    >     >     >     > > 
    >     >     >     > > Chris
    >     >     >     > > 
    >     >     >     > > 
    >     >     >     > > PS: I have no idea why I didn't finish writing this 
email and I just noticed when closing everything down ... sorry for the late 
reply.
    >     >     >     > > 
    >     >     >     > > 
    >     >     >     > > 
    >     >     >     > > Am 11.03.20, 09:30 schrieb "Etienne Robinet" 
<[email protected]>:
    >     >     >     > > 
    >     >     >     > >     Hi all,
    >     >     >     > >     
    >     >     >     > >     I have a quick question. I've been working on the 
CIP encapsulation but hitting a problem with the mspec design. Here is the 
error I am facing: https://i.imgur.com/iCfh59n.png
    >     >     >     > >     
    >     >     >     > >     The problem here is that this CipRRData should 
also be of type EipPacket. When the command of an EipPacket is '0x66' this 
means SendRRData (for Read/Write and Request/Response so I have to discriminate 
it on the sub level). The problem is that after generation, CipRRData 
implements Message but does not extend EipPacket. How should I do it? Here is 
the mspec:
    >     >     >     > >     
    >     >     >     > >     [discriminatedType 'EipPacket'
    >     >     >     > >         [discriminator uint 16 'command']
    >     >     >     > >         [implicit      uint 16 'len' 'lengthInBytes - 
24']
    >     >     >     > >         [simple        uint 32 'sessionHandle']
    >     >     >     > >         [simple        uint 32 'status']
    >     >     >     > >         [array         uint 8  'senderContext' count 
'8']
    >     >     >     > >         [simple        uint 32 'options']
    >     >     >     > >         [typeSwitch 'command'
    >     >     >     > >                 ['0x0065' EipConnectionRequest
    >     >     >     > >                     [const  uint    16   
'protocolVersion'   '0x01']
    >     >     >     > >                     [const  uint    16   'flags'      
       '0x00']
    >     >     >     > >                 ]
    >     >     >     > >                 ['0x0066' EipDisconnectRequest
    >     >     >     > >                 ]
    >     >     >     > >                 ['0x006F' CipRRData
    >     >     >     > >                     [const  uint    32  
'EipInterface' '0x00000000']
    >     >     >     > >                     [const  uint    8   'timeout'   
'0x0000']
    >     >     >     > >                 ]
    >     >     >     > >             ]
    >     >     >     > >     ]
    >     >     >     > >     [discriminatedType 'CipRRData'
    >     >     >     > >         [simple         uint        8       'itemNb']
    >     >     >     > >         [array          CipItem     'items'    length 
 'itemNb']
    >     >     >     > >         [discriminator  uint        8       
'CipService']
    >     >     >     > >         [typeSwitch 'CipService'
    >     >     >     > >             ['0x52' CipUnconnectedRequest
    >     >     >     > >                 [simple CommandData    'data']
    >     >     >     > >             ]
    >     >     >     > >             ['0xCC' CipReadResponse
    >     >     >     > >                 [reserved   uint            8   
'0x0000']
    >     >     >     > >                 [simple     uint            8   
'status']
    >     >     >     > >                 [simple     uint            8   
'extStatus']
    >     >     >     > >                 [simple     uint            8    
'dataType']
    >     >     >     > >                 [array      uint            8   
'data'  length  'dataType']
    >     >     >     > >     
    >     >     >     > >             ]
    >     >     >     > >         ]
    >     >     >     > >     ]
    >     >     >     > >     
    >     >     >     > >     [type 'CipItem'
    >     >     >     > >         [simple uint    16  'typeID']
    >     >     >     > >         [simple uint    16  'size']
    >     >     >     > >     ]
    >     >     >     > >     
    >     >     >     > >     [discriminatedType 'CommandData'
    >     >     >     > >         [reserved         uint    8   '0x02']
    >     >     >     > >         [reserved         uint    8   '0x20']   // 
setRequestPathLogicalClassSegment
    >     >     >     > >         [reserved         uint    8   '0x06']   // 
set request class path
    >     >     >     > >         [reserved         uint    8   '0x24']   // 
setRequestPathLogicalInstanceSegment
    >     >     >     > >         [reserved         uint    8   '0x01']   // 
setRequestPathInstance
    >     >     >     > >         [discriminator  uint    8   'CipService']
    >     >     >     > >         [typeSwitch 'CipService'
    >     >     >     > >             ['0x4C' CipReadRequest
    >     >     >     > >                 [simple     uint    8   
'RequestPathSize']
    >     >     >     > >                 [reserved   uint    8   '0x91']
    >     >     >     > >                 [array      uint    8   'tag'   
length  '(RequestPathSize*2) - 1']
    >     >     >     > >                 [reserved   uint    16  '0x0001']  
//itemCount set to 1 for now
    >     >     >     > >             ]
    >     >     >     > >         ]
    >     >     >     > >     
    >     >     >     > >     ]
    >     >     >     > >     
    >     >     >     > >     
    >     >     >     > >     [enum int   16   'CIPDataTypeCode' [uint 8  
'size']
    >     >     >     > >         ['0X00C1'   BOOL            ['1']]
    >     >     >     > >         ['0X00CA'   REAL            ['4']]
    >     >     >     > >         ['0X00C4'   DINT            ['4']]
    >     >     >     > >         ['0X00C3'   INT             ['2']]
    >     >     >     > >         ['0X00C2'   SINT            ['1']]
    >     >     >     > >         ['0X02A0'   STRUCTURED      ['88']]
    >     >     >     > >         ['0X02A0'   STRING          ['88']]
    >     >     >     > >         ['0X02A0'   STRING36        ['40']]
    >     >     >     > >         ['-1'       UNKNOWN         ['-1']]
    >     >     >     > >     ]
    >     >     >     > >     
    >     >     >     > >     
    >     >     >     > >     Thanks for any help!
    >     >     >     > >     
    >     >     >     > >     Etienne 
    >     >     >     > >     On 2020/03/10 15:18:47, Etienne Robinet 
<[email protected]> wrote: 
    >     >     >     > >     > Hi all,
    >     >     >     > >     > I've managed to implement the EIP Session 
Register/Unregister (used for connected message which is best for high 
frequency fetching). I will push it to my branch and create a document 
explaining my steps.
    >     >     >     > >     > Next I want to do was to to the CIP 
encapsulation part for accessing tag by their name. The thing is, CIP is (from 
what I heard) proper to Allen Bradley. Should I leave it in the EIP driver or 
modify and adapt the current AB driver later on? For now I will continue on eip.
    >     >     >     > >     > 
    >     >     >     > >     > Etienne
    >     >     >     > >     > 
    >     >     >     > >     > On 2020/03/10 14:41:42, Cesar Garcia 
<[email protected]> wrote: 
    >     >     >     > >     > > Hi,
    >     >     >     > >     > > 
    >     >     >     > >     > > You can document the process step by step, 
you will surely find observation
    >     >     >     > >     > > points.
    >     >     >     > >     > > 
    >     >     >     > >     > > I am working with the handwritten S7 driver, 
but in the future I would
    >     >     >     > >     > > support the team in migrate to mspec, so the 
experience you will gain with
    >     >     >     > >     > > the Etheret / IP is very important.
    >     >     >     > >     > > 
    >     >     >     > >     > > Best regards,
    >     >     >     > >     > > 
    >     >     >     > >     > > El mar., 10 mar. 2020 a las 9:17, Christofer 
Dutz (<
    >     >     >     > >     > > [email protected]>) escribió:
    >     >     >     > >     > > 
    >     >     >     > >     > > > Hi Etienne,
    >     >     >     > >     > > >
    >     >     >     > >     > > > I would strongly suggest you install the 
Antlr plugn for the IDE you use.
    >     >     >     > >     > > > The problem is that ANTLR seems to gobble 
up a lot of errors and tries to
    >     >     >     > >     > > > be smart in a lot of cases.
    >     >     >     > >     > > > Whenever I have problems like this I use 
the ANTLR visual parser to parse
    >     >     >     > >     > > > a block of mspec (one type at a time) and 
try to narrow down the cause.
    >     >     >     > >     > > >
    >     >     >     > >     > > > Chris
    >     >     >     > >     > > >
    >     >     >     > >     > > >
    >     >     >     > >     > > >
    >     >     >     > >     > > > Am 10.03.20, 13:31 schrieb "Etienne 
Robinet" <[email protected]>:
    >     >     >     > >     > > >
    >     >     >     > >     > > >     Hi all,
    >     >     >     > >     > > >     I've been struggling with implementing 
the EIP driver. I started
    >     >     >     > >     > > > writing the mspec after creating both a 
module for the protocol and the one
    >     >     >     > >     > > > from the driver. I copied and adapted the 
pom(s) from the AB-ETH but only
    >     >     >     > >     > > > the enum is generated.
    >     >     >     > >     > > >     Here is a link to the forked branch:
    >     >     >     > >     > > > 
https://github.com/etiennerobinet/plc4x/tree/eip
    >     >     >     > >     > > >
    >     >     >     > >     > > >     I've been studying the EIP/CIP protocol 
and now I am confident what
    >     >     >     > >     > > > the packages should contain but I can not 
figure out how to generate this
    >     >     >     > >     > > > with the templates. Am I missing something?
    >     >     >     > >     > > >
    >     >     >     > >     > > >     Etienne
    >     >     >     > >     > > >
    >     >     >     > >     > > >
    >     >     >     > >     > > >
    >     >     >     > >     > > 
    >     >     >     > >     > > -- 
    >     >     >     > >     > > *CEOS Automatización, C.A.*
    >     >     >     > >     > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, 
C.A.,*
    >     >     >     > >     > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR 
GUAMACHITO,*
    >     >     >     > >     > > 
    >     >     >     > >     > > *FRENTE A LA ASOCIACION DE 
GANADEROS,BARCELONA,EDO. ANZOATEGUI*
    >     >     >     > >     > > *Ing. César García*
    >     >     >     > >     > > *Cel: 0416-681.03.99*
    >     >     >     > >     > > 
    >     >     >     > >     > > *Cel: 0414-760.98.95*
    >     >     >     > >     > > 
    >     >     >     > >     > > *Hotline Técnica SIEMENS: 0800 1005080*
    >     >     >     > >     > > 
    >     >     >     > >     > > *Email: [email protected]
    >     >     >     > >     > > <[email protected]>*
    >     >     >     > >     > > 
    >     >     >     > >     > 
    >     >     >     > >     
    >     >     >     > > 
    >     >     >     > > 
    >     >     >     > 
    >     >     >     
    >     >     > 
    >     >     > 
    >     >     
    >     > 
    >     > 
    >     
    > 
    > 
    

Reply via email to