Hi Lukasz, but we don't have a: [enum uint 16 little endian 'CommandId'] But only a: [enum uint 16 'CommandId']
And in your case I think perhaps the constants are not correct. So having a 16 bit uint will result in a 4 digit hex string: So if you are having problems in mapping them to your constants, perhaps the constants are in the wrong endianness. I have encountered (but can't recall where) that the Enum constants in a BE protocol were written down in LE notation. Of course the thing can't work then. So if for example you have the constant "1" in a BE protocol with a uint 16 enum type, your constant is not 0x0001, but 0x0100 instead. Chris Am 14.04.20, 12:37 schrieb "Łukasz Dywicki" <[email protected]>: The legendary "two bytes" (shall we create a band with this name?!) are coming from unfortunate State type. I don't mind these to be an int/sint/uint or whathever - this is matter of interpretation. If you could please check again my earlier messages you will find struggle I have which is - how much given type takes. We have that for enums [enum uint 16 little endian 'CommandId'] but we don't have that for complex types [type 'State'] This leads to situation that we don't know how to read and interpret incoming byte sequence or how to properly write it back to stream. It would be great if we could limit the issue just to // read state = StateIO.parseStatic(io.readUnsignedInt(16, true)); // true->LE // write wio = new WriteBuffer(2); StateIO.staticSerialize(wio, new State(...)); io.writeUnsignedInt(8, wio.read, true); // true->LE However to do that first we need to know that State is a uint 16 LE and then do a lot of mambo-jambo in code generators to cope with that. :-) Best, Łukasz On 14.04.2020 12:20, Christofer Dutz wrote: > Oh gee ... I totally remember having exactly the same discussion with Sebastian about "bytes" ... > > The problem is there is generally no "byte" "int" and "uint" because a byte = 8 bits is either signed or unsigned. That should the 3rd option be? Perhaps-signed? > So generally I use "uint 8" for what you refer to as a "byte 8". > > Wo what would be the difference between your "2 byte little endian" and an "uint 16" with a LE ReadBuffer? > > I think what you have to rid yourself of thinking of int as number and a byte not being a number. > > Chris > > > > Am 14.04.20, 10:52 schrieb "Łukasz Dywicki" <[email protected]>: > > Hey Christian, > The problem I face is quite simple. State type in mspec i declared as a > bunch of bits. Type length is fixed, however not available anywhere in > mspec or code generator to re-arrange bytes upfront. All we have exposed > at reader/write level is read/write bit. > To be fair LE/BE support in read/write buffers is limited just to > numbers. There is no such support for raw bytes or bits, cause for that > you need to declare a length of LE/BE sequence. > > I would love if I could just declare State as '2 byte little endian' so > it would be read properly upfront and parsed with no changes in > generated code, however I'm not sure how to do it and where. That's why > I'm playing with different things described in earlier mail. > Since all type handling is general I am just afraid of more complicated > scenarios where we have variable length structures such as arrays. > > Best regards, > Łukasz > > > On 14.04.2020 09:41, Christofer Dutz wrote: > > Hi Lukasz, > > > > I am not sure I am understanding the problems you are facing. We already have LE and BE protocols. > > For example EIP is LE and the rest is generally BE. It seems that ADS/AMS is also LE. > > mspec doesn't even know about endianness. > > > > Up till now the endianness doesn't have an effect on bit-fields or single-bit ints. > > It only starts to affect if a field goes from one byte to the next, which is usually for (u)int and floating point values. > > > > That's why we have created the Read/WriteBuffers to set their endianness in the constructor. > > > > So if you're creating a driver for ADS/AMS which is LE, then you write the mspec according to the sequence the information is located in the transferred bytes and have the Read/WriteBuffer handle the endianness issue. > > > > I do see a problem when there are drivers that use mixed endianness, but we have still to encounter such a protocol. > > > > So I have to admit that I don't like any of the mspec changes you proposed, as I think you are just not using the tools we have the right way. > > > > Chris > > > > > > > > Am 14.04.20, 00:32 schrieb "Łukasz Dywicki" <[email protected]>: > > > > Hey Niclas, > > I realized how old the old things are when I started preparing > > automation training for mere mortals and got into history of frames and > > even cabling. Mr. Modbus and EIA-485 is definitely older than I. ;-) > > > > Getting back to the point - yes. I been thinking how to address the byte > > order in effective way. Here are two approaches I have for now: > > > > A) My initial attempt is just a temporary buffer which is then written > > in reverse order to caller. For reading it is similar - just getting N > > bytes in reversed order. The hard part is.. knowing N. I had to add a > > static calculation in order to allocate valid buffer sizes. I tend to > > work but I'm not happy with this approach cause it involves additional work. > > B) Second idea I've got is really simple and relies on code generation. > > We know in which order fields are coming. Here I'm referring to a State > > field which is just bunch of bits. If we would group fields in bytes and > > generate code in reverse order then it has chance to work. Requirement > > for that - ability to know basic field sizes upfront. > > C) Try to combine above with bit-io or Read/WriteBuffers as these are > > places which know actual position and state of buffers which are being > > read/written. > > > > Now, getting to two cases which are a problem. CommandId and State. So > > with command id situation is simple as it is declared as enum and it is > > read as uint. We know size upfront and can generate valid method call > > (readIntLE). > > [enum uint 16 little endian 'CommandId' > > ['0x00' INVALID] > > ['0x01' ADS_READ_DEVICE_INFO] > > ['0x02' ADS_READ] > > ['0x03' ADS_WRITE] > > ['0x04' ADS_READ_STATE] > > ['0x05' ADS_WRITE_CONTROL] > > ['0x06' ADS_ADD_DEVICE_NOTIFICATION] > > ['0x07' ADS_DELETE_DEVICE_NOTIFICATION] > > ['0x08' ADS_DEVICE_NOTIFICATION] > > ['0x09' ADS_READ_WRITE] > > ] > > > > Second candidate is what I'm stuck right now sniping next cycles of > > problems. So in case of State we have complex type composed from 2 > > bytes. A note here - instead of two bytes we might have a variable > > length type which includes array or other variable section. > > [type little endian 'State' > > [simple bit 'broadcast' ] > > [reserved int 7 '0x0' ] > > [simple bit 'initCommand' ] > > [simple bit 'updCommand' ] > > [simple bit 'timestampAdded' ] > > [simple bit 'highPriorityCommand' ] > > [simple bit 'systemCommand' ] > > [simple bit 'adsCommand' ] > > [simple bit 'noReturn' ] > > [simple bit 'response' ] > > ] > > > > The order of reading big endian encoded data to impose little endian > > shift would be (please correct me if I'm wrong): > > 1) init > > 2) udp > > 3) add timestamp > > 4) priority > > 5) system > > 6) ads > > 7) noreturn > > 8) response (end of byte 1) > > 9) broadcast > > 10) reserved (end of byte ) > > We can do same trick for writing, by re-arranging fields. By this way we > > avoid any additional byte level operations. > > > > Overall trouble with generated driver is to declare "how much" bytes > > should be read and interpreted. We have precise size information at the > > runtime - due to length fields, we can leverage it at generation time, > > but then we won't be able to cover all cases. > > > > I would love to keep it simple and do not break things thus I need your > > advice on how to approach this problem in a valid way. > > > > Cheers, > > Łukasz > > > > > > On 13.04.2020 03:26, Niclas Hedhman wrote: > > > <anecdotal-rant> > > > For us who were around and shaping the protocols in the 1980s, and people > > > before us (and before standards like RS-232), a lot of the "specifications" > > > came out of "observation of implementation we managed to get to work", > > > rather than "implement this spec". A lot was due to extreme memory > > > constraints (in my case, multi-tasking operating system, serial protocol > > > 187kbps, interpreted programming language with floating point ops and user > > > applications in 2kB RAM and 8kB EPROM) and a general lack of information, > > > like what other people were doing, sharing experiences and so on. > > > > > > And there were many "innovative" ways to squeeze just a little bit extra > > > out of the hardware, resulting in "hard to understand" consequences. Bit > > > packing was a typical one, multiple functions packed into a single byte. > > > Look at page 14 in https://www.nxp.com/docs/en/data-sheet/80C31_80C32.pdf > > > and read up on "UART Enahanced Mode", and we used this, i.e. 9 bits, no > > > parity and clever use of address and mask to create a slave-to-slave direct > > > protocol, where the master's role was to signal which slave "owned" the > > > cable. Yeah, in that 8kB ROM limitation (I think protocol was about 1kB > > > ROM) and something like 150 bytes RAM for comm protocol. > > > > > > Could you implement a compatible device to this with PLC4X and modern > > > hardware (i.e. no 8031/32 co-processor)? Possibly but bit-banging is needed > > > to support the 9bit data (+start and stop bits) and an awful lot of CPU > > > cycles on something that was automatic on one of the slowest long-lived > > > microcontroller ever. > > > </anecdotal-rant> > > > > > > My point was only to highlight that some of the strange things you see in > > > protocols today, have its roots in pre-standardization days. Today no one > > > would go down that route, because the hardware cost nothing now (8031 + > > > 8kB EPROM + 2kB static RAM + battery backup => ~$50 in 1983's currency) and > > > longevity of software is more important. > > > > > > Cheers > > > Niclas > > > > > > > > > On Sun, Apr 12, 2020 at 10:10 PM Christofer Dutz <[email protected]> > > > wrote: > > > > > >> Hi Lukasz, > > >> > > >> I think it really gets tricky when using BE and having some byte-odd-sizes > > >> ... I remember in the Firmata protocol there were some bitmasks and then 10 > > >> bit uint as BE ... not it really got tricky as the specs were written from > > >> a point of view: You read 16 bits BE and then the first6 bits mean XYZ > > >> instead of describing how the bits actually travel over the wire. > > >> > > >> Chris > > >> > > >> > > >> > > >> Am 11.04.20, 01:21 schrieb "Łukasz Dywicki" <[email protected]>: > > >> > > >> I've made some progress with topic by modyfing mspec and allowing > > >> 'little endian' flag on fields. This moved me further to next issue - > > >> which is whole type encoded little endian. > > >> > > >> In ADS driver such type is State, which has 2 bytes and uses 8 bits for > > >> various flags. > > >> There are two cases which require different approach - reading and > > >> writing. So for reading we need to swap N bytes based on type length. > > >> For writing we need to alocate buffer for N bytes and swap them before > > >> writing. > > >> > > >> I am stuck now with freemaker templates and bit-io. > > >> > > >> Cheers, > > >> Łukasz > > >> > > >> > > >> > > >> On 10.04.2020 17:57, Łukasz Dywicki wrote: > > >> > I am doing some tests of ADS serialization. > > >> > > > >> > I've run into some troubles with payload which is generated with new > > >> > driver. I'm not sure if that's my fault or generated code. > > >> > > > >> > I did a verification of what Wireshark shows and how ads structures > > >> are > > >> > parsed. There is a gap I think. For example ams port number 1000 > > >> > (0x1027) is read as 4135. > > >> > > > >> > Obviously I used wrong structures while implementing protocol logic > > >> in > > >> > first place, but now I am uncertain of how fields are encoded. How we > > >> > mark field as little endian when rest of payload is big endian? Do we > > >> > have `uint_le`? > > >> > > > >> > As far I remember route creation logic I was tracking last week used > > >> > combination of LE and BE. > > >> > > > >> > Best regards, > > >> > Łukasz > > >> > > > >> > > >> > > >> > > > > > > > > >