Hi Lukasz,
I wasn't suggesting to look how WireShark decodes things. Cause I would assume
that they read a short in little endian and then (on the rearranged bytes)
apply some bit checks.
I was more suggesting that you look into the bytes Wireshark shows you and to
check their exact position.
When implementing drivers, I used the Mac's Calculator tool quite often to see
the bits for a given byte value.
In your example I can't see any need for endianness at all ... it's all just
bits and one empty block which forms a full byte together with the first bit.
As this block doesn't cross any byte boundaries I can't see any problems with
this.
Assuming I understand what you are implying with
[type little endian 'State'
[simple bit 'broadcast' ]
[reserved int 7 '0x0' ]
[simple bit 'initCommand' ]
[simple bit 'updCommand' ]
[simple bit 'timestampAdded' ]
[simple bit 'highPriorityCommand' ]
[simple bit 'systemCommand' ]
[simple bit 'adsCommand' ]
[simple bit 'noReturn' ]
[simple bit 'response' ]
]
Then it should be equal to:
[type 'State'
[simple bit 'initCommand' ]
[simple bit 'updCommand' ]
[simple bit 'timestampAdded' ]
[simple bit 'highPriorityCommand' ]
[simple bit 'systemCommand' ]
[simple bit 'adsCommand' ]
[simple bit 'noReturn' ]
[simple bit 'response' ]
[simple bit 'broadcast' ]
[reserved int 7 '0x0' ]
]
Which also seems to be the exact order how the bits go over the wire ... I mean
... it doesn't make any sense to put the 7 empty bits in the middle.
Chris
Am 30.04.20, 22:42 schrieb "Łukasz Dywicki" <[email protected]>:
Hey Chris and others,
I let this topic to dust and freeze a bit, however I would like to lift
it up again. Since the 0.7 release is now in discussion and ADS is not
ported yet I believe it is reasonable to validate this problem.
As you suggested I've checked wireshark sources to see how they parse
state fragment of AMS header. While I can not read C properly and was
unable to locate actual reading logic, I do see they care about endianness:
https://github.com/wireshark/wireshark/blob/5cf3fd03f1538b37704d83b6c38b8223f9036108/plugins/epan/ethercat/packet-ams.c#L429
Their frame traversal goes in following order:
- response
- no return
- ads cmd
- system cmd
- high priority
- timestamp add
- udp
- init cmd
- broadcast
When I've tried to model mspec with respect to little endian order, I
end up with following field order:
- init cmd
- udp
- timestamp add
- high priority
- system cmd
- ads cmd
- no return
- response
- [reserved]
- broadcast
I haven't seen ADS protocol book, my main source of information is
infosys which is rather short in this area. I doubt if they would
describe fields in above order.
My initial attempts were similar to what you said - to read the value
and then shift bytes. With your feedback I started to look for better
ways to solve it. With my last attempt I solved the problem by
re-adjusting fields during code generation, so they appear in a valid
byte order. Beside additional flag at the mspec there is a need for this
helper:
build-utils/protocol-base-mspec/src/main/java/org/apache/plc4x/plugins/codegenerator/language/mspec/model/definitions/DefaultComplexTypeDefinition.java
In above commit the State declaration in the mspec looks like this:
[type little endian 'State'
[simple bit 'broadcast' ]
[reserved int 7 '0x0' ]
[simple bit 'initCommand' ]
[simple bit 'updCommand' ]
[simple bit 'timestampAdded' ]
[simple bit 'highPriorityCommand' ]
[simple bit 'systemCommand' ]
[simple bit 'adsCommand' ]
[simple bit 'noReturn' ]
[simple bit 'response' ]
]
Maybe it is not in line with wireshark, but it is consistent and:
1) requires minor change in code generator
2) does not involve additional processing of data
3) mspec is still easy to write
4) type declaration is in line with wireshark output when reading from
the left and not from the top. ;-)
5) it can be adjusted to be 100% consistent with wireshark by changing
helper logic. ;-)
Best regards,
Łukasz
On 14.04.2020 21:25, Christofer Dutz wrote:
> Hi Lukasz,
>
> I see it differently.
>
> If you say something is LE/BE then it should be consistent.
>
> I for my part like it if the mspec is consistent with what I see in
WireShark. Otherwise you would always have to do a sort of 2 step parsing:
>
> "Read 4 bytes in BE and then on the rearranged byte sequence take the
first 3 bits and call them X and the next bit after that Y and so on."
>
> In this case you would also have to know how large the chunk is to read
in order to know how to decode it's content.
> Having a historically partitioned set of two 16 bit bit-fields would look
completely different to a 32 bit bit-field.
>
> I don't like adding this extra level, even if it's probably the way
protocols were implemented when lacking the ability to write individual bits.
> I guess the usual process was to read a BE short (2 bytes) and to the
resulting unsigned short value apply different logical or operations to get the
information.
> In PLC4X we can simply read any number of bits and don't have to twist
our minds in which chunks I have to read things first.
>
> So I think the way you are proposing is probably the wider used version
due to legacy restrictions, but also the more complicated way.
>
> So I would like to keep it simple, even if the developer will have to do
a little more brain-work.
>
> I mean all we are doing in this project is going the extra mile so others
don't have to ... at least the ones contributing are doing that.
>
> What do the others say to this? (Ideally ones that have already used
mspec or ones that understand the problem)
>
> Chris
>
>
> Am 14.04.20, 15:46 schrieb "Łukasz Dywicki" <[email protected]>:
>
> Hey Chris,
> Sorry for wrongly addressed mail, it was intended to go to mailing
list.
>
> To the point - I think that what you propose with reordering fields
> manually shift the load from the tool to the developer. It will lead
to
> further implementation errors caused by a need to reorder fields while
> creating spec. It will be inconsistent with rest of places where
things
> are in "natural order" (big endian) except one or two types which
> collects bit flags which will have to be declared in different order.
> What I did in my naive implementation with "little endian" flag on the
> State type is re-arrangement of fields during generation time.
> It does not require any byte shifting at the runtime and keeps natural
> order of fields without the need for manual reordering of flags in
mspec
> declaration.
>
> I understand that keeping mspec simple is an important priority,
however
> doing it at the cost of developers who will use it to implement codecs
> will not help us in long term.
> I'm quite sure that sooner or later we will get a protocol with mix
of
> BE/LE fields.
>
> Cheers,
> Łukasz
>
>
> On 14.04.2020 14:57, Christofer Dutz wrote:
> > Hi Lukasz (adding dev@ to the recipients again)
> >
> >
> >
> > you are not quite correct. Enum types do declare a base type where
they
> > are declared … not where they are used.
> >
> >
> >
> > If you have bit-fields then why don’t you define them as sequence of
> > bits? I really can’t understand why you need to flip anything.
> >
> > I think you’re trying to do something similar to Sebastian when he
> > wanted to introduce some bit-mask types.
> >
> >
> >
> > I could imagine that in the spec it might be written … these two
bytes
> > are a bit-mask and the bit 1 means X bit 10 means Y, …
> >
> > So why not define the bit fields in the sequence they are sent over
the
> > wire?
> >
> >
> >
> > Assuming you have a bit field of 16 bits BE uint. If the spec now
says:
> >
> >
> >
> >
> >
> > Bit: 15|14|13|12|11|10|9 |8 |7 |6 |5 |4 |3
|2
> > |1 |0
> >
> > Meaning: A |B |C |D |E | F |G|H |I | J | K |L |
M|N |O |P
> >
> >
> >
> > Then the order they are sent is:
> >
> > 7 |6 |5 |4 |3 |2 |1 |0 | 15|14|13|12|11|10|9 |8
> >
> > So you have to declare the bit fields in the order:
> >
> > I | J | K |L | M|N |O |P |A |B
|C |D
> > |E | F |G|H
> >
> >
> >
> > So I don’t quite understand what you’re trying to flip here.
> >
> >
> >
> > Chris
> >
> >
> >
> > *Von: *Łukasz Dywicki <[email protected]>
> > *Datum: *Dienstag, 14. April 2020 um 13:26
> > *An: *Christofer Dutz <[email protected]>
> > *Betreff: *Re: Big and littleendian fields in one mspec
> >
> >
> >
> > I've added the endianness switch to the types in my experiments.
These
> > are not needed for enums as these are read as int and then mapped to
> > constants. I referred to these as an example - enum does have a
length
> > indication and type behind it.
> >
> >
> >
> > Again, I will bring the issue - StateIO currently fails to do
anything
> > useful due to BE/LE switch. Because this type uses single bits which
> > need to be flipped before reading or after writing otherwise they
end up
> > in improper order. Out of 16 bits 9 are in use so we have a lot of
> > possible combinations (2^9), which seems too much to create an enum.
> >
> > Since you didn't like my initial proposal and modifications (as they
> > might be redundant to what is available in the buffer API), how
would
> > you handle State serialization without affecting mspec and without
> > further complication to code generation?
> >
> >
> >
> > Best,
> >
> > Łukasz
> >
> >
> >
> > wt., 14 kwi 2020 o 12:47 Christofer Dutz <[email protected]
> > <mailto:[email protected]>> napisał(a):
> >
> > Hi Lukasz,
> >
> > but we don't have a:
> > [enum uint 16 little endian 'CommandId']
> > But only a:
> > [enum uint 16 'CommandId']
> >
> > And in your case I think perhaps the constants are not correct.
So
> > having a 16 bit uint will result in a 4 digit hex string:
> > So if you are having problems in mapping them to your constants,
> > perhaps the constants are in the wrong endianness.
> >
> > I have encountered (but can't recall where) that the Enum
constants
> > in a BE protocol were written down in LE notation.
> > Of course the thing can't work then.
> >
> > So if for example you have the constant "1" in a BE protocol
with a
> > uint 16 enum type, your constant is not 0x0001, but 0x0100
instead.
> >
> > Chris
> >
> >
> >
> >
> > Am 14.04.20, 12:37 schrieb "Łukasz Dywicki" <[email protected]
> > <mailto:[email protected]>>:
> >
> > The legendary "two bytes" (shall we create a band with this
> > name?!) are
> > coming from unfortunate State type. I don't mind these to
be an
> > int/sint/uint or whathever - this is matter of
interpretation.
> >
> > If you could please check again my earlier messages you
will find
> > struggle I have which is - how much given type takes.
> >
> > We have that for enums
> > [enum uint 16 little endian 'CommandId']
> >
> > but we don't have that for complex types
> > [type 'State']
> >
> > This leads to situation that we don't know how to read and
interpret
> > incoming byte sequence or how to properly write it back to
stream.
> >
> > It would be great if we could limit the issue just to
> > // read
> > state = StateIO.parseStatic(io.readUnsignedInt(16, true));
//
> > true->LE
> > // write
> > wio = new WriteBuffer(2);
> > StateIO.staticSerialize(wio, new State(...));
> > io.writeUnsignedInt(8, wio.read, true); // true->LE
> >
> > However to do that first we need to know that State is a
uint 16
> > LE and
> > then do a lot of mambo-jambo in code generators to cope with
> > that. :-)
> >
> > Best,
> > Łukasz
> >
> >
> > On 14.04.2020 12:20, Christofer Dutz wrote:
> > > Oh gee ... I totally remember having exactly the same
> > discussion with Sebastian about "bytes" ...
> > >
> > > The problem is there is generally no "byte" "int" and
"uint"
> > because a byte = 8 bits is either signed or unsigned. That
should
> > the 3rd option be? Perhaps-signed?
> > > So generally I use "uint 8" for what you refer to as a
"byte 8".
> > >
> > > Wo what would be the difference between your "2 byte
little
> > endian" and an "uint 16" with a LE ReadBuffer?
> > >
> > > I think what you have to rid yourself of thinking of int
as
> > number and a byte not being a number.
> > >
> > > Chris
> > >
> > >
> > >
> > > Am 14.04.20, 10:52 schrieb "Łukasz Dywicki"
> > <[email protected] <mailto:[email protected]>>:
> > >
> > > Hey Christian,
> > > The problem I face is quite simple. State type in
mspec i
> > declared as a
> > > bunch of bits. Type length is fixed, however not
available
> > anywhere in
> > > mspec or code generator to re-arrange bytes upfront.
All
> > we have exposed
> > > at reader/write level is read/write bit.
> > > To be fair LE/BE support in read/write buffers is
limited
> > just to
> > > numbers. There is no such support for raw bytes or
bits,
> > cause for that
> > > you need to declare a length of LE/BE sequence.
> > >
> > > I would love if I could just declare State as '2 byte
> > little endian' so
> > > it would be read properly upfront and parsed with no
> > changes in
> > > generated code, however I'm not sure how to do it and
> > where. That's why
> > > I'm playing with different things described in
earlier mail.
> > > Since all type handling is general I am just afraid of
> > more complicated
> > > scenarios where we have variable length structures
such as
> > arrays.
> > >
> > > Best regards,
> > > Łukasz
> > >
> > >
> > > On 14.04.2020 09:41, Christofer Dutz wrote:
> > > > Hi Lukasz,
> > > >
> > > > I am not sure I am understanding the problems you
are
> > facing. We already have LE and BE protocols.
> > > > For example EIP is LE and the rest is generally BE.
It
> > seems that ADS/AMS is also LE.
> > > > mspec doesn't even know about endianness.
> > > >
> > > > Up till now the endianness doesn't have an effect on
> > bit-fields or single-bit ints.
> > > > It only starts to affect if a field goes from one
byte
> > to the next, which is usually for (u)int and floating point
values.
> > > >
> > > > That's why we have created the Read/WriteBuffers to
set
> > their endianness in the constructor.
> > > >
> > > > So if you're creating a driver for ADS/AMS which is
LE,
> > then you write the mspec according to the sequence the
information
> > is located in the transferred bytes and have the
Read/WriteBuffer
> > handle the endianness issue.
> > > >
> > > > I do see a problem when there are drivers that use
mixed
> > endianness, but we have still to encounter such a protocol.
> > > >
> > > > So I have to admit that I don't like any of the
mspec
> > changes you proposed, as I think you are just not using the
tools we
> > have the right way.
> > > >
> > > > Chris
> > > >
> > > >
> > > >
> > > > Am 14.04.20, 00:32 schrieb "Łukasz Dywicki"
> > <[email protected] <mailto:[email protected]>>:
> > > >
> > > > Hey Niclas,
> > > > I realized how old the old things are when I
started
> > preparing
> > > > automation training for mere mortals and got
into
> > history of frames and
> > > > even cabling. Mr. Modbus and EIA-485 is
definitely
> > older than I. ;-)
> > > >
> > > > Getting back to the point - yes. I been
thinking how
> > to address the byte
> > > > order in effective way. Here are two approaches
I
> > have for now:
> > > >
> > > > A) My initial attempt is just a temporary buffer
> > which is then written
> > > > in reverse order to caller. For reading it is
> > similar - just getting N
> > > > bytes in reversed order. The hard part is..
knowing
> > N. I had to add a
> > > > static calculation in order to allocate valid
buffer
> > sizes. I tend to
> > > > work but I'm not happy with this approach cause
it
> > involves additional work.
> > > > B) Second idea I've got is really simple and
relies
> > on code generation.
> > > > We know in which order fields are coming. Here
I'm
> > referring to a State
> > > > field which is just bunch of bits. If we would
group
> > fields in bytes and
> > > > generate code in reverse order then it has
chance to
> > work. Requirement
> > > > for that - ability to know basic field sizes
upfront.
> > > > C) Try to combine above with bit-io or
> > Read/WriteBuffers as these are
> > > > places which know actual position and state of
> > buffers which are being
> > > > read/written.
> > > >
> > > > Now, getting to two cases which are a problem.
> > CommandId and State. So
> > > > with command id situation is simple as it is
> > declared as enum and it is
> > > > read as uint. We know size upfront and can
generate
> > valid method call
> > > > (readIntLE).
> > > > [enum uint 16 little endian 'CommandId'
> > > > ['0x00' INVALID]
> > > > ['0x01' ADS_READ_DEVICE_INFO]
> > > > ['0x02' ADS_READ]
> > > > ['0x03' ADS_WRITE]
> > > > ['0x04' ADS_READ_STATE]
> > > > ['0x05' ADS_WRITE_CONTROL]
> > > > ['0x06' ADS_ADD_DEVICE_NOTIFICATION]
> > > > ['0x07' ADS_DELETE_DEVICE_NOTIFICATION]
> > > > ['0x08' ADS_DEVICE_NOTIFICATION]
> > > > ['0x09' ADS_READ_WRITE]
> > > > ]
> > > >
> > > > Second candidate is what I'm stuck right now
sniping
> > next cycles of
> > > > problems. So in case of State we have complex
type
> > composed from 2
> > > > bytes. A note here - instead of two bytes we
might
> > have a variable
> > > > length type which includes array or other
variable
> > section.
> > > > [type little endian 'State'
> > > > [simple bit 'broadcast' ]
> > > > [reserved int 7 '0x0' ]
> > > > [simple bit 'initCommand' ]
> > > > [simple bit 'updCommand' ]
> > > > [simple bit 'timestampAdded' ]
> > > > [simple bit 'highPriorityCommand' ]
> > > > [simple bit 'systemCommand' ]
> > > > [simple bit 'adsCommand' ]
> > > > [simple bit 'noReturn' ]
> > > > [simple bit 'response' ]
> > > > ]
> > > >
> > > > The order of reading big endian encoded data to
> > impose little endian
> > > > shift would be (please correct me if I'm wrong):
> > > > 1) init
> > > > 2) udp
> > > > 3) add timestamp
> > > > 4) priority
> > > > 5) system
> > > > 6) ads
> > > > 7) noreturn
> > > > 8) response (end of byte 1)
> > > > 9) broadcast
> > > > 10) reserved (end of byte )
> > > > We can do same trick for writing, by
re-arranging
> > fields. By this way we
> > > > avoid any additional byte level operations.
> > > >
> > > > Overall trouble with generated driver is to
declare
> > "how much" bytes
> > > > should be read and interpreted. We have precise
size
> > information at the
> > > > runtime - due to length fields, we can leverage
it
> > at generation time,
> > > > but then we won't be able to cover all cases.
> > > >
> > > > I would love to keep it simple and do not break
> > things thus I need your
> > > > advice on how to approach this problem in a
valid way.
> > > >
> > > > Cheers,
> > > > Łukasz
> > > >
> > > >
> > > > On 13.04.2020 03:26, Niclas Hedhman wrote:
> > > > > <anecdotal-rant>
> > > > > For us who were around and shaping the
protocols
> > in the 1980s, and people
> > > > > before us (and before standards like RS-232),
a
> > lot of the "specifications"
> > > > > came out of "observation of implementation we
> > managed to get to work",
> > > > > rather than "implement this spec". A lot was
due
> > to extreme memory
> > > > > constraints (in my case, multi-tasking
operating
> > system, serial protocol
> > > > > 187kbps, interpreted programming language with
> > floating point ops and user
> > > > > applications in 2kB RAM and 8kB EPROM) and a
> > general lack of information,
> > > > > like what other people were doing, sharing
> > experiences and so on.
> > > > >
> > > > > And there were many "innovative" ways to
squeeze
> > just a little bit extra
> > > > > out of the hardware, resulting in "hard to
> > understand" consequences. Bit
> > > > > packing was a typical one, multiple functions
> > packed into a single byte.
> > > > > Look at page 14 in
> > https://www.nxp.com/docs/en/data-sheet/80C31_80C32.pdf
> > > > > and read up on "UART Enahanced Mode", and we
used
> > this, i.e. 9 bits, no
> > > > > parity and clever use of address and mask to
> > create a slave-to-slave direct
> > > > > protocol, where the master's role was to
signal
> > which slave "owned" the
> > > > > cable. Yeah, in that 8kB ROM limitation (I
think
> > protocol was about 1kB
> > > > > ROM) and something like 150 bytes RAM for comm
> > protocol.
> > > > >
> > > > > Could you implement a compatible device to
this
> > with PLC4X and modern
> > > > > hardware (i.e. no 8031/32 co-processor)?
Possibly
> > but bit-banging is needed
> > > > > to support the 9bit data (+start and stop
bits)
> > and an awful lot of CPU
> > > > > cycles on something that was automatic on one
of
> > the slowest long-lived
> > > > > microcontroller ever.
> > > > > </anecdotal-rant>
> > > > >
> > > > > My point was only to highlight that some of
the
> > strange things you see in
> > > > > protocols today, have its roots in
> > pre-standardization days. Today no one
> > > > > would go down that route, because the hardware
> > cost nothing now (8031 +
> > > > > 8kB EPROM + 2kB static RAM + battery backup =>
> > ~$50 in 1983's currency) and
> > > > > longevity of software is more important.
> > > > >
> > > > > Cheers
> > > > > Niclas
> > > > >
> > > > >
> > > > > On Sun, Apr 12, 2020 at 10:10 PM Christofer
Dutz
> > <[email protected] <mailto:[email protected]>>
> > > > > wrote:
> > > > >
> > > > >> Hi Lukasz,
> > > > >>
> > > > >> I think it really gets tricky when using BE
and
> > having some byte-odd-sizes
> > > > >> ... I remember in the Firmata protocol there
were
> > some bitmasks and then 10
> > > > >> bit uint as BE ... not it really got tricky
as
> > the specs were written from
> > > > >> a point of view: You read 16 bits BE and
then the
> > first6 bits mean XYZ
> > > > >> instead of describing how the bits actually
> > travel over the wire.
> > > > >>
> > > > >> Chris
> > > > >>
> > > > >>
> > > > >>
> > > > >> Am 11.04.20, 01:21 schrieb "Łukasz Dywicki"
> > <[email protected] <mailto:[email protected]>>:
> > > > >>
> > > > >> I've made some progress with topic by
> > modyfing mspec and allowing
> > > > >> 'little endian' flag on fields. This
moved me
> > further to next issue -
> > > > >> which is whole type encoded little
endian.
> > > > >>
> > > > >> In ADS driver such type is State, which
has 2
> > bytes and uses 8 bits for
> > > > >> various flags.
> > > > >> There are two cases which require
different
> > approach - reading and
> > > > >> writing. So for reading we need to swap N
> > bytes based on type length.
> > > > >> For writing we need to alocate buffer
for N
> > bytes and swap them before
> > > > >> writing.
> > > > >>
> > > > >> I am stuck now with freemaker templates
and
> > bit-io.
> > > > >>
> > > > >> Cheers,
> > > > >> Łukasz
> > > > >>
> > > > >>
> > > > >>
> > > > >> On 10.04.2020 17:57, Łukasz Dywicki
wrote:
> > > > >> > I am doing some tests of ADS
serialization.
> > > > >> >
> > > > >> > I've run into some troubles with
payload
> > which is generated with new
> > > > >> > driver. I'm not sure if that's my
fault or
> > generated code.
> > > > >> >
> > > > >> > I did a verification of what Wireshark
> > shows and how ads structures
> > > > >> are
> > > > >> > parsed. There is a gap I think. For
example
> > ams port number 1000
> > > > >> > (0x1027) is read as 4135.
> > > > >> >
> > > > >> > Obviously I used wrong structures while
> > implementing protocol logic
> > > > >> in
> > > > >> > first place, but now I am uncertain of
how
> > fields are encoded. How we
> > > > >> > mark field as little endian when rest
of
> > payload is big endian? Do we
> > > > >> > have `uint_le`?
> > > > >> >
> > > > >> > As far I remember route creation logic
I
> > was tracking last week used
> > > > >> > combination of LE and BE.
> > > > >> >
> > > > >> > Best regards,
> > > > >> > Łukasz
> > > > >> >
> > > > >>
> > > > >>
> > > > >>
> > > > >
> > > >
> > > >
> > >
> > >
> >
>
>