Hi folks,

so Lukasz just sent me a little pcap file with some AMS packets in there and my 
assumption was correct:

for example in the byte-stream I can see the "flags" being 0x0400 ... However 
wireshark read this as unsigned short LE and therefore re-aranged the bytes:
    StateFlags: 0x0004
        .... .... .... ...0 = RESPONSE: Not set
        .... .... .... ..0. = NO RETURN: Not set
        .... .... .... .1.. = ADS COMMAND: Set
        .... .... .... 0... = SYSTEM COMMAND: Not set
        .... .... ...0 .... = HIGH PRIORITY COMMAND: Not set
        .... .... ..0. .... = TIMESTAMP ADDED: Not set
        .... .... .0.. .... = UDP COMMAND: Not set
        .... .... 0... .... = INIT COMMAND: Not set
        0... .... .... .... = BROADCAST: Not set

So in above example only one field is true: "ADS COMMAND" ... so if I decode 
0x0400 to binary that’s: 00000100 00000000

So this exactly fits my proposed mspec definition of: 

    [type 'State'
            [simple     bit 'initCommand'           ]
            [simple     bit 'updCommand'            ]
            [simple     bit 'timestampAdded'        ]
            [simple     bit 'highPriorityCommand'   ]
            [simple     bit 'systemCommand'         ]
            [simple     bit 'adsCommand'            ]
            [simple     bit 'noReturn'              ]
            [simple     bit 'response'              ]
            [simple     bit 'broadcast'             ]
            [reserved   int 7 '0x0'                 ]
        ]

So I strongly object introducing any special endianness "feature" for this (in 
this case) ... 
we might encounter something where we need it, but for this we don't.

Chris



Am 30.04.20, 23:02 schrieb "Christofer Dutz" <[email protected]>:

    Hi Lukasz,

    I wasn't suggesting to look how WireShark decodes things. Cause I would 
assume that they read a short in little endian and then (on the rearranged 
bytes) apply some bit checks. 

    I was more suggesting that you look into the bytes Wireshark shows you and 
to check their exact position.

    When implementing drivers, I used the Mac's Calculator tool quite often to 
see the bits for a given byte value.

    In your example I can't see any need for endianness at all ... it's all 
just bits and one empty block which forms a full byte together with the first 
bit.
    As this block doesn't cross any byte boundaries I can't see any problems 
with this.

    Assuming I understand what you are implying with 

    [type little endian 'State'
            [simple     bit 'broadcast'             ]
            [reserved   int 7 '0x0'                 ]
            [simple     bit 'initCommand'           ]
            [simple     bit 'updCommand'            ]
            [simple     bit 'timestampAdded'        ]
            [simple     bit 'highPriorityCommand'   ]
            [simple     bit 'systemCommand'         ]
            [simple     bit 'adsCommand'            ]
            [simple     bit 'noReturn'              ]
            [simple     bit 'response'              ]
        ]

    Then it should be equal to:

    [type 'State'
            [simple     bit 'initCommand'           ]
            [simple     bit 'updCommand'            ]
            [simple     bit 'timestampAdded'        ]
            [simple     bit 'highPriorityCommand'   ]
            [simple     bit 'systemCommand'         ]
            [simple     bit 'adsCommand'            ]
            [simple     bit 'noReturn'              ]
            [simple     bit 'response'              ]
            [simple     bit 'broadcast'             ]
            [reserved   int 7 '0x0'                 ]
        ]

    Which also seems to be the exact order how the bits go over the wire ... I 
mean ... it doesn't make any sense to put the 7 empty bits in the middle.

    Chris


    Am 30.04.20, 22:42 schrieb "Łukasz Dywicki" <[email protected]>:

        Hey Chris and others,
        I let this topic to dust and freeze a bit, however I would like to lift
        it up again. Since the 0.7 release is now in discussion and ADS is not
        ported yet I believe it is reasonable to validate this problem.

        As you suggested I've checked wireshark sources to see how they parse
        state fragment of AMS header. While I can not read C properly and was
        unable to locate actual reading logic, I do see they care about 
endianness:
        
https://github.com/wireshark/wireshark/blob/5cf3fd03f1538b37704d83b6c38b8223f9036108/plugins/epan/ethercat/packet-ams.c#L429

        Their frame traversal goes in following order:
        - response
        - no return
        - ads cmd
        - system cmd
        - high priority
        - timestamp add
        - udp
        - init cmd
        - broadcast

        When I've tried to model mspec with respect to little endian order, I
        end up with following field order:
        - init cmd
        - udp
        - timestamp add
        - high priority
        - system cmd
        - ads cmd
        - no return
        - response
        - [reserved]
        - broadcast

        I haven't seen ADS protocol book, my main source of information is
        infosys which is rather short in this area. I doubt if they would
        describe fields in above order.

        My initial attempts were similar to what you said - to read the value
        and then shift bytes. With your feedback I started to look for better
        ways to solve it. With my last attempt I solved the problem by
        re-adjusting fields during code generation, so they appear in a valid
        byte order. Beside additional flag at the mspec there is a need for this
        helper:
        
build-utils/protocol-base-mspec/src/main/java/org/apache/plc4x/plugins/codegenerator/language/mspec/model/definitions/DefaultComplexTypeDefinition.java

        In above commit the State declaration in the mspec looks like this:
        [type little endian 'State'
            [simple     bit 'broadcast'             ]
            [reserved   int 7 '0x0'                 ]
            [simple     bit 'initCommand'           ]
            [simple     bit 'updCommand'            ]
            [simple     bit 'timestampAdded'        ]
            [simple     bit 'highPriorityCommand'   ]
            [simple     bit 'systemCommand'         ]
            [simple     bit 'adsCommand'            ]
            [simple     bit 'noReturn'              ]
            [simple     bit 'response'              ]
        ]

        Maybe it is not in line with wireshark, but it is consistent and:
        1) requires minor change in code generator
        2) does not involve additional processing of data
        3) mspec is still easy to write
        4) type declaration is in line with wireshark output when reading from
        the left and not from the top. ;-)
        5) it can be adjusted to be 100% consistent with wireshark by changing
        helper logic. ;-)

        Best regards,
        Łukasz


        On 14.04.2020 21:25, Christofer Dutz wrote:
        > Hi Lukasz,
        > 
        > I see it differently.
        > 
        > If you say something is LE/BE then it should be consistent. 
        > 
        > I for my part like it if the mspec is consistent with what I see in 
WireShark. Otherwise you would always have to do a sort of 2 step parsing:
        > 
        > "Read 4 bytes in BE and then on the rearranged byte sequence take the 
first 3 bits and call them X and the next bit after that Y and so on."
        > 
        > In this case you would also have to know how large the chunk is to 
read in order to know how to decode it's content.
        > Having a historically partitioned set of two 16 bit bit-fields would 
look completely different to a 32 bit bit-field. 
        > 
        > I don't like adding this extra level, even if it's probably the way 
protocols were implemented when lacking the ability to write individual bits.
        > I guess the usual process was to read a BE short (2 bytes) and to the 
resulting unsigned short value apply different logical or operations to get the 
information.
        > In PLC4X we can simply read any number of bits and don't have to 
twist our minds in which chunks I have to read things first. 
        > 
        > So I think the way you are proposing is probably the wider used 
version due to legacy restrictions, but also the more complicated way.
        > 
        > So I would like to keep it simple, even if the developer will have to 
do a little more brain-work. 
        > 
        > I mean all we are doing in this project is going the extra mile so 
others don't have to ... at least the ones contributing are doing that.
        > 
        > What do the others say to this? (Ideally ones that have already used 
mspec or ones that understand the problem)
        > 
        > Chris
        > 
        > 
        > Am 14.04.20, 15:46 schrieb "Łukasz Dywicki" <[email protected]>:
        > 
        >     Hey Chris,
        >     Sorry for wrongly addressed mail, it was intended to go to 
mailing list.
        >     
        >     To the point - I think that what you propose with reordering 
fields
        >     manually shift the load from the tool to the developer. It will 
lead to
        >     further implementation errors caused by a need to reorder fields 
while
        >     creating spec. It will be inconsistent with rest of places where 
things
        >     are in "natural order" (big endian) except one or two types which
        >     collects bit flags which will have to be declared in different 
order.
        >     What I did in my naive implementation with "little endian" flag 
on the
        >     State type is re-arrangement of fields during generation time.
        >     It does not require any byte shifting at the runtime and keeps 
natural
        >     order of fields without the need for manual reordering of flags 
in mspec
        >     declaration.
        >     
        >     I understand that keeping mspec simple is an important priority, 
however
        >     doing it at the cost of developers who will use it to implement 
codecs
        >     will not help us in long term.
        >     I'm quite sure that sooner or later we will get a  protocol with 
mix of
        >     BE/LE fields.
        >     
        >     Cheers,
        >     Łukasz
        >     
        >     
        >     On 14.04.2020 14:57, Christofer Dutz wrote:
        >     > Hi Lukasz (adding dev@ to the recipients again)
        >     > 
        >     >  
        >     > 
        >     > you are not quite correct. Enum types do declare a base type 
where they
        >     > are declared … not where they are used.
        >     > 
        >     >  
        >     > 
        >     > If you have bit-fields then why don’t you define them as 
sequence of
        >     > bits? I really can’t understand why you need to flip anything.
        >     > 
        >     > I think you’re trying to do something similar to Sebastian when 
he
        >     > wanted to introduce some bit-mask types.
        >     > 
        >     >  
        >     > 
        >     > I could imagine that in the spec it might be written … these 
two bytes
        >     > are a bit-mask and the bit 1 means X bit 10 means Y, …
        >     > 
        >     > So why not define the bit fields in the sequence they are sent 
over the
        >     > wire?
        >     > 
        >     >  
        >     > 
        >     > Assuming you have a bit field of 16 bits BE uint. If the spec 
now says:
        >     > 
        >     >  
        >     > 
        >     >  
        >     > 
        >     > Bit:                        15|14|13|12|11|10|9 |8 |7 |6 |5  |4 
|3  |2
        >     >  |1  |0
        >     > 
        >     > Meaning:            A  |B  |C  |D  |E  | F  |G|H |I  | J | K |L 
| M|N |O |P
        >     > 
        >     >  
        >     > 
        >     > Then the order they are sent is:
        >     > 
        >     > 7 |6 |5  |4 |3  |2  |1  |0 | 15|14|13|12|11|10|9 |8
        >     > 
        >     > So you have to declare the bit fields in the order:
        >     > 
        >     >                                I  | J | K |L | M|N |O |P  |A  
|B  |C  |D
        >     >  |E  | F  |G|H
        >     > 
        >     >  
        >     > 
        >     > So I don’t quite understand what you’re trying to flip here.
        >     > 
        >     >  
        >     > 
        >     > Chris
        >     > 
        >     >  
        >     > 
        >     > *Von: *Łukasz Dywicki <[email protected]>
        >     > *Datum: *Dienstag, 14. April 2020 um 13:26
        >     > *An: *Christofer Dutz <[email protected]>
        >     > *Betreff: *Re: Big and littleendian fields in one mspec
        >     > 
        >     >  
        >     > 
        >     > I've added the endianness switch to the types in my 
experiments. These
        >     > are not needed for enums as these are read as int and then 
mapped to
        >     > constants. I referred to these as an example - enum does have a 
length
        >     > indication and type behind it.
        >     > 
        >     >  
        >     > 
        >     > Again, I will bring the issue - StateIO currently fails to do 
anything
        >     > useful due to BE/LE switch. Because this type uses single bits 
which
        >     > need to be flipped before reading or after writing otherwise 
they end up
        >     > in improper order. Out of 16 bits 9 are in use so we have a lot 
of
        >     > possible combinations (2^9), which seems too much to create an 
enum.
        >     > 
        >     > Since you didn't like my initial proposal and modifications (as 
they
        >     > might be redundant to what is available in the buffer API), how 
would
        >     > you handle State serialization without affecting mspec and 
without
        >     > further complication to code generation?
        >     > 
        >     >  
        >     > 
        >     > Best,
        >     > 
        >     > Łukasz
        >     > 
        >     >  
        >     > 
        >     > wt., 14 kwi 2020 o 12:47 Christofer Dutz 
<[email protected]
        >     > <mailto:[email protected]>> napisał(a):
        >     > 
        >     >     Hi Lukasz,
        >     > 
        >     >     but we don't have a:
        >     >     [enum uint 16 little endian 'CommandId']
        >     >     But only a:
        >     >     [enum uint 16 'CommandId']
        >     > 
        >     >     And in your case I think perhaps the constants are not 
correct. So
        >     >     having a 16 bit uint will result in a 4 digit hex string:
        >     >     So if you are having problems in mapping them to your 
constants,
        >     >     perhaps the constants are in the wrong endianness.
        >     > 
        >     >     I have encountered (but can't recall where) that the Enum 
constants
        >     >     in a BE protocol were written down in LE notation.
        >     >     Of course the thing can't work then.
        >     > 
        >     >     So if for example you have the constant "1" in a BE 
protocol with a
        >     >     uint 16 enum type, your constant is not 0x0001, but 0x0100 
instead.
        >     > 
        >     >     Chris
        >     > 
        >     > 
        >     > 
        >     > 
        >     >     Am 14.04.20, 12:37 schrieb "Łukasz Dywicki" 
<[email protected]
        >     >     <mailto:[email protected]>>:
        >     > 
        >     >         The legendary "two bytes" (shall we create a band with 
this
        >     >     name?!) are
        >     >         coming from unfortunate State type. I don't mind these 
to be an
        >     >         int/sint/uint or whathever - this is matter of 
interpretation.
        >     > 
        >     >         If you could please check again my earlier messages you 
will find
        >     >         struggle I have which is - how much given type takes.
        >     > 
        >     >         We have that for enums
        >     >         [enum uint 16 little endian 'CommandId']
        >     > 
        >     >         but we don't have that for complex types
        >     >         [type 'State']
        >     > 
        >     >         This leads to situation that we don't know how to read 
and interpret
        >     >         incoming byte sequence or how to properly write it back 
to stream.
        >     > 
        >     >         It would be great if we could limit the issue just to
        >     >         // read
        >     >         state = StateIO.parseStatic(io.readUnsignedInt(16, 
true)); //
        >     >     true->LE
        >     >         // write
        >     >         wio = new WriteBuffer(2);
        >     >         StateIO.staticSerialize(wio, new State(...));
        >     >         io.writeUnsignedInt(8, wio.read, true); // true->LE
        >     > 
        >     >         However to do that first we need to know that State is 
a uint 16
        >     >     LE and
        >     >         then do a lot of mambo-jambo in code generators to cope 
with
        >     >     that. :-)
        >     > 
        >     >         Best,
        >     >         Łukasz
        >     > 
        >     > 
        >     >         On 14.04.2020 12:20, Christofer Dutz wrote:
        >     >         > Oh gee ... I totally remember having exactly the same
        >     >     discussion with Sebastian about "bytes" ...
        >     >         >
        >     >         > The problem is there is generally no "byte" "int" and 
"uint"
        >     >     because a byte = 8 bits is either signed or unsigned. That 
should
        >     >     the 3rd option be? Perhaps-signed?
        >     >         > So generally I use "uint 8" for what you refer to as 
a "byte 8".
        >     >         >
        >     >         > Wo what would be the difference between your "2 byte 
little
        >     >     endian" and an "uint 16" with a LE ReadBuffer?
        >     >         >
        >     >         > I think what you have to rid yourself of thinking of 
int as
        >     >     number and a byte not being a number.
        >     >         >
        >     >         > Chris
        >     >         >
        >     >         >
        >     >         >
        >     >         > Am 14.04.20, 10:52 schrieb "Łukasz Dywicki"
        >     >     <[email protected] <mailto:[email protected]>>:
        >     >         >
        >     >         >     Hey Christian,
        >     >         >     The problem I face is quite simple. State type in 
mspec i
        >     >     declared as a
        >     >         >     bunch of bits. Type length is fixed, however not 
available
        >     >     anywhere in
        >     >         >     mspec or code generator to re-arrange bytes 
upfront. All
        >     >     we have exposed
        >     >         >     at reader/write level is read/write bit.
        >     >         >     To be fair LE/BE support in read/write buffers is 
limited
        >     >     just to
        >     >         >     numbers. There is no such support for raw bytes 
or bits,
        >     >     cause for that
        >     >         >     you need to declare a length of LE/BE sequence.
        >     >         >     
        >     >         >     I would love if I could just declare State as '2 
byte
        >     >     little endian' so
        >     >         >     it would be read properly upfront and parsed with 
no
        >     >     changes in
        >     >         >     generated code, however I'm not sure how to do it 
and
        >     >     where. That's why
        >     >         >     I'm playing with different things described in 
earlier mail.
        >     >         >     Since all type handling is general I am just 
afraid of
        >     >     more complicated
        >     >         >     scenarios where we have variable length 
structures such as
        >     >     arrays.
        >     >         >     
        >     >         >     Best regards,
        >     >         >     Łukasz
        >     >         >     
        >     >         >     
        >     >         >     On 14.04.2020 09:41, Christofer Dutz wrote:
        >     >         >     > Hi Lukasz,
        >     >         >     >
        >     >         >     > I am not sure I am understanding the problems 
you are
        >     >     facing. We already have LE and BE protocols.
        >     >         >     > For example EIP is LE and the rest is generally 
BE. It
        >     >     seems that ADS/AMS is also LE.
        >     >         >     > mspec doesn't even know about endianness.
        >     >         >     >
        >     >         >     > Up till now the endianness doesn't have an 
effect on
        >     >     bit-fields or single-bit ints.
        >     >         >     > It only starts to affect if a field goes from 
one byte
        >     >     to the next, which is usually for (u)int and floating point 
values.
        >     >         >     >
        >     >         >     > That's why we have created the 
Read/WriteBuffers to set
        >     >     their endianness in the constructor.
        >     >         >     >
        >     >         >     > So if you're creating a driver for ADS/AMS 
which is LE,
        >     >     then you write the mspec according to the sequence the 
information
        >     >     is located in the transferred bytes and have the 
Read/WriteBuffer
        >     >     handle the endianness issue.
        >     >         >     >
        >     >         >     > I do see a problem when there are drivers that 
use mixed
        >     >     endianness, but we have still to encounter such a protocol.
        >     >         >     >
        >     >         >     > So I have to admit that I don't like any of the 
mspec
        >     >     changes you proposed, as I think you are just not using the 
tools we
        >     >     have the right way.
        >     >         >     >
        >     >         >     > Chris
        >     >         >     >
        >     >         >     >
        >     >         >     >
        >     >         >     > Am 14.04.20, 00:32 schrieb "Łukasz Dywicki"
        >     >     <[email protected] <mailto:[email protected]>>:
        >     >         >     >
        >     >         >     >     Hey Niclas,
        >     >         >     >     I realized how old the old things are when 
I started
        >     >     preparing
        >     >         >     >     automation training for mere mortals and 
got into
        >     >     history of frames and
        >     >         >     >     even cabling. Mr. Modbus and EIA-485 is 
definitely
        >     >     older than I. ;-)
        >     >         >     >     
        >     >         >     >     Getting back to the point - yes. I been 
thinking how
        >     >     to address the byte
        >     >         >     >     order in effective way. Here are two 
approaches I
        >     >     have for now:
        >     >         >     >     
        >     >         >     >     A) My initial attempt is just a temporary 
buffer
        >     >     which is then written
        >     >         >     >     in reverse order to caller. For reading it 
is
        >     >     similar - just getting N
        >     >         >     >     bytes in reversed order. The hard part is.. 
knowing
        >     >     N. I had to add a
        >     >         >     >     static calculation in order to allocate 
valid buffer
        >     >     sizes. I tend to
        >     >         >     >     work but I'm not happy with this approach 
cause it
        >     >     involves additional work.
        >     >         >     >     B) Second idea I've got is really simple 
and relies
        >     >     on code generation.
        >     >         >     >     We know in which order fields are coming. 
Here I'm
        >     >     referring to a State
        >     >         >     >     field which is just bunch of bits. If we 
would group
        >     >     fields in bytes and
        >     >         >     >     generate code in reverse order then it has 
chance to
        >     >     work. Requirement
        >     >         >     >     for that - ability to know basic field 
sizes upfront.
        >     >         >     >     C) Try to combine above with bit-io or
        >     >     Read/WriteBuffers as these are
        >     >         >     >     places which know actual position and state 
of
        >     >     buffers which are being
        >     >         >     >     read/written.
        >     >         >     >     
        >     >         >     >     Now, getting to two cases which are a 
problem.
        >     >     CommandId and State. So
        >     >         >     >     with command id situation is simple as it is
        >     >     declared as enum and it is
        >     >         >     >     read as uint. We know size upfront and can 
generate
        >     >     valid method call
        >     >         >     >     (readIntLE).
        >     >         >     >     [enum uint 16 little endian 'CommandId'
        >     >         >     >         ['0x00' INVALID]
        >     >         >     >         ['0x01' ADS_READ_DEVICE_INFO]
        >     >         >     >         ['0x02' ADS_READ]
        >     >         >     >         ['0x03' ADS_WRITE]
        >     >         >     >         ['0x04' ADS_READ_STATE]
        >     >         >     >         ['0x05' ADS_WRITE_CONTROL]
        >     >         >     >         ['0x06' ADS_ADD_DEVICE_NOTIFICATION]
        >     >         >     >         ['0x07' ADS_DELETE_DEVICE_NOTIFICATION]
        >     >         >     >         ['0x08' ADS_DEVICE_NOTIFICATION]
        >     >         >     >         ['0x09' ADS_READ_WRITE]
        >     >         >     >     ]
        >     >         >     >     
        >     >         >     >     Second candidate is what I'm stuck right 
now sniping
        >     >     next cycles of
        >     >         >     >     problems. So in case of State we have 
complex type
        >     >     composed from 2
        >     >         >     >     bytes. A note here - instead of two bytes 
we might
        >     >     have a variable
        >     >         >     >     length type which includes array or other 
variable
        >     >     section.
        >     >         >     >     [type little endian 'State'
        >     >         >     >         [simple     bit 'broadcast'             
]
        >     >         >     >         [reserved   int 7 '0x0'                 
]
        >     >         >     >         [simple     bit 'initCommand'           
]
        >     >         >     >         [simple     bit 'updCommand'            
]
        >     >         >     >         [simple     bit 'timestampAdded'        
]
        >     >         >     >         [simple     bit 'highPriorityCommand'   
]
        >     >         >     >         [simple     bit 'systemCommand'         
]
        >     >         >     >         [simple     bit 'adsCommand'            
]
        >     >         >     >         [simple     bit 'noReturn'              
]
        >     >         >     >         [simple     bit 'response'              
]
        >     >         >     >     ]
        >     >         >     >     
        >     >         >     >     The order of reading big endian encoded 
data to
        >     >     impose little endian
        >     >         >     >     shift would be (please correct me if I'm 
wrong):
        >     >         >     >     1) init
        >     >         >     >     2) udp
        >     >         >     >     3) add timestamp
        >     >         >     >     4) priority
        >     >         >     >     5) system
        >     >         >     >     6) ads
        >     >         >     >     7) noreturn
        >     >         >     >     8) response (end of byte 1)
        >     >         >     >     9) broadcast
        >     >         >     >     10) reserved (end of byte )
        >     >         >     >     We can do same trick for writing, by 
re-arranging
        >     >     fields. By this way we
        >     >         >     >     avoid any additional byte level operations.
        >     >         >     >     
        >     >         >     >     Overall trouble with generated driver is to 
declare
        >     >     "how much" bytes
        >     >         >     >     should be read and interpreted. We have 
precise size
        >     >     information at the
        >     >         >     >     runtime - due to length fields, we can 
leverage it
        >     >     at generation time,
        >     >         >     >     but then we won't be able to cover all 
cases.
        >     >         >     >     
        >     >         >     >     I would love to keep it simple and do not 
break
        >     >     things thus I need your
        >     >         >     >     advice on how to approach this problem in a 
valid way.
        >     >         >     >     
        >     >         >     >     Cheers,
        >     >         >     >     Łukasz
        >     >         >     >     
        >     >         >     >     
        >     >         >     >     On 13.04.2020 03:26, Niclas Hedhman wrote:
        >     >         >     >     > <anecdotal-rant>
        >     >         >     >     > For us who were around and shaping the 
protocols
        >     >     in the 1980s, and people
        >     >         >     >     > before us (and before standards like 
RS-232), a
        >     >     lot of the "specifications"
        >     >         >     >     > came out of "observation of 
implementation we
        >     >     managed to get to work",
        >     >         >     >     > rather than "implement this spec". A lot 
was due
        >     >     to extreme memory
        >     >         >     >     > constraints (in my case, multi-tasking 
operating
        >     >     system, serial protocol
        >     >         >     >     > 187kbps, interpreted programming language 
with
        >     >     floating point ops and user
        >     >         >     >     > applications in 2kB RAM and 8kB EPROM) 
and a
        >     >     general lack of information,
        >     >         >     >     > like what other people were doing, sharing
        >     >     experiences and so on.
        >     >         >     >     >
        >     >         >     >     > And there were many "innovative" ways to 
squeeze
        >     >     just a little bit extra
        >     >         >     >     > out of the hardware, resulting in "hard to
        >     >     understand" consequences. Bit
        >     >         >     >     > packing was a typical one, multiple 
functions
        >     >     packed into a single byte.
        >     >         >     >     > Look at page 14 in
        >     >     https://www.nxp.com/docs/en/data-sheet/80C31_80C32.pdf
        >     >         >     >     > and read up on "UART Enahanced Mode", and 
we used
        >     >     this, i.e. 9 bits, no
        >     >         >     >     > parity and clever use of address and mask 
to
        >     >     create a slave-to-slave direct
        >     >         >     >     > protocol, where the master's role was to 
signal
        >     >     which slave "owned" the
        >     >         >     >     > cable. Yeah, in that 8kB ROM limitation 
(I think
        >     >     protocol was about 1kB
        >     >         >     >     > ROM) and something like 150 bytes RAM for 
comm
        >     >     protocol.
        >     >         >     >     >
        >     >         >     >     > Could you implement a compatible device 
to this
        >     >     with PLC4X and modern
        >     >         >     >     > hardware (i.e. no 8031/32 co-processor)? 
Possibly
        >     >     but bit-banging is needed
        >     >         >     >     > to support the 9bit data (+start and stop 
bits)
        >     >     and an awful lot of CPU
        >     >         >     >     > cycles on something that was automatic on 
one of
        >     >     the slowest long-lived
        >     >         >     >     > microcontroller ever.
        >     >         >     >     > </anecdotal-rant>
        >     >         >     >     >
        >     >         >     >     > My point was only to highlight that some 
of the
        >     >     strange things you see in
        >     >         >     >     > protocols today, have its roots in
        >     >     pre-standardization days. Today no one
        >     >         >     >     > would go down that route, because the 
hardware
        >     >     cost nothing now (8031  +
        >     >         >     >     > 8kB EPROM + 2kB static RAM + battery 
backup =>
        >     >     ~$50 in 1983's currency) and
        >     >         >     >     > longevity of software is more important.
        >     >         >     >     >
        >     >         >     >     > Cheers
        >     >         >     >     > Niclas
        >     >         >     >     >
        >     >         >     >     >
        >     >         >     >     > On Sun, Apr 12, 2020 at 10:10 PM 
Christofer Dutz
        >     >     <[email protected] 
<mailto:[email protected]>>
        >     >         >     >     > wrote:
        >     >         >     >     >
        >     >         >     >     >> Hi Lukasz,
        >     >         >     >     >>
        >     >         >     >     >> I think it really gets tricky when using 
BE and
        >     >     having some byte-odd-sizes
        >     >         >     >     >> ... I remember in the Firmata protocol 
there were
        >     >     some bitmasks and then 10
        >     >         >     >     >> bit uint as BE ... not it really got 
tricky as
        >     >     the specs were written from
        >     >         >     >     >> a point of view: You read 16 bits BE and 
then the
        >     >     first6 bits mean XYZ
        >     >         >     >     >> instead of describing how the bits 
actually
        >     >     travel over the wire.
        >     >         >     >     >>
        >     >         >     >     >> Chris
        >     >         >     >     >>
        >     >         >     >     >>
        >     >         >     >     >>
        >     >         >     >     >> Am 11.04.20, 01:21 schrieb "Łukasz 
Dywicki"
        >     >     <[email protected] <mailto:[email protected]>>:
        >     >         >     >     >>
        >     >         >     >     >>     I've made some progress with topic by
        >     >     modyfing mspec and allowing
        >     >         >     >     >>     'little endian' flag on fields. This 
moved me
        >     >     further to next issue -
        >     >         >     >     >>     which is whole type encoded little 
endian.
        >     >         >     >     >>
        >     >         >     >     >>     In ADS driver such type is State, 
which has 2
        >     >     bytes and uses 8 bits for
        >     >         >     >     >>     various flags.
        >     >         >     >     >>     There are two cases which require 
different
        >     >     approach - reading and
        >     >         >     >     >>     writing. So for reading we need to 
swap N
        >     >     bytes based on type length.
        >     >         >     >     >>     For writing we need to alocate 
buffer for N
        >     >     bytes and swap them before
        >     >         >     >     >>     writing.
        >     >         >     >     >>
        >     >         >     >     >>     I am stuck now with freemaker 
templates and
        >     >     bit-io.
        >     >         >     >     >>
        >     >         >     >     >>     Cheers,
        >     >         >     >     >>     Łukasz
        >     >         >     >     >>
        >     >         >     >     >>
        >     >         >     >     >>
        >     >         >     >     >>     On 10.04.2020 17:57, Łukasz Dywicki 
wrote:
        >     >         >     >     >>     > I am doing some tests of ADS 
serialization.
        >     >         >     >     >>     >
        >     >         >     >     >>     > I've run into some troubles with 
payload
        >     >     which is generated with new
        >     >         >     >     >>     > driver. I'm not sure if that's my 
fault or
        >     >     generated code.
        >     >         >     >     >>     >
        >     >         >     >     >>     > I did a verification of what 
Wireshark
        >     >     shows and how ads structures
        >     >         >     >     >> are
        >     >         >     >     >>     > parsed. There is a gap I think. 
For example
        >     >     ams port number 1000
        >     >         >     >     >>     > (0x1027) is read as 4135.
        >     >         >     >     >>     >
        >     >         >     >     >>     > Obviously I used wrong structures 
while
        >     >     implementing protocol logic
        >     >         >     >     >> in
        >     >         >     >     >>     > first place, but now I am 
uncertain of how
        >     >     fields are encoded. How we
        >     >         >     >     >>     > mark field as little endian when 
rest of
        >     >     payload is big endian? Do we
        >     >         >     >     >>     > have `uint_le`?
        >     >         >     >     >>     >
        >     >         >     >     >>     > As far I remember route creation 
logic I
        >     >     was tracking last week used
        >     >         >     >     >>     > combination of LE and BE.
        >     >         >     >     >>     >
        >     >         >     >     >>     > Best regards,
        >     >         >     >     >>     > Łukasz
        >     >         >     >     >>     >
        >     >         >     >     >>
        >     >         >     >     >>
        >     >         >     >     >>
        >     >         >     >     >
        >     >         >     >     
        >     >         >     >
        >     >         >     
        >     >         >
        >     > 
        >     
        > 


Reply via email to