Thinking of it, maybe it would be better to extend signature of subscription inquiry to be isSubscriptionSupported(PlcTag) ? My motivation for this is rather basic - the BACnet stuff which is on the way will have per-participant subscriptions. Profinet (I suppose) is same for cyclic/acyclic subscriptions and so on. This gives driver opportunity to make smarter decision. Obviously for point to point connection such S7-TCP we can rely on device type negotiated earlier, *but* spanning further, we could finally let S7-1200 subscriptions only for MODE events.

Cheers,
Łukasz

On 13.03.2024 21:16, Christofer Dutz wrote:
Changing the title ….

So, I just updated the S7 driver to no longer simply report true on 
“isSubscriptionSupported()” and it now only reports “true”, if it’s a S7-300 or 
S7-400.
If there is more, that needs to be enabled in order to support subscriptions on 
such a device, it would be cool, if we could detect that during the connection 
process and report accordingly.

Chris


Von: Cesar Garcia <[email protected]>
Datum: Mittwoch, 13. März 2024 um 21:12
An: [email protected] <[email protected]>
Betreff: Re: Board report ....
Hello Chris,

The S7-300/S7-400 devices have an important group of functions for event
handling. In the process part (PCS7) this is handled intensively.

At the time, all these operations are on the Tag associated with the
request, so any service type subscription is a subscription to events.

In general the S7-300/S7-400 support;

    - *MODE*: Change of operating state in the controller, change from STOP
    to RUN and vice versa.
    - *SYS*: System events, associated with internal events of the
    controller or events previously parameterized for their indication.
    - *USR*: Events programmed by the user and that are registered in the
    internal diagnostic buffer.
    - *ALM*: Alarm events generated by the user program, ALARM_S, ALARM_8,
    NOTIFY.
    - And additionally "*CYC*" cyclic mode transfer.


But in general they are all seen as events, hence the inconsistency pointed
out by Bjorn.

All these events are implemented, of course, they have many points of
improvement that must be addressed.

I currently do not have a PN or CP-343-1 CPU for testing with S7-300.

As you point out, with Zylk's contribution it can complement the CP-443-1
for redudance tests (thanks Zylk).

Well, the story is long... I'm going for a good coffee.

Kind regards,

El mié, 13 mar 2024 a las 14:57, Christofer Dutz (<[email protected]>)
escribió:

Hi Björn,

the problem with the subscriptions in S7 are that they do work, but only
on S7 300 (I think).
I mentioned before on this list, that we should probably do
context-sensitive “isXYZSupported” functions.
Unfortunately, I haven’t yet had the time to implement them.

So, to make it short … in general the S7 protocol doesn’t support
subscriptions, except for a small subset of device types.
If Cesar could possibly tell me which devices support Subscriptions, I
could implement something to make this happen (Shouldn’t be too much work).

One day we’ll probably have simulated subscriptions, but admittedly as
nobody really seems to be interested in working on core-services like this,
it’s probably gonna take a while.
In the past I was able to work on PLC4X full time, but as no company
(except Zylk) was really willing to pay for any form of development, I had
to pick a job that pays the bills.
I’m still on it, but doing this in my free time.

Chris

Von: Björn Haverland <[email protected]>
Datum: Mittwoch, 13. März 2024 um 18:52
An: [email protected] <[email protected]>
Betreff: Re: Board report ....
Hi,

as I'm starting to get used to the project I do have some questions,
especially regarding the mentioned v1.0.0.

I tried to set up a plc4j with the quickstart guide which utilizes the S7
protocol.

So there are examples, in the example folder as well, which are just not
working. (The Subscription for instance) I do understand that the lib
hasn't had a Major release yet, but I think it could set people off.

I like to suggest to change the docs on that points. I know it is hard to
test everything but if a feature isn't implemented a wrong documentation
just leads to frustration.
Cesar has implemented a working CyclicSubscription, and I think he is
going to merge it to the dev branch soon. But still there are other
subscription methods shown which won't work, just yet.

I'd like to hear your opinion on this.

Best regards

Bjoern



Gesendet von Outlook für Android<https://aka.ms/AAb9ysg>
________________________________
From: Christofer Dutz <[email protected]>
Sent: Wednesday, March 13, 2024 12:00:11 PM
To: [email protected] <[email protected]>
Subject: Board report ....

Hi all,

unfortunately I had almost forgotten to submit the board report after
coming back from my little snowboard vacation.
I took the liberty of posting the following report. If there are changes
you’d like to see, please tell me asap and I can edit it.



## Description:
The mission of the Apache PLC4X project is creating a set of libraries for
communicating with industrial programmable logic controllers (PLCs) using a
variety of protocols but with a shared API.

## Project Status:
Current project status: Ongoing with moderate activity
Issues for the board: None

## Membership Data:
Apache PLC4X was founded 2019-04-17 (5 years ago)
There are currently 21 committers and 13 PMC members in this project.
The Committer-to-PMC ratio is roughly 3:2.

Community changes, past quarter:
- No new PMC members. Last addition was César García on 2021-10-01.
- No new committers. Last addition was Jinlin Hong on 2022-11-02.

## Project Activity:
Version 0.12.0 was released on 2024-02-19

The project has been working on closing many issues this quarter.
We were able to cut the number of open issues by half. Also did we
invest a considerable amount of time for working towards reproducible
builds and automating most of the release process. Also did we update
the content on the website, especially thanks to a new documentation-
generator now the configuration for our drivers is automatically going
to be up to date.

## Community Health:
We know we haven't invited any new committers for quite some time.
This is definitely not due to a high committer bar, but more related
to the fact that the people needing Apache PLC4X seem to come from a
part of the industry that is completely new to the concept of open-source.

Only very few people accept our offer to mentor them to scratching their
own itches.

Interestingly the project is gaining more and more popularity on the user-
side.

Activity on the mailing lists seems to have increased slightly (8% - 605
emails)

The community is looking forward to a community meetup in Frankfurt the
weekend after the board meeting. Here we hope to re-ignite some of the
community activity and focus on perhaps releasing a 1.0.0 version of
PLC4X this year.



--
*CEOS Automatización, C.A.*
*GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
*PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*

*FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
*Ing. César García*

*Cel: +58 414-760.98.95*

*Hotline Técnica SIEMENS: 0800 1005080*

*Email: [email protected]
<[email protected]>*

Reply via email to