On Mon,9/28/2015 11:26 AM, Kenneth Talbott wrote:
Several years ago the NEC relaxed the requirement that safety ground and
neutral be connected at only one place. Now you may leave the bonding screw
in place in remote panels.
http://ecmweb.com/code-basics/grounding-and-bonding-part-2-3
The link above is from Mike Holt, widely considered an authority on
electrical codes. He makes his living teaching and writing about the
topic. This is part of his review of revisions to Article 250, Grounding
and Bonding, that appeared in the 2011 code. In the very last paragraph,
are these words:
"As a rule, the neutral should never be connected to the enclosure or
equipment grounding conductor anywhere except in the service disconnects
and the secondary side of separately derived systems. Objectionable
neutral current presents a real danger and can damage equipment as well
as cause fires and electric shock or electrocution."
For all practical purposes, the 2011 code is the most recent, because it
usually takes 5-6 years for local authorities to adopt a revision. Upon
reading your email, I reviewed a draft of the 2014 code, and the
requirement for one, and only one, neutral to ground bond is still part
of it.
The only "remote panel" in which a bond would be permitted between
neutral and ground is one in a second building where ground is not
carried between buildings, or when the remote panel is for a "separately
derived system." A system is separately derived when fed by a
transformer. The practice of not carrying ground between buildings no
longer permitted, but is grandfathered in existing installations from
earlier versions of NEC.
73, Jim K9YC
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net
This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com