Yes NEC 2008 250.32B EXCEPTION is that to which I refer

When the debate is lost, slander becomes the tool of the loser.   Socrates


-----Original Message-----
From: elecraft-boun...@mailman.qth.net
[mailto:elecraft-boun...@mailman.qth.net] On Behalf Of Jim Brown
Sent: Monday, September 28, 2015 5:30 PM
To: Reflector Elecraft
Subject: Re: [Elecraft] Grounding

On Mon,9/28/2015 11:26 AM, Kenneth Talbott wrote:
> Several years ago the NEC relaxed the requirement that safety ground 
> and neutral be connected at only one place.  Now you may leave the 
> bonding screw in place in remote panels.

http://ecmweb.com/code-basics/grounding-and-bonding-part-2-3

The link above is from Mike Holt, widely considered an authority on
electrical codes. He makes his living teaching and writing about the topic.
This is part of his review of revisions to Article 250, Grounding and
Bonding, that appeared in the 2011 code. In the very last paragraph, are
these words:

"As a rule, the neutral should never be connected to the enclosure or
equipment grounding conductor anywhere except in the service disconnects and
the secondary side of separately derived systems. Objectionable neutral
current presents a real danger and can damage equipment as well as cause
fires and electric shock or electrocution."

For all practical purposes, the 2011 code is the most recent, because it
usually takes 5-6 years for local authorities to adopt a revision.  Upon
reading your email, I reviewed a draft of the 2014 code, and the requirement
for one, and only one, neutral to ground bond is still part of it.

The only "remote panel" in which a bond would be permitted between neutral
and ground is one in a second building where ground is not carried between
buildings, or when the remote panel is for a "separately derived system." A
system is separately derived when fed by a transformer. The practice of not
carrying ground between buildings no longer permitted, but is grandfathered
in existing installations from earlier versions of NEC.

73, Jim K9YC

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html Message
delivered to ktalb...@gamewood.net

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

Reply via email to