Dear Don,

This leaves me a bit concerned.  I am planning to put up a K9AY 
receiving antenna in my backyard and it is supposed to be connected 
to a ground rod.  I had never seen it suggested that this must be 
connected to the utility ground stake.  I'm not even sure where the 
utility ground stake is.  I've never noticed one though I will ask my 
electrician.  If there is one, it is likely to be pretty far from the K9AY.

73,

Dick, KA1SA

At 10:22 PM 1/20/2010, Don Wilhelm wrote:
>Joe,
>
>That is *one* reason *any* ground rod should be tied back to the utility
>ground stake.  It is as requirement of NEC, and should not be ignored.
>If you drive ground rods for the ham station, connect those ground rods
>to the utility entrance ground rod - no exceptions.  The ideal is #6 or
>larger wire, but if you cannot do that use whatever wire you can.  Your
>safety depends on it.  If you cannot connect extra ground rods to the AC
>mains entry ground, then do not drive those extra ground rods - they are
>*not* an RF ground (see my many posts in the archives on that topic) -
>and as Joe points out, in the event of a lightning strike (or equipment
>fault), they may create a dangerous condition.
>
>You have 3 "grounds" to consider in the hamshack - 1) The AC safety
>ground,  2) The lightning path ground, and 3) The RF ground.
>1) and 2) may be one and the same, but 3) is a "horse of a different
>color", and has nothing to do with a "mother earth" ground - it is a
>point of low impedance at the frequency of interest, and usually exists
>at some point in the antenna system, quite apart from "mother earth".
>The English folks have the language a bit better and refer to "earthing"
>which is often apart from "grounding", but we here in the US use the
>same term for all common connections and in the process create confusion
>for ourselves.
>
>73,
>Don W3FPR
>
>Joe Subich, W4TV wrote:
> > This creates a situation that is potentially hazardous
> > to your equipment.  The AC "third (green) wire" is supposed
> > to be connected to ground only at the main panel/service
> > entrance.  However, since it is connected to the chassis
> > of the power supply, it is also connected through the power
> > supply and radio to ground via the coaxial cable.
> >
> > If the point at which the coaxial cables enter the building
> > is not the same place that power enters the building, any
> > nearby lightning strike can set up a significant difference
> > in voltage between the power line "safety ground" and the
> > RF ground (feedline shields/tower).  That difference can
> > fry any electronics connected to both "grounds."
> >
> > There are techniques for dealing with this problem ... but
> > they are not necessarily easy or inexpensive.
> >
> > 73,
> >
> >    ... Joe, W4TV
> >
> >
> >
> >
> >
> >
> >> -----Original Message-----
> >> From: elecraft-boun...@mailman.qth.net
> >> [mailto:elecraft-boun...@mailman.qth.net] On Behalf Of Don Wilhelm
> >> Sent: Wednesday, January 20, 2010 8:01 PM
> >> To: David Woolley (E.L)
> >> Cc: Rich; elecraft@mailman.qth.net
> >> Subject: Re: [Elecraft] Grounding negative side of power supply?
> >>
> >>
> >> The AC side should always be connected to the power supply chassis -
> >> unless it is of the "double insulated" design where no ungrounded
> >> metallic part can come into contact with the human body.
> >> Yes, cutting
> >> the AC "green wire ground" is a dangerous thing indeed - the entire
> >> chassis could rise to the AC mains voltage in the event of a fault.
> >>
> >> The power supply negative *can* certainly be floating *if*
> >> the designer
> >> made provisions for doing that.  It requires that all the common
> >> connections on the secondary side of the transformer are
> >> isolated from
> >> ground.  As I recall, Astrons are not built that way.
> >>
> >> 73,
> >> Don W3FPR
> >>
> >> David Woolley (E.L) wrote:
> >>
> >>> Rich wrote:
> >>>
> >>>
> >>>> I had a situation with an older (analog) power supply
> >>>>
> >> (that had its
> >>
> >>>> negative side grounded to the main AC ground) that tripped
> >>>>
> >> the Ground
> >>
> >>>> Fault Circuit Interrupter (GFCI) in one of the bathrooms.
> >>>> Eliminating the bond to ground
> >>>>
> >>>>
> >>> I consider this dangerous advice.  If you have an ELCB
> >>>
> >> tripping, you
> >>
> >>> do
> >>> not treat the problem symptomatically, by creating an
> >>>
> >> unsafer system,
> >>
> >>> you find out what the real problem is and you fix it.
> >>>
> >>> I can't tell what the exact wiring configuration is here, but it is
> >>> very
> >>> likely that you have created a situation where there are
> >>>
> >> pieces of metal
> >>
> >>> in reach which have low impedance paths to very different "earths".
> >>>
> >>>
> >>>
> >> ______________________________________________________________
> >> Elecraft mailing list
> >> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> >> Help: http://mailman.qth.net/mmfaq.htm
> >> Post: mailto:Elecraft@mailman.qth.net
> >>
> >> This list hosted by: http://www.qsl.net
> >> Please help support this email list: http://www.qsl.net/donate.html
> >>
> >
> > ______________________________________________________________
> > Elecraft mailing list
> > Home: http://mailman.qth.net/mailman/listinfo/elecraft
> > Help: http://mailman.qth.net/mmfaq.htm
> > Post: mailto:Elecraft@mailman.qth.net
> >
> > This list hosted by: http://www.qsl.net
> > Please help support this email list: http://www.qsl.net/donate.html
> > ------------------------------------------------------------------------
> >
> >
> > No virus found in this incoming message.
> > Checked by AVG - www.avg.com
> > Version: 9.0.730 / Virus Database: 271.1.1/2634 - Release Date: 
> 01/20/10 04:12:00
> >
> >
>______________________________________________________________
>Elecraft mailing list
>Home: http://mailman.qth.net/mailman/listinfo/elecraft
>Help: http://mailman.qth.net/mmfaq.htm
>Post: mailto:Elecraft@mailman.qth.net
>
>This list hosted by: http://www.qsl.net
>Please help support this email list: http://www.qsl.net/donate.html

==================================================
  Richard S. Lindzen
  Alfred P. Sloan Professor of Atmospheric 
Sciences 

  Office: 54-1720, MIT
          Cambridge, MA 02139 USA
          1 (617) 253-2432 (voice)
          1 (617) 253-6208 (fax)

  Temporary Home: 100 Memorial Drive
                             Apt. 2-2a
                           Cambridge, MA 02142 USA
                           1 (617) 945-5784 (voice)
================================================== 

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html

Reply via email to