Hi Rick, I've been the same similar situation. I lost. Your eletronegativities with the material you've mentioned are ok. I lost to internal toothed washers. The inspector wanted EXTERNAL toothed washers. That insured seeing a toothed washer during inspection. I managed to get by without any special coatings. We had some paint over the whatever plating was being used. I also lost to just a wire from here to there. Had to heatshrink it to avoid ANY possible abrasion of the insulation. Someone mentioned torquing the nuts. Good point.
Talk about a simplicity being converted to complexity. Make sure that this is the ONLY issue with this guy. Sounds like the guy I had. He went one issue at a time. Sorry to be so negative. Regards ... Doug bcoll...@gmicolor.com wrote: > > Rick Busche wrote: > > I have a projector assembly which is essentially a large metal > structure (frame) with a metal projector platform which swivels for > purposes of maintenance. The structure is painted steel, with pressed > in bronze bushings at all motion points each of which have been > measured at significantly less than 0.10 ohms. Arguably, there is no > guarantee that these structures will remain bonded at these levels > over time and bonding wires (braid, with crimped ring lugs) have been > added across the pivot points. These wires are secured to the > structure using a toothed washer and screw. The intent of the toothed > washer is to bight through the paint to ensure conductivity. > My customer's safety officer (in Europe) is now insisting that the > paint must be ground off to bare metal and coated with Zinc paint > prior to affixing the lug to the structure. I am concerned that this > is an excessive requirement. It has been my understanding that the > toothed washer (and the screw for that matter) creates a gas tight > connection which is acceptable for all bonding requirements. > I would be interested in hearing from the group regarding this bonding > issue. I can find no standard or specification which disallows this > biting washer or requires Zinc paint. > Any comments would be appreciated. > Rick Busche > rbus...@es.com > > Reply: > > You may have already thought of this but... > > My approach to this kind of requirement is to respectfully ask the > customer to cite the language in the standard that requires this > construction. If they are unable to provide this reference, I would ask > if they have a specific requirement for this construction method other > than a standard. If they still cannot supply you with a good reason, I > would have to say that you can decline their request. > > Bear in mind that these folks are your customer and this may be an > unspoken expectation on their part. If it is something they are willing > to pay for and you can charge them for it, it may be desirable to do. > > I learned long ago that if I cannot cite the standard that is the basis > for my requirement (or finding in the case of auditing), I don't insist > on having it my way. > > Regards > Bob Collier > Graphics Microsystems > bcoll...@gmicolor.com > Nobody pays me for these opinions, perhaps there is a reason... -- ************************************************************ ------------------------------------------------------------ The comments and opinions stated herein are mine alone, and do not reflect those of my employer. ------------------------------------------------------------ ************************************************************