Hello from San Diego:


As a general rule, products powered from a (NEC, CEC)
Class 2, (IEC) SELV, or battery power source need 
not be certified for safety.  The general rule (e.g.,
NEC, LVD, et al) exempts products operating at ELV, 
e.g., 50 volts or less.  

(As near as I can tell, the NEC does not specifically 
exempt Class 2 devices from "listing," but does by
implication.  The LVD specifically exempts products
operating at 50 volts and less.)

The NEC Class 2 designation originally included 
household doorbell circuits.  Doorbells are not
certified for safety.

Back in the days when independent third-party 
certifiers were near-monopolies, the third-parties
were very busy.  They would turn down or discourage
applications for low-voltage product certifications
-- because such certifications were not required 
under the regulations.

Today, third-party certifiers are jumping at every
chance to earn money.  They are happy to take our
money to certify low-voltage products that are 
technically exempt from certification under the
applicable regulations.  After all, the customer
knows best!

So, the answer you get when you ask a third-party
certifier will depend on how busy he is at the 
moment you ask him!  

But, the answer really comes from the regulations
that require certification.  In most countries and
jurisdictions, low-voltage products are exempt from
safety certification.

However, IEC 950 and its clones are a different 
matter.  Slowly, TC 74 is adding more and more safety
requirements for low-voltage products.  It will be
interesting to see if the various regulations will 
pick up on this and begin requiring safety certification
for low-voltage products within the scope of IEC 950.
 
Regarding batteries... yes, most batteries exceed the
"limited power" criteria in IEC 950.  Most batteries
should be fused.


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                      Product Safety Engineer
 Hewlett-Packard Company           Product Regulations Group 
 All-In-One Division               Tel   :   +1 619 655 3329 
 16399 West Bernardo Drive         FAX   :   +1 619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------






---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to