Sorry to add to the confusion, but the British trade 
association FEI publishes a document on periodic 
safety checks for business equipment, which includes 
a table of conductor sizes and fuse sizes
for British plugs, with the following note:
"BS 1363 specifies only the use of 3 A or 13 A fuses. 
Conditions applicable to using a 5 A fuse with a 0.5 mm2 
conductor are given in BS 1363."

This seems to tie up with my (old) copy of BS1363, 
which specifies a 3A fuse for 0.5mm2 cord, and a 13A fuse 
for 0.75, 1.00, 1.25 and 1.50 mm2 cords. 
Adjacent to the 3A fuse rating for 0.5 mm2 cord is (5);
with a note that "the figure in brackets indicates the fuse
rating where a non-rewirable plug/cord assy is used
with certain types of equipment where the use of a 5A
fuse link is necessary because of the high instantaneous
input current".

If anyone has the latest version of BS 1363:1984, or 
BS 1363:Part 1:1995, they could confirm the above.
I note that in the BSI catalogue, under the entry for 
BS 1362 (fuses for BS 1363 plugs), it states 
"for use in plugs complying with BS 1363, the preferred
current ratings are 3A and 13A. 
John Crabb, Development Excellence (Product Safety) ,     
NCR  Financial Solutions Group Ltd.,  Kingsway West, Dundee, Scotland. DD2
3XX
E-Mail :john.cr...@scotland.ncr.com
Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.   VoicePlus
6-341-2289.


> -----Original Message-----
> From: Chris Duprés [SMTP:chris_dup...@compuserve.com]
> Sent: 17 November 1999 23:36
> To:   Laura Leyba-Newton
> Cc:   emc-pstc
> Subject:      RE: internet information
> 
> 
> Hi Laura.
> 
> You mention wire type:
> <HO3VVF3G0.75>
> 
> This looks like 0.75mm2 cross section area cable, and should be protected
> by a 5A fuse.
> 
> Chris Duprés
> Surrey, UK.
> 

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).