At 09:31 29/10/01 -0000, John Crabb wrote:
>
>IEC60950 requires that capacitor exceeding 0.1uF should have a means of
>discharge resulting
>in a time constant not exceeding 1 second for pluggable equipment Type A.


".. a means of discharge"

As I understand it there is no need to blindly install a resistor. 
Depending on the product, it may discharge the filter caps.

This is how I test when the need arises:

Hook up a relay normally closed, providing power to your appliance.
Connect one input of your scope (battery powered scope is best)
as the trigger on the relay coil. Connect the other input in voltage
capture mode across the appliance terminals. When you open the relay, the
second 
input is triggered by the first input and captures the residual voltage
across the appliance filter.
(in reality you see a few mains cycles as well due to the operating time of 
the relay)

You will also need a small dc supply for the relay.

Repeat the test about 50 times and if you have a good portable scope you
should be
able to print off the discharge waveform and stick it in the design file. 

Cheap. :)

Enci


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to