Oops - wrong short circuit test - just realized. Sorry about that. My mind
is occupied by that one currently...

The on-board short-circuit test is to simulate a short occurring for
whatever reason (manufacturing defect, design defect, operational fault).
Since something bad happened, in my opinion the card is allowed to fail as
long as it fails safe. Opening a fuse is certainly an acceptable method to
remove the electrical safety hazard.

...Marko

-----Original Message-----
From: Marko Radojicic 
Sent: Monday, November 25, 2002 11:14 AM
To: 'j...@aol.com'; emc-p...@majordomo.ieee.org; t...@world.std.com
Subject: RE: Short circuit tests in GR-1089


Joe,

The short-circuit test is to simulate the most prevalent source of telecom
disruption: the back-hoe.

When a buried cable is inadvertently cut, the pairs could short together or
to the cable sheath. I really can't see how a test lab can misinterpret the
requirement (R4-6 for telecom ports). It clearly states that replacing fuses
is not an allowable situation.

"The EUT shall not be damaged, shall not require manual intervention (such
as to reset circuit breaker or replace fuses) to restore service, and shall
not become a fire, fragmentation, or electrical safety hazard as a result of
the application of a short circuit ..."

I'm quite sure that whomever you spoke with at the test lab is in error and
will probably reconsider their position if they read the standard a little
more carefully.

Cheers,
Marko

Marko Radojicic
Manager, Compliance and Reliability
Turnstone Networks, inc.
2220 Central Expressway
Santa Clara, CA
95050

mar...@turnstone.com
408/907-1739



-----Original Message-----
From: j...@aol.com [mailto:j...@aol.com]
Sent: Monday, November 25, 2002 10:25 AM
To: emc-p...@majordomo.ieee.org; t...@world.std.com
Subject: Short circuit tests in GR-1089


Hello All:

I am hoping that some of you can help clarify the intent of requirement
R9-20 
in Telcordia GR-1089.  Taken literally, the requirement says that there
shall 
be no damage to equipment, conductors, or components when the DC power
supply 
is shorted at the load.  This could even be interpreted to preclude the use 
of a fuse that has to be replaced.

One test lab has told me that as long as no fire hazard is created from this

test, it is considered to have been passed.  Needless to say, this differs a

bit from the literal interpretation.

I guess it would help if I had a better feel for the overall goal of the 
short circuit testing.  Any insight on this would be most appreciated.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848
http://www.randolph-telecom.com