Do you have the liberty to share your report - or details and results with
the group?

                        - Robert -

       Robert A. Macy, PE    m...@california.com
       408 286 3985              fx 408 297 9121
       AJM International Electronics Consultants
       101 E San Fernando, Suite 402
       San Jose, CA  95112


----- Original Message -----
From: "Spencer, David H" <david.spen...@usa.xerox.com>
To: <emc-p...@majordomo.ieee.org>
Sent: Wednesday, October 30, 2002 8:57 AM
Subject: RE: Measuring AC Line Impedance


>
> Follow up............................
>
> Having just completed an ton of work on this using input I got around here
> (thanks to Don Borowski, Patrick Lawler, Joe Randolph and  John Woodgate).
> I believe we have characterized the AC mains of our facility.
>
> As a sanity check/ technical check can any one comment on process.
>
> Part one
> 1)Open circuit voltage measured.
> 2)Resistive load placed in circuit.
> 3) Voltage drop and current measured.
> 4) Voltage drop divided by current provides  resistance component of AC
> mains.
>
> Part 2
> 1) Open circuit voltage measured.
> 2)Reactive load placed in circuit (approximately 120uF!)
> 3) Voltage change (increase really) and current measured (phase angle was
> recorded to back check math vectorialy).
> 4) Voltage change divided by current provides reactive component of AC
> mains.
>
>
> As a side note, I also connected an isolation transformer as the reactive
> load,  the reactive numbers were very very close.
>
> The resistive number + reactive number then make up the AC line impedance
> for this site:  Ztest if you will.
>
>
>
> My two remaining questions:
>
> Is this method of characterizing the AC line impedance valid (is there
> something I'm missing)?
>
> Based on my knowledge of these values, and their ratio to the reference
> impedance(s) specified in EN61000-3-3 and EN61000-3-11, I should be able
to
> calculate and correlate the measured Dmax, Pst, et. al...to the limits
> specified in those standards.
> (REFERENCE section 6.1.3 of EN61000-3-11), using our existing AC mains.
>
>
> Any comments or input would be welcome.
> Thanks
>
> Regards
> David Spencer
> Xerox Corp.
>
>
> -----Original Message-----
> From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
> Sent: Thursday, September 19, 2002 11:56 AM
> To: emc-p...@majordomo.ieee.org
> Subject: Re: Measuring AC Line Impedance
>
>
>
> I read in !emc-pstc that Spencer, David H <david.spen...@usa.xerox.com>
> wrote (in <052106A55179D611B34300096BB02E3F8B1D@USAMCMS4>) about
> 'Measuring AC Line Impedance' on Thu, 19 Sep 2002:
>
> >Is anyone familiar with a method to measure and calculate those values.
> The
> >generic values I have for short circuit condition (which include 4 wires
in
> >a magnetic conduit) come out higher than my measured values, and those do
> >not include the motor generator source.
>
> Put a large capacitor (mains voltage rated) across the mains and measure
> the voltage change; it may actually increase. You need about 50 uF to
> get a decent change on 120 V 60 Hz mains. With that result and the one
> with the resistive load, you can calculate the source impedance as an R
> and L in series.
>
> I'd be interested to learn the result.
> --
> Regards, John Woodgate, OOO - Own Opinions Only.
http://www.jmwa.demon.co.uk
>
> Interested in professional sound reinforcement and distribution? Then go
to
> http://www.isce.org.uk
> PLEASE do NOT copy news posts to me by E-MAIL!
>
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
>
> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>
> To cancel your subscription, send mail to:
>      majord...@ieee.org
> with the single line:
>      unsubscribe emc-pstc
>
> For help, send mail to the list administrators:
>      Ron Pickard:              emc-p...@hypercom.com
>      Dave Heald:               davehe...@attbi.com
>
> For policy questions, send mail to:
>      Richard Nute:           ri...@ieee.org
>      Jim Bacher:             j.bac...@ieee.org
>
> All emc-pstc postings are archived and searchable on the web at:
>     http://ieeepstc.mindcruiser.com/
>     Click on "browse" and then "emc-pstc mailing list"
>
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
>
> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>
> To cancel your subscription, send mail to:
>      majord...@ieee.org
> with the single line:
>      unsubscribe emc-pstc
>
> For help, send mail to the list administrators:
>      Ron Pickard:              emc-p...@hypercom.com
>      Dave Heald:               davehe...@attbi.com
>
> For policy questions, send mail to:
>      Richard Nute:           ri...@ieee.org
>      Jim Bacher:             j.bac...@ieee.org
>
> All emc-pstc postings are archived and searchable on the web at:
>     http://ieeepstc.mindcruiser.com/
>     Click on "browse" and then "emc-pstc mailing list"


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to