> I am interested
>to know what the actual magnitude of ground differences may be from one end
>of a plant to another as well as where the numbers come from.  

It depends on what sort of equipment is present. Some things have very
high leakage current, putting a lot of amps in total into ground
conductors. Then, in old plants, there may be bad ground wiring that
doesn't show up as a fault.

>Have they
>been calculated or actually measured? 

Both. Usually after the problem has been discovered by chance. I've
measured 9 V over a distance of 20 m, but there are reports of much
higher voltages.

>If shields are connected directly to
>chassis at each node of a network will there be an effect of equalizing the
>ground levels through the network or will enough current flow to melt the
>shield of the cable?

Both are possible.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to