I read in !emc-pstc that richhug...@aol.com wrote (in <44E75E95.7A170092
.0ba45...@aol.com>) about 'Dielectric withstand voltage for power
supplies' on Thu, 26 Jun 2003:

>[R_Hughes >] Technically incorrect: it is also possible to have a design
>where the secondary circuit is floating from earth and where you have a
>double-wound transformer with a screen connected to protective earth.  It's
>called 'Method 2' and the requirements are in IEC/EN 60950-1 clause 2.2.3.2.
>In this case, breakdown from primary to secondary is rendered unlikely
>because breakdown from primary to protective earth is made to be more
>likely.  It is also permissible to construct PCBs or other components this
>way.  Admittedly in practice this is seldom done because by the time you
>have made the protective screen 'meaty' enough you may as well have provided
>insulation. 

Actually, it's often done like that in professional audio equipment, to
which IEC/EN 60065 applies. I am more familiar with that standard, in
which there is no special mention of the technique, and I'd forgotten
that EN60950 goes into the method more formally, in 2.2.3.2 of IEC/EN
60950-1:2001. 

The technique stems from traditional a.m. radio receivers, where the
interwinding screen provides greatly increased immunity to conducted
disturbances entering from the mains supply. The implications of it for
safety were realised when IEC/EN 60065 began to be applied in earnest to
professional audio equipment, around 30 years ago. It allows the signal
circuits of individual pieces of equipment to be optionally connected to
the PEC or not, which is particularly useful for outside broadcast
equipment, to prevent earth currents flowing in the screens of signal
cables.

For the EMC purpose, a single layer of winding, which the winding
machines can put on automatically, has been found effective, but the
current-carrying capacity of such a layer of thin wire might have
insufficient current-carrying capacity for the safety purpose, and this
is dealt with in Annex C of IEC/EN 60950-1. However, in the NOTE to C.2,
there is, despite a disclaimer, an implication that a foil screen is
necessary. The same note says that the requirement is that an overload
device operates in the event of a fault before the screen is damaged,
and this may be satisfied by a screen of quite thin wire if the
operating current of the overload device is less than 1 A or so.

But don't take my word for it!
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               emc_p...@symbol.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to