Good morning, Richard.

I'm not familiar with the UL 498, other than reading it's scope, but the
reason the receptacles are rated 60 C may be based, in part, on the
temperature rating of the wire that's expected to be connected to it.
The most common building wire rating is 60 C and is most likely what's
used in the vast majority of applications (because it's also the least
expensive).  Similarly, the most widely available flexible cords are
rated 60 C.

Speculation aside, medical grade devices seems the shortest answer.

Cooper has several medical grade duplex receptacles to 70 C:
http://64.239.63.88/catalog/

B-I-A in Germany claims 75 C:
http://www.biagmbh.com/katalog/pdfs/18/1884.pdf


I also saw a couple of Chinese companies claiming 66 C ratings.


A longer answer:

You didn't give much detail on which components in the DPITU were
getting to 64 C.  What should be important is what temperature the
attachment plug blades and the insulating materials used in the
receptacle and DPITU housing get to.  If these are sufficiently below 60
C that inaccuracy of test equipment and test methods can be comfortably
accounted for, the application might be OK.  You'll be tied to only
those manufacturers/cat. nos. you test.

Or, select a little outside the minimum.  Perhaps using the above
detailed thermal analysis in conjunction with selecting a 5-20R T-blade
outlet.

If there's room in your compliance budget and not in your manufacturing
budget, you can consider repeating the testing in UL 498 on candidate
receptacles at the higher temperature.  This means you'll need to follow
Ted Eckert's advice of contacting 


Regards,

Peter L. Tarver, PE
ptar...@ieee.org 

CONFIDENTIALITY
This e-mail message and any attachments thereto, is intended only for use by
the addressee(s) named herein and may contain legally privileged and/or
confidential information. If you are not the intended recipient of this e-mail
message, you are hereby notified that any dissemination, distribution or
copying of this e-mail message, and any attachments thereto, is strictly
prohibited.  If you have received this e-mail message in error, please
immediately notify the sender and permanently delete the original and any
copies of this email and any prints thereof.
ABSENT AN EXPRESS STATEMENT TO THE CONTRARY HEREINABOVE, THIS E-MAIL IS NOT
INTENDED AS A SUBSTITUTE FOR A WRITING.  Notwithstanding the Uniform
Electronic Transactions Act or the applicability of any other law of similar
substance and effect, absent an express statement to the contrary hereinabove,
this e-mail message its contents, and any attachments hereto are not intended
to represent an offer or acceptance to enter into a contract and are not
otherwise intended to bind the sender, Sanmina-SCI Corporation (or any of its
subsidiaries), or any other person or entity.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           emcp...@ptcnh.net
     Mike Cantwell           mcantw...@ieee.org

For policy questions, send mail to:

     Jim Bacher:             j.bac...@ieee.org
     David Heald:            emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

Reply via email to