Scott,

 

Does the 60950 standard give examples of what would satisfy the “two
independent fixings” requirement?  How would a terminal block satisfy this?  

 

I have heard that a wire nut can be used for the electrical connection, but
you have to also mechanically hold the wires together which can be done with a
cable tie.  No where have I found this documented, though.

 

The Other Brian

 

________________________________

From: scott barrows [mailto:sbarro...@yahoo.com] 
Sent: Monday, November 17, 2008 2:50 PM
To: sbarro...@yahoo.com; Ted Eckert; EMC-PSTC@LISTSERV.IEEE.ORG; Aldous,
Scott; Kunde, Brian
Subject: RE: What's the deal with Wire Nuts?

 

Hello Other Brian, 

That is a term I have heard from years gone by. 

 

A standard does not specifically prohibit them however if you look at IEC
60950 para 3.1.9 it would be difficult to use wire nut that met the
requirements of "two independent fixings". Most EU standards have a similar
discription as well.

 

Best Regards,

Scott

 



--- On Mon, 11/17/08, Kunde, Brian <brian_ku...@lecotc.com> wrote:

        From: Kunde, Brian <brian_ku...@lecotc.com>
        Subject: RE: What's the deal with Wire Nuts?
        To: sbarro...@yahoo.com, "Ted Eckert" <ted.eck...@microsoft.com>,
EMC-PSTC@LISTSERV.IEEE.ORG, "Aldous, Scott" <scott.ald...@aei.com>
        Date: Monday, November 17, 2008, 2:31 PM

        Where does the term, “Redundant Captive Device” come from?

         

        The device which has the wire nuts (twist-on wire connectors) is a water
chiller used as a peripheral for a piece of laboratory equipment to be sold
internationally.  The manufacturer is not used to making laboratory equipment,
but industrial cooling devices in the US where it maybe acceptable to use wire
nuts. 

 

Looking at the IEC/EN 61010-1 standard I cannot see any specific requirement
for redundant captive device or redundant connection.  I do see a statement in
10.5.3b regarding “insulation which supports the TERMINALS shall be made of
material that will not soften” due to dissipated heat from current through
the connection.  I assume that if the plastic cap of a wire nut gets hot from
current passing through the connection and softens then the connection will
become loose.  Some wire nuts are all plastic and the larger ones have a
copper spring inside. In either case, it is the plastic that secures the
connection.

 

On a crimp type connection (such as a spade lug or crimp splice), even though
they have a plastic case, the electrical connection is made from a metal part
which is not likely to soften. 

 

It would be nice if there was a clear statement (chapter and verse)
documenting if wire nuts can be used in Europe or not or some kind of
interpretation letter.

 

The Other Brian

 

________________________________

From: scott barrows [mailto:sbarro...@yahoo.com] 
Sent: Monday, November 17, 2008 12:26 PM
To: Ted Eckert; Kunde, Brian ; EMC-PSTC@LISTSERV.IEEE.ORG; Aldous, Scott
Subject: RE: What's the deal with Wire Nuts?

 

It is not a redundant captive device.

 

Scott

--- On Mon, 11/17/08, Aldous, Scott <scott.ald...@aei.com> wrote:

        From: Aldous, Scott <scott.ald...@aei.com>
        Subject: RE: What's the deal with Wire Nuts?
        To: "Ted Eckert" <ted.eck...@microsoft.com>, " Kunde, Brian "
<brian_ku...@lecotc.com>, EMC-PSTC@LISTSERV.IEEE.ORG
        Date: Monday, November 17, 2008, 12:08 PM

Hi Brian,

 

When I worked for UL, I had heard that the use of wire nuts was not acceptable
for the EU (CE Marking), but I don’t recall ever seeing the source of this
alleged requirement. I have a vague recollection about them not having any
type of international certifications, but I’m not sure about that.

 

There is a book, CE Marking Handbook: A Practical Approach to Global Safety
Certification, by David Lohbeck, published in 1998, which covers this, but not
in depth. You can preview the book on Google.

 

On page 119, that book indicates that “ U.S. wire-nuts are not permitted for
wire connections.” I don’t believe the source of this statement is
provided, and it well may just be the opinion of the author.

 

Scott Aldous

Compliance Engineer

Advanced Energy

Tel: 970-407-6872

Fax: 970-407-5872

________________________________

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ted Eckert
Sent: Monday, November 17, 2008 9:39 AM
To: Kunde, Brian ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

Hello Brian,

 

Off hand, I am unaware of anything preventing the use of a twist-on wire
connector in portable equipment, but that doesn’t mean that the prohibition
doesn’t exist.  Other list members may know of specific cases where the
connectors are prohibited.  However, the description of the connector covered
in electrical tape indicates that the connector is likely used outside of its
UL Listing (if it is even a Listed connector.)

 

First, let me state that “Wire-Nut” is a registered trademark of Ideal
Industries.  If you are looking for information in standards, the term
“twist-on wire connector” will be used.

 

Vibration during use is probably not the main issue.  There are many types of
fixed equipment, such as an air conditioner or other motor driven appliance,
where twist-on connectors are used and they are subject to regular vibration. 
The connectors may see more vibration in these applications than they might
see in some portable appliances.

 

However, your description gives me cause to be concerned.  UL does List
twist-on connectors under category code ZMVV and they have been around for
quite a while.  (Ideal’s UL file number is E5238 and that should give you an
idea as to the age of the product.)  The connectors’ Listing does have some
very specific requirements.  Specific size connectors are Listed only for use
with specific wire sizes and types.  The installation instructions must be
followed closely.  Some of the wire connectors specify that you should not
twist the wires first.  The twisting of the wire connector will twist the
wires to make the proper connection.  If you see a connector covered with
black tape, there is likely a problem.  The tape is typically used when there
is a concern that the connector will come loose.  This is done based on the
installer’s experience.  If they have had connectors come loose, it is
because they are likely using them incorrectly.  The tape does not fix
anything.  Electrical tape will not likely withstand the test of time and the
adhesive will degrade.  Cheap electrical tape rarely lasts long at all.

 

There are numerous crimp connectors suitable for connecting wires.  There are
but splices and crimp connectors designed to perform the same purpose as a
twist-on connector.  The crimp connectors make a good, permanent splice.  The
twist-on connector is intended for use where connections are made in the
field, particularly where they may need to be undone for servicing.  Crimp
connections and terminal blocks are better options for factory connections.

 

Ted Eckert

Compliance Engineer

Microsoft Corporation

ted.eck...@microsoft.com

 

The opinions expressed are my own and do not necessarily reflect those of my
employer.

 

 

 

From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Monday, November 17, 2008 6:18 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: What's the deal with Wire Nuts?

 

Greetings Experts.

 

This should be an easy one for those who know the answer.

 

What is the deal with Wire Nuts?  Where can be they be used, where can’t
they be used?  Are there different rules for permanently mounted equipment
verse portable equipment? Do you have to also use a mechanical device such are
a tie wrap? How about black tape?

 

Our company does not use wire nuts but we always had the impression that
safety inspectors do not like to see wire nuts in portable equipment.  We are
evaluating a product made by another company that uses wire nuts on primary
wiring with black tape wrapped around it.  Is this technique acceptable
internationally on portable equipment?

 

Thanks to all in advance for the education.  

 

The Other Brian

_________________________ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you. 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

This message, including any attachments, may contain information that is
confidential and proprietary information of Advanced Energy Industries, Inc.
The dissemination, distribution, use or copying of this message or any of its
attachments is strictly prohibited without the express written consent of
Advanced Energy Industries, Inc. 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

 

_________________________ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you. 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

 

_________________________ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you. 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 


Reply via email to