In message <FCA549BE3ECF9D4CB8CB8576837EA4890A6D58@ZEUS.cetest.local>, 
dated Wed, 28 Oct 2009, "ce-test, qualified testing bv - Gert Gremmen" 
<g.grem...@cetest.nl> writes:

>
>Not true for identical equipment.

Please cite the standard or regulation that supports that opinion.

>Any single product was tested as a single equipment and interaction in 
>the close field between single units is not part of the tests. The 
>current EMC regulations do *NOT* consider combining multiple pieces at 
>all. Radiation may (will) add up even if the signals are not in phase. 
>Same for harmonics and conducted emissions.

Agreed.

>EMC regulation was not made with the idea that a consumer may combine 
>multiple identical boxes in a rack.

Please cite the standard or regulation that supports that opinion.
>
>
>When buying a rack of equipment, the client may expect similar 
>protection as when buying a single piece of equipment, and the 
>Manufacturer is expected to have evaluated the consequences.

If it's bought as a single item of commerce, yes. As a custom assembly, 
the individual DoCs and assessments are valid for EMC by additional 
safety tests may be required, usually for temperature effects only.
>
>This does however, not address the combination of multiple different 
>Items in a rack. Technically more or less like to buying a IKEA rack 
>and setting up a audio/video combination.
>
>In practice most equipment integrators make a mixture of different and 
>identical types of products, and in that case CE+CE <> CE at all.

Please cite the standard or regulation that supports that opinion.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
Help stamp out intolerance!

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@socal.rr.com>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to