Dear all,

Thank you for your comments.

The below mentioned construction was rejected. The client needs to use high 
breaking fuse and not enhanced fuse.

The problem is that in every switch mode power supply you can get high short 
circuit current which is causing non-high breaking fuse to burst (there is a 
resistance <1ohm even with power supply cord). This happens during fault 
condition testing in primary circuit right after the fuse (e.g. across the 
varistor or diode bridge). But test has to be performed on the correct branch 
circuit and in peak of input voltage. But the problem is that standard does not 
define precisely how to conduct the abnormal condition (e.g. IEC 60950-1).

There are many power supplies on the market with low breaking or enhanced 
breaking type of fuse and they are approved by different certification bodies. 
Some power supplies have only TR5 low breaking fuse. That's why I decided to 
ask you experts for 2nd opinion.

UL has a PAG about this issue and does not allow it. However in the past many 
such construction were acceptable also by UL.

Best regards,

Boštjan Glavič
Head of Laboratory, Laboratory of Electronic Engineering
www.siq.si
SIQ Ljubljana, Trzaska c. 2, SI-1000 Ljubljana, Slovenia, VAT ID: SI23509678
t +386 (0)1 4778 265, m +386 (0)41 391 283, f +386 (0)1 4778 444


-----Original Message-----
From: Pete Perkins [mailto:peperkin...@cs.com] 
Sent: Wednesday, August 07, 2013 11:33 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Cc: Boštjan Glavič
Subject: RE: [PSES] breakage of the fuse

Bostjan commented:      During the abnormal tests in primary circuit,
internal input fuse operates and glass breaks. However, fuse is inside the 
tubing and broken glass does not spread around.

Would you accept such construction?

        - - - - -

Bostjan,

        Such a question can have several answers, among other things it
depends upon who the 'you' is.   

        If the 'you' is a party who suffered personal injury or financial 
damage they probably wouldn't be willing to accept such construction & you will 
hear from them.  

        If the 'you' is a test house or regulator they probably would be 
looking closely for a way to not accept such construction.  

        If the 'you' is a tinkerer who likes to solve difficult problems they 
probably would accept such construction & be happy that they could fix it and 
get on with using the product. 

        Perhaps the question you should ask is 'would your mother accept such 
construction?' or would she be all over you because of what happened.  

        Would the general public know how to clear out the mess in the 
fuseholder and insert a new fuse to get back in operation?  

        Think about it; not all questions have one simple answer.  

:>)     br,     Pete

 

Peter E Perkins, PE

Principal Product Safety Engineer

PO Box 23427

Tigard, ORe  97281-3427

 

503/452-1201     fone/fax

p.perk...@ieee.org

 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to