In message
<64D32EE8B9CBDD44963ACB076A5F6ABB02716E48@Mailbox-Tech.lecotech.local>,
dated Wed, 16 Sep 2015, "Kunde, Brian" <brian_ku...@lecotc.com> writes:
However, our 300 watt power supplies are used in a product that is
plugged into a 30A – 50A single phase branch circuit. I assume that
such a circuit in a commercial or industrial environment can produce
much larger inrush currents than is possible with our test equipment in
the EMC Lab.
To drop a worst-case 10% of 230 V at 50 A, the source resistance is
0.046 ohms, and the prospective short-circuit current is 500 A. You can
expect real supplies not to be anywhere near worst-case for
voltage-drop, so think 2500 A or so.
--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion
list. To post a message to the list, send your e-mail to <emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>
For policy questions, send mail to:
Jim Bacher: <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>