In the US, 120 Vac and 60 Hz.  The filter has a pass band below 1 kHz, and a
stop band of 100 dB at 10 kHz.  That requires large amounts of
line-to-ground capacity and series inductance, and obviously at least five
poles.

Ken Javor
Phone: (256) 650-5261



From: Richard Nute <ri...@ieee.org>
Reply-To: <ri...@ieee.org>
Date: Tue, 18 Jul 2017 11:47:22 -0700
To: <EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] Chamber grounding [General Use]

 
³But as soon as mains filters are mounted on the wall, one has to cope with
leakage currents (blind current) as large as 6 amp or more.²

6 amps!  At 230 volts, 50 Hz, Xc is 38.8 ohms.  Total C from line to earth
is 69.2 uF!  (Presumably the filter has an equal capacitance from neutral to
earth.)  Why does a chamber need so much filtering at mains frequency?
 
Rich
 
 
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website:      http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html>
List rules:     http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher  <j.bac...@ieee.org>
David Heald <dhe...@gmail.com>



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to