The rationale was that the points of the star washer created the conductive
grounding path. Since the points were fairly small, and the ground fault
current was high, a fault current would be forced to flow across those tiny
point-contacts. This had the danger of causing the points to melt or arc.
The heat-sinking of the rest of the assembly will prevent overheating.
Many years ago, I tested a #18 power cord wire, cutting each strand one at a
time and then testing the impedance at 25 amps. At 3 strands, the wire failed.
The heat-sinking provided by the cut strands kept the remaining strands from
overheating.
Conventional wisdom not backed up by testing.
Best regards,
Rich
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>
For policy questions, send mail to:
Jim Bacher: <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>