I know you could pull single phase from the 3phase, but it is essentially that already, just coming from the panel on the wall instead of splitting at the machine. This machine is fed by 3 beakers on the panel. (I just checked) I was wrong before the 2 spindles are on one 208 3phase beaker, the 4 servo drives are on one 208 single phase, and the PC and other low voltage stuff is a 110 beaker. All 3 right in a row in the same panel box. I guess there is the potential of a ground loop problem from these 3 separate feeds (that each have their own ground wire.) What would be the right way to remedy this?
----- Original Message ----- From: "Gene Heskett" <ghesk...@wdtv.com> To: emc-users@lists.sourceforge.net Sent: Thursday, December 10, 2015 4:06:07 AM Subject: Re: [Emc-users] linuxcnc 2.7.3 - mesa 7i77 update On Wednesday 09 December 2015 23:30:15 Todd Zuercher wrote: > Is there a way to issue a stop/start command to the sserial interface > on the 5i25? > > I am a little bit at a loss where to begin with looking for the source > of the possible noise issue. Peter mentioned earlier some things to > check. The DB25 cable is the one that came with the Mesa plug and go > kit, and is not routed near any power cables, The power source for > the servo drives is 220 3 phase and the PC is on 110 single phase, > arranging for them to use the same power source may be difficult. Todd, if the power company didn't use a wild leg (and I haven't seen one of those since back in the '50's of the last century) for the "220" 3 phase, but a true 3 phase circuit using a transformer per phase at the service pole, which today on this side of the pond is 254 volts per phase, measured from phase to phase. The trick is to treat the "220" load as a delta load, where the 4th wire neutral is just for equipment grounding. But, measuring that same set of 3 wires from each wire to the neutral, looking at it as a "wye" load should show nominally 127 volts to neutral for all 3 wires. The critical measurement, to detect whether the power company used a wild leg, is to measure from each of those 3 hot wires, to a local ground rod. If one wire is way off the 127 reading, they've used a wild leg, which only needs 2 transformers on the service pole. If you get that 127, then just hook the PC to that and the neutral. Any one of the hot wires will do. If you get an obviously higher reading on one wire, like above 140 volts, don't hook the PC power to that one, but I would also rattle the power companies cage asking for a true 3 phase circuit. Cheers, Gene Heskett -- "There are four boxes to be used in defense of liberty: soap, ballot, jury, and ammo. Please use in that order." -Ed Howdershelt (Author) Some mill pix are at: Genes Web page <http://geneslinuxbox.net:6309/gene/GO704-pix> ------------------------------------------------------------------------------ _______________________________________________ Emc-users mailing list Emc-users@lists.sourceforge.net https://lists.sourceforge.net/lists/listinfo/emc-users ------------------------------------------------------------------------------ _______________________________________________ Emc-users mailing list Emc-users@lists.sourceforge.net https://lists.sourceforge.net/lists/listinfo/emc-users