On Monday 11 January 2021 03:48:07 Chris Albertson wrote:

> The motor is NOT seeing a 4,000 Hz square wave current.  The motor is
> an inductive load and it is filtering the 4KHz to nearly DC.   Look
> and see, Use a real scope (no hal scope) on the line and look at
> current v. time.
>
> Look at the PID controller.  it will always oscillate if you are
> trying to control position with a velocity measurement and are
> controlling torque.

feedback is encoder counts against velocity command from motion. I think.

> On Sat, Jan 9, 2021 at 11:38 PM Gene Heskett <[email protected]> 
wrote:
> >  What would happen if I dropped
> > the pwmgen frequency to 400 hz. that same percentage of a pulse
> > coming into the controller would have 10x the length of time to
> > actually move the motor, which may drive it closer to a null than


Cheers, Gene Heskett
-- 
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)
If we desire respect for the law, we must first make the law respectable.
 - Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/gene>


_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to