In my experience of installing EVSE locations over the past several years,
I have found the following to be most common. A dedicated (meaning that the
20 Amp breaker serves only the one outlet) 120 volt, 20 Amp receptacle
(usually spec grade or higher) for level for the L1. For L2, a 230 volt, 50
Amp circuit with a Clipper Creek EVSE or equivalent (many of these can be
set up with a 30 Amp option, but to avoid the need to upsize the circuit
later, I recommend installing with #6 wires and a 50 Amp 2 pole circuit
breaker, but always follow the manufacturer's instructions, as it will be
your defense when dealing with inspectors and insurance people.)
In my opinion, Clipper seems to offer a very robust product at a reasonable
price. And the tech support is good when needed.
If you do not have enough room in your electrical panel for the added
circuits, then it is usually best to have a sub panel installed for this
purpose. I usually offer customers this option, and suggest the idea of
adding out door outlets fed by this box for holiday light use as well,
reducing the typical overloading of circuits that often happens at such
times.

-Tom

On Mon, Jan 25, 2016 at 9:01 AM, Hoegberg via EV <ev@lists.evdl.org> wrote:

>
>
> ----------------------------------------
> > Date: Sun, 24 Jan 2016 14:02:10 -0800
> > To: ev@lists.evdl.org
> > Subject: Re: [EVDL] Updated: Outdoor home EVSE: Installing External
> ChargeAccess
> > From: ev@lists.evdl.org
> >
> > Mike,
> > L1 is only 110V as fas as I know,
> > so 240V 50A is more than most L2 can sustain and definitely L2.
> > I think many countries do not have L1 where the household supply is 230V
> > (delivered as 3-phase 400V to reduce copper usage by 1/3 since
> > the "Neutral" return only needs to be the same gauge as of each of the
> > phases, since the phases partially cancel each other,
>
> -Hm, I have almost forgotten about the situation in your place
>
> how do you do 1 phase motors efficient? I dont get it
> Say if you have a large motor? for example *over* 2kW
> that is about what a normal 1.5mm2 cable for 1phase
> can do here, over that level it really starts to be
> a bit crazy to use a 1 phase motor here
>
> BTW
> I think here (Sweden) the maximum "unbalanced" *feed in*
> power at 1 of the phases(=230V) is about 3500 W, after that
> it is "illegal" / not allowed by the powercompany to install.
> And about 4600W allowed unbalanced power in Germany
> (feed in = for example grid tied solar, or the steamengine :-)
>
>
>
> But what if you need to connect your 40 kW windmill at
> your 1phase house ? that would demand insane cables
> and crazy currents at the very low voltage us-system.
>
> And do you still *always* use only 1 wire(phase) systems
> instead of 3 , even if it is rotating stuff you need in the endpoint?
> (like motors or generators)
>
> what if you get a bigger async motor, how to turn that efficient if
> there is no rotating field between the normal L1,L2,L3 at the terminals?
> :-)
> Do you use inverters for your big motors/generators to generate the
> 3phases?
>
>
>
>
> > which is similar to the common US "two phase" system that saves 1/4 of
> > the copper as also here the Neutral is the same gauge as the 2 phase
> > wires instead of double the surface.
>
> -Sometimes it is just 3 of the powerwires +shield(connected to
> earth/ground)
> and sometimes it is no shield. (+neutral +protective earth)
>
> Because if you have no 230V-stuff (1phase&neutral = 230V) at
> the end of the 400Vac motor cable, then you probably dont need the neutral
> anyway
>
>
>
>
>
> > The standard household outlets in Europe are 230V 16A which means that
> > they can deliver about 3kW continuously
>
> - Almost correct, I think
>
> The old standard is called Schuko, se pictures
> http://www.internationalconfig.com/icc6.asp?item=70141
> that translate to "safety-plug", I guess.. and I remember reading
> that it is not always specified to be continuous used at max load.
> i think it is 6hour at 16A. but did not find that now,
> So about 3600W resistive load.
>
> Also some have 1phase blueplug=230V outdoors, a 16Amp Europlug.
> it is similar to the normal industrial 3phase "redplugs", red =400V
> ("IEC 60309" , but they are 16A @ 6h rating.  but it is more robust,
>    have lock, & IP44 if they are mounted to face downwards)
>
>  -But of course it is only ok with 16A per phase if you
>  have copper enough and then fuses for this.
> 16Amp needs the fat cables of 2.5mm2 inside
> the walls to be correct. 1.5mm2 will get hot..
>
> Normal households plugs here have 1.5 mm2 and 10Amp fuses
> So that is enough for about 2.3kW resistive per group and
> 1 phase plug(s) = 230V = and we use neutral for return.
>
>
>
> (I assume it CAN be ok / legal to install a wall-charger at
> "400Vac from 2 phases", then we use no neutral
> as I think 400 Volt also is the voltage between 2 phases,
> in that way you get even more power(4kw?)
> out from 2pcs of 10A 1.5mm2wires :-)
> and if we have 16A 2-phase I think it wil be:
> 400V*16A =6400W @1.5mm2 :-P
>
> but.. you should of course NOT use a "230V 1-phase"
> shucko/IEC-plugs at a 400Vac extensioncord.., as dangerous
> fuckups *will* occur later when you plug in something
> else there, that cant handle you nice and lethal illegal 400Vac
> "230"-cord....  :-)
>
>
>
>
> > incidentally the older Leaf L2
> > charger power spec (half the full L2 spec of 6kW of 240V 24A which maxes
> > out a standard 30A dryer outlet)
>
> And 6kW switchmode 3phase chargers would only be
> about 8.7 amps here = we use 1.5mm2 copper.
> (my houses main fuses are 20Amp)
>
> 3phase FTW ! ;-)
>
>
> / John
>
> _______________________________________________
> UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
> http://lists.evdl.org/listinfo.cgi/ev-evdl.org
> Read EVAngel's EV News at http://evdl.org/evln/
> Please discuss EV drag racing at NEDRA (
> http://groups.yahoo.com/group/NEDRA)
>
>


-- 
Remember, it is not that the glass is half empty, in reality, the glass is
merely twice the size that it needs to be! -TNT'82
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20160125/064b321d/attachment.htm>
_______________________________________________
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
http://lists.evdl.org/listinfo.cgi/ev-evdl.org
Read EVAngel's EV News at http://evdl.org/evln/
Please discuss EV drag racing at NEDRA (http://groups.yahoo.com/group/NEDRA)

Reply via email to