20A sounds low until you realize that it is likely 3x 20A at 230V (400V
three-phase) so it is almost 14kW.
I believe that most houses where I lived in The Netherlands had a single
25A or 35A main fuse (not accessible to the home owner, only to the
utility) as most homes were only fed from a single phase and alternating
phases were connected in the subsequent homes in the street. The home
itself had typically between 3 to 6 circuits that were fused with 16A.
Only if you requested an upgrade, for example for electric cooking,
would you get a new meter and 3 main fuses installed and then you could
install a 3-phase outlet providing 400V instead of 230 single phase.
I believe that it was allowed to use 3 separate fuses or breakers to
feed the 3-phase outlet since it was never used without Neutral.

Cor van de Water 
Chief Scientist 
Proxim Wireless 
  
office +1 408 383 7626                    Skype: cor_van_de_water 
XoIP   +31 87 784 1130                    private: cvandewater.info 

http://www.proxim.com

This email message (including any attachments) contains confidential and
proprietary information of Proxim Wireless Corporation.  If you received
this message in error, please delete it and notify the sender.  Any
unauthorized use, disclosure, distribution, or copying of any part of
this message is prohibited.


-----Original Message-----
From: EV [mailto:ev-boun...@lists.evdl.org] On Behalf Of EVDL
Administrator via EV
Sent: Monday, January 25, 2016 2:13 PM
To: Electric Vehicle Discussion List
Subject: Re: [EVDL] Updated: Outdoor home EVSE: Installing
ExternalChargeAccess

On 25 Jan 2016 at 18:01, Hoegberg via EV wrote:

> (my houses main fuses are 20Amp)

That seems like a very small amount of power for a house.  You  can't
charge 
2 EVs at once, if they have 3.3kW chargers, is this not so?  Even
charging 
one 3.3kW EV would mean little power left for other uses in the house.

Here in the US, my older home has a 100 amp main circuit breaker (that
is, a 
pair of breakers mechanically fastened together, one breaker for each
120v 
"hot leg" of the line).  Most newer houses in the US have a 200 amp main

breaker at 240 volts, so they can (in theory) supply up to 48kW.  Some
very 
large houses have 400 amp service (96kW).

David Roden - Akron, Ohio, USA
EVDL Administrator

= = = = = = = = = = = = = = = = = = = = = = = = = = = = =
EVDL Information: http://www.evdl.org/help/
= = = = = = = = = = = = = = = = = = = = = = = = = = = = = 
Note: mail sent to "evpost" and "etpost" addresses will not 
reach me.  To send a private message, please obtain my 
email address from the webpage http://www.evdl.org/help/ .
= = = = = = = = = = = = = = = = = = = = = = = = = = = = =


_______________________________________________
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
http://lists.evdl.org/listinfo.cgi/ev-evdl.org
Read EVAngel's EV News at http://evdl.org/evln/
Please discuss EV drag racing at NEDRA
(http://groups.yahoo.com/group/NEDRA)

_______________________________________________
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
http://lists.evdl.org/listinfo.cgi/ev-evdl.org
Read EVAngel's EV News at http://evdl.org/evln/
Please discuss EV drag racing at NEDRA (http://groups.yahoo.com/group/NEDRA)

Reply via email to