On 2/12/26 13:40, EV List Lackey via EV wrote:
On 12 Feb 2026 at 9:22, Thos True via EV wrote:

If you are connecting a 30A charger, it would be wise to choose a 30A
circuit breaker, rather than a 50A.

I'm not a pro electrician, so please forgive me if I'm speaking out of turn,
but wouldn't you use a 40a breaker there?


Yes, that is correct. You need a 50 amp breaker for a 40 amp EVSE and 40 amp for a 30A EVSE to prevent nuisance trips.

He also didn't mention what wire size to use. But if you install a NEMA 14-50, you should use the correct (50 amp rated) wire gauge (size can change depending upon the length of the run, but typically be a 6AWG or 4AWG for longer runs to reduce resistance losses).

I suspect it may be against code (but safe) to downsize the breaker (smaller than the wire/outlet requires).

So if you have a 30 amp EVSE, using a 40A Breaker isn't a bad idea to trip faster if the load goes well above expected, BUT, if somebody plugs anything else into the NEMA 14-50 that expects to be able to get 50 amp power, it will trip the 40A breaker quickly.

What you CAN'T do is use the incorrect (too small, lower amp rating) wire size...that's unsafe, especially if somebody later swaps out the 40A breaker to a 50A breaker because they see the 14-50 at the other end and don't pay attention to the wire size.

Jay
_______________________________________________
Address messages to [email protected]
No other addresses in TO and CC fields
HELP: http://www.evdl.org/help/