Many thanks Chris, I will try this out and see how it works. I think the
drawbacks would be acceptable because if the UPS is on battery, nothing
else really matters.

Don Goodhue
Information Systems Officer
Union Bank


-----Original Message-----
From: [email protected]
[mailto:[EMAIL PROTECTED] On Behalf Of Christopher L.
Sweeney
Sent: Wednesday, September 19, 2007 11:13 AM
To: InterMapper Discussion
Subject: RE: [IM-Talk] APC UPS AP961x probe Notifier

At 10:25 AM -0400 9/19/07, Don Goodhue wrote:
>I like that idea. If you have some quick instructions to do this I 
>would certainly appreciate it.
>

The short way:

I've attached a modified version of the probe. Save this attachment. 
In the InterMapper client or IMRA, choose File->Import->Probe... and
select the saved attachment. That should be all that's necessary. You
now simply need to attach a notifier to the appropriate devices and
enable it for the critical state.

The only drawback to this solution that I noticed when I was making the
changes is that this means that when you're on battery, the state will
always be critical, which would probably cause you to miss all the other
problems, as they're warning or alarm. If the other problems which cause
alarms are something you'd still want to be notified of, you might want
to further modify the probe so that "on battery" is alarm and everything
else is critical.

-- Christopher

P.S. Here's the long way for doing it yourself, as I said I'd give
instructions:

On the machine running the Intermapper server, find the InterMapper
Settings folder. For Windows, this will usually be in C:\Program
Files\InterMapper; for Mac OS X, this will usually be in
/Library/Application Support. For Linux/Unix, it will be named
InterMapper_Settings and will usually be in the home directory of the
user under which intermapperd is running.

In the InterMapper Settings folder, find the Probes folder. In the
probes folder should be a file named com.dartware.ups.apc-ap961x.txt. 
Load that into a text editor.

Find the section labelled "<snmp-device-thresholds>". In that section
will be the line:

alarm:    $batTimeOn > 0                                      "UPS 
has been running on battery for $batTimeOn seconds."

Change "alarm" to "critical" so that it reads:

critical:    $batTimeOn > 0                                      "UPS 
has been running on battery for $batTimeOn seconds."

At the top of the file, find the line which reads:

"version"       =  "2.53"

Change "2.53" to "2.54" or higher:

"version"       =  "2.54"

Save your changes.

In the client (local or IMRA), pick any device, right-click, and choose
"Set Probe..." (Don't worry--we won't actually set one.) In the dialog
that appears, click "Reload Probes" in the bottom left corner. You
should get a message saying how many changed and how many had errors. It
might take a few seconds. Then put away that message and click "Cancel"
in the Set Probe dialog.

That should finish the editing of the probe. You now simply need to
attach a notifier to the appropriate devices and enable it for the
critical state.