To do this you would also need to modify opf_hessfcn.m accordingly, and there 
are almost certainly numerous other places in the code where the number of 
non-linear inequality constraints would have to be updated. This isn’t exactly 
a trivial task. Hopefully some day I’ll get a chance to include user-defined 
non-linear constraints as a MATPOWER feature, but we’re not there yet.

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853  USA
phone: (607) 255-9645

On Jul 14, 2014, at 11:49 PM, Abhyankar, Shrirang G. <abhy...@mcs.anl.gov> 
wrote:

> Patrick,
>    I'm afraid setting Smin limit on tie line flow is not as
> straightforward as I initially thought. The reason being that with
> MATPOWER's optimal power flow, the flow constraint for a transmission line
> is set as
> |S_flow| - Smax^2 \le 0. MATPOWER uses rate_A limit as the flow limit
> (Smax) for branches. So, while a Smax  can be set for the line flow, Smin
> is not implemented.
> 
> You'll have to do a little bit of hackery to do what you want. Here are
> the steps:
> i) Set the Smin values for branches in branch RATE_B column (RATE_B is not
> used anyways for the OPF so this should be fine). Only tie lines will have
> a non-zero Smin, others will be zero. This will help
>   you to identify the tie lines and set constraints only for them.
> ii) Modify the file opf_consfcn.m (the routine sets up the equality and
> inequality constraints for the OPF) to include additional inequality
> constraints for the tie lines in the h vector. Note that the optimization
> expects the inequality
>    constraints in the standard form h(x) \le 0. So your additional
> inequality constraints should be Smin(tie_line_idx).^2 - |
> S_flow(tie_line_idx)) |
> 
> Shri
> 
> -----Original Message-----
> From: Eser  Patrick <es...@student.ethz.ch>
> Reply-To: MATPOWER discussion forum <matpowe...@list.cornell.edu>
> Date: Mon, 14 Jul 2014 17:30:48 +0000
> To: MATPOWER discussion forum <matpowe...@list.cornell.edu>
> Subject: AW: Convergence issues: OPF simulation of several interconnected
> countries
> 
>> Ray, Carlos, Shri,
>> 
>> Thanks for your inputs, I really appreciate your help.
>> 
>> With regard to your responses:
>> 
>> @Shri: How would I impose the Smin and Smax of the tie-line in the
>> MATPOWER intput? I can't see anything alike in the mpc.branch struct, as
>> PF, QF, PT and QT are ignored as inputs according to the manual. Fixing
>> the S-value to the cross-border flow value would definitely help me!
>> 
>> @Carlos: No, there are no phase shifters in the system. Would including
>> phase shifters at crucial points help me?
>> 
>> @Ray,Shri: I have already cooked the problem down to two countries, so I
>> totally agree to your boiling-down approach. I will have to look at each
>> line in detail, but I wanted to make sure first, that I am not making a
>> general mistake that completely prevents convergence.
>> 
>> Thanks again! 
>> ________________________________________
>> Von: bounce-117289979-69334...@list.cornell.edu
>> [bounce-117289979-69334...@list.cornell.edu]&quot; im Auftrag von
>> &quot;Abhyankar, Shrirang G. [abhy...@mcs.anl.gov]
>> Gesendet: Montag, 14. Juli 2014 17:40
>> An: MATPOWER discussion forum
>> Betreff: RE: Convergence issues: OPF simulation of several interconnected
>> countries
>> 
>> Patrick,
>> The first thing that I would try to do is to make sure 1. and 2. give
>> similar solution. I would do this by imposing the cross-border flows in 1
>> as constraints on the tie-lines in 2. So Smax and Smin of the tie-line
>> would be set to the cross-border flow value. The OPF may not converge if
>> you set Smax=Smin=cross-border-flow so allow a little margin for the flow
>> to vary.
>> Also, instead of running the OPF on n countries at once, I would start
>> with just 2 countries first. This would help to identify any problems
>> relatively easily.
>> Another thing to consider are your cost function coefficients. If the
>> countries have different currencies then you'll have to convert the
>> coefficients accordingly.
>> 
>> Good luck,
>> Shri
>> ________________________________________
>> From: bounce-117288115-33970...@list.cornell.edu
>> [bounce-117288115-33970...@list.cornell.edu] on behalf of Eser  Patrick
>> [es...@student.ethz.ch]
>> Sent: Monday, July 14, 2014 8:34 AM
>> To: MATPOWER-L@cornell.edu
>> Subject: Convergence issues: OPF simulation of several interconnected
>> countries
>> 
>> Dear MATPOWER Community,
>> 
>> I am trying to solve a relatively large (>1000 buses) AC OPF problem. It
>> consists of several individual countries (200-300 buses each). Please
>> allow me to describe my procedures, to paint the full picture.
>> 
>> 1. In a first study, I simulated all countries individually. The
>> cross-border power flows to the neighboring countries is known to me from
>> a database. I include these cross-border flows by implementing
>> "pseudo-generators" of zero production cost or "pseudo-demand" at the
>> borders. This procedure works nicely, I get convergence in almost every
>> case I run.
>> 
>> 2. Now I would like to simulate not only one country, but all my
>> countries interconnected as one large system. I have "stitched" the
>> transmission grids of the individual countries together in a realistic
>> manner. If I run the OPF without further constraints, I receive
>> converging simulations. But unfortunately, the flow between my countries
>> is massively too high, probably due to price level differences between my
>> countries. I would like to prevent these high cross-border flows, which
>> leads to point 3.
>> 
>> 3. I would like to limit the power flow (especially the real power flow)
>> between my countries (so on individual branches in my full system), but
>> am not able to get a converging simulation. I have played around
>> extensively the MVA ratings of the lines (long and short term), but as
>> soon as I impose realistic line ratings, I only get "infeasible solution"
>> problems. As a workaround, I tried replacing the AC cross-border
>> transmission lines with DC lines (and limiting real power flow in those
>> DC lines). This does converge sometimes, but not always. I am using MIPS
>> and/or IPOPT.
>> 
>> I would massively appreciate any help in this regard. Some questions
>> about the problem:
>> 
>> What is the best ways to limit the power flow in an individual branch?
>> Why are my simulations never converging, if I impose MVA ratings?
>> Has anybody solved such a problem before? It seems quite straightforward,
>> I am sure someone has already done something like this with MATPOWER.
>> What would you suggest me to do?
>> Should I rather use other solvers than MIPS or IPOPT?
>> As I am not an expert of transmission system, what indicators should I be
>> looking at to find out, where my simulations are going wrong?
>> 
>> Thanks a lot for your comments.
>> 
>> Best Regards,
>> 
>> Patrick
>> 
>> 
>> 
>> 
>> 
> 
> 
> 