Hi Jose,

thank you for the reply. I want to keep voltage in kV, hence the 0.415. I
am looking for alternatives that could allow me to run analysis without
having to divide my load demand by 1000 each time. And I thought probably
by changing the R+jX value, it might help. If I don't want to divide my
load power by 1000 each time, what should I change in the casefile?

On Thu, Oct 27, 2016 at 12:20 AM, Jose Luis Marín <mari...@aia.es> wrote:

>
> If you want to do things properly, I guess you would have to do *all* of
> the following:
>
>    - First, MATPOWER expects baseMVA to be in MW.  If you want to use a
>    p.u. system based around Volts and 1 kW (instead of the traditional kV and
>    100 MW), then you need baseMVA=0.001 at the beginning of your case file.
>    - Expressing voltages in pu should be no problem, just divide the
>    quantity in volts by your voltage levels (in your case I see it's only one,
>    415 Volts)
>    - Now, MATPOWER expects all power quantities (P, Q) to be expressed in
>    MW.  So if your values are in kW, divide them by 1000.
>    - Finally, to convert resistances and reactances (R, X), use your
>    baseMVA and voltage base as follows: take the initial quantity in Ohms, and
>    multiply it by:  baseMVA / Vbase^2 = 1000 Watts / (415 Volts)^2 =
>    5.806357961968356e-03
>    - You don't have Bshunt values in your case, but if you had, the
>    conversion factor would be just the inverse of the one used for resistance
>    and  reactance.
>
> I hope I'm not missing anything, I think that's all you need in your case.
>
> --
> Jose L. Marin
> Grupo AIA
>
>
>
>
> 2016-10-26 14:44 GMT+02:00 Nazurah Nasir <nurnazu...@gmail.com>:
>
>> But does that means I should not divide my input power data by 1000 to
>> make it in MW? If I do that, it won't converge. For example, these are my
>> Power input for one time:
>>
>> Columns 1 through 6
>>     1.0000    3.0000         0         0         0         0
>>     2.0000    1.0000    0.0012    0.0004         0         0
>>     3.0000    1.0000    0.0019    0.0006         0         0
>>     4.0000    1.0000    0.0006    0.0002         0         0
>>     5.0000    1.0000    0.0024    0.0008         0         0
>>     6.0000    1.0000    0.0012    0.0004         0         0
>>     7.0000    1.0000    0.0010    0.0003         0         0
>>     8.0000    1.0000    0.0023    0.0008         0         0
>>     9.0000    1.0000    0.0005    0.0002         0         0
>>    10.0000    1.0000    0.0006    0.0002         0         0
>>    11.0000    1.0000    0.0012    0.0004         0         0
>>    12.0000    1.0000         0         0         0         0
>>   Columns 7 through 12
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>>   Column 13
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>     0.9400
>>
>> Thank you very much for the help
>>
>> Yours sincerely,
>> Nur
>>
>> On Wed, Oct 26, 2016 at 11:14 PM, Nazurah Nasir <nurnazu...@gmail.com>
>> wrote:
>>
>>> Aren't I supposed to make the R and X in p.u. if I want to use them in
>>> MATPOWER? Regardless, your simulation seems to be more sensible. But, I
>>> just curious, so we don't necessarily change the R and X into p.u. values?
>>>
>>> Thanks for the response.
>>>
>>> On Wed, Oct 26, 2016 at 3:26 PM, Saranya A <asar...@gmail.com> wrote:
>>>
>>>> Hi Nur,
>>>> Dont divide R and X with the voltage. I get the following power flow
>>>> without those two lines.
>>>>
>>>> ------------
>>>> runpf('LV10')
>>>>
>>>> MATPOWER Version 6.0b1, 01-Jun-2016 -- AC Power Flow (Newton)
>>>>
>>>> Newton's method power flow converged in 5 iterations.
>>>>
>>>> Converged in 0.02 seconds
>>>> ============================================================
>>>> ====================
>>>> |     System Summary
>>>>         |
>>>> ============================================================
>>>> ====================
>>>>
>>>> How many?                How much?              P (MW)            Q
>>>> (MVAr)
>>>> ---------------------    -------------------  -------------
>>>>  -----------------
>>>> Buses             12     Total Gen Capacity     261.0        -302.0 to
>>>> 302.0
>>>> Generators        11     On-line Capacity       250.0        -300.0 to
>>>> 300.0
>>>> Committed Gens     1     Generation (actual)      1.2               0.5
>>>> Loads             10     Load                     1.0               0.3
>>>>   Fixed           10       Fixed                  1.0               0.3
>>>>   Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
>>>> Shunts             0     Shunt (inj)             -0.0               0.0
>>>> Branches          11     Losses (I^2 * Z)         0.23              0.16
>>>> Transformers       0     Branch Charging (inj)     -                0.0
>>>> Inter-ties         0     Total Inter-tie Flow     0.0               0.0
>>>> Areas              1
>>>>
>>>>                           Minimum                      Maximum
>>>>                  -------------------------
>>>>  --------------------------------
>>>> Voltage Magnitude   0.717 p.u. @ bus 11         1.000 p.u. @ bus 1
>>>> Voltage Angle      -5.40 deg   @ bus 11         0.00 deg   @ bus 1
>>>> P Losses (I^2*R)             -                  0.06 MW    @ line 1-2
>>>> Q Losses (I^2*X)             -                  0.04 MVAr  @ line 1-2
>>>>
>>>> ============================================================
>>>> ====================
>>>> |     Bus Data
>>>>         |
>>>> ============================================================
>>>> ====================
>>>>  Bus      Voltage          Generation             Load
>>>>   #   Mag(pu) Ang(deg)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)
>>>> ----- ------- --------  --------  --------  --------  --------
>>>>     1  1.000    0.000*     1.23      0.46       -         -
>>>>     2  0.950   -0.744       -         -        0.10      0.03
>>>>     3  0.905   -1.483       -         -        0.10      0.03
>>>>     4  0.864   -2.206       -         -        0.10      0.03
>>>>     5  0.828   -2.898       -         -        0.10      0.03
>>>>     6  0.797   -3.541       -         -        0.10      0.03
>>>>     7  0.770   -4.116       -         -        0.10      0.03
>>>>     8  0.749   -4.607       -         -        0.10      0.03
>>>>     9  0.733   -4.993       -         -        0.10      0.03
>>>>    10  0.722   -5.260       -         -        0.10      0.03
>>>>    11  0.717   -5.397       -         -        0.10      0.03
>>>>    12  1.000    0.000       -         -         -         -
>>>>                         --------  --------  --------  --------
>>>>                Total:      1.23      0.46      1.00      0.30
>>>>
>>>> ============================================================
>>>> ====================
>>>> |     Branch Data
>>>>        |
>>>> ============================================================
>>>> ====================
>>>> Brnch   From   To    From Bus Injection   To Bus Injection     Loss
>>>> (I^2 * Z)
>>>>   #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)
>>>> Q (MVAr)
>>>> -----  -----  -----  --------  --------  --------  --------  --------
>>>>  --------
>>>>    1      1      2      1.23      0.46     -1.17     -0.42     0.055
>>>>    0.04
>>>>    2      2      3      1.07      0.39     -1.03     -0.36     0.046
>>>>    0.03
>>>>    3      3      4      0.93      0.33     -0.89     -0.30     0.038
>>>>    0.03
>>>>    4      4      5      0.79      0.27     -0.76     -0.25     0.030
>>>>    0.02
>>>>    5      5      6      0.66      0.22     -0.64     -0.20     0.023
>>>>    0.02
>>>>    6      6      7      0.54      0.17     -0.52     -0.16     0.016
>>>>    0.01
>>>>    7      7      8      0.42      0.13     -0.41     -0.13     0.011
>>>>    0.01
>>>>    8      8      9      0.31      0.10     -0.30     -0.09     0.006
>>>>    0.00
>>>>    9      9     10      0.20      0.06     -0.20     -0.06     0.003
>>>>    0.00
>>>>   10     10     11      0.10      0.03     -0.10     -0.03     0.001
>>>>    0.00
>>>>   11      1     12      0.00      0.00      0.00      0.00     0.000
>>>>    0.00
>>>>                                                              --------
>>>>  --------
>>>>                                                     Total:     0.228
>>>>    0.16
>>>>
>>>> On Tue, Oct 25, 2016 at 10:31 PM, Nazurah Nasir <nurnazu...@gmail.com>
>>>> wrote:
>>>>
>>>>>
>>>>>
>>>>> Hi all MatPower community,
>>>>>
>>>>> I am trying to develop a simple LV network in radial network
>>>>> distribution. However, my model did not converge or if I scale the R and 
>>>>> X,
>>>>> the results is too big (which means the R,X) scaling is wrong. I tried for
>>>>> one month now but still could get around why it is not converging.
>>>>>
>>>>> I need to work on this PowerFlow to work inside my bilevel programming
>>>>> loop. but it seems my code won't work because the power flow is not
>>>>> converging.
>>>>>
>>>>> I need help on verifying my parameter. Attached is my code that I
>>>>> build. As the MatPower is in three phase balanced, I lumped my loads that
>>>>> connected to a bus as one load, hence the voltage at the bus is 0.415kV. 
>>>>> My
>>>>> input power are all in kW, hence I change the impedance values accordingly
>>>>> by multiplying it by 1000. The input power is just a dummy value of 0.1MW
>>>>> because it will update itself in a loop. But since input power is in kW, I
>>>>> should divide that by 1000 right?
>>>>>
>>>>> Thank you so much for the help.
>>>>>
>>>>>
>>>>> Best regards,
>>>>> Nur
>>>>>
>>>>>
>>>>
>>>
>>
>