Hello ! sorry ! I try again!
you most change type of bus
[image: image.png]
then add GEN for example
[image: image.png]
and
[image: image.png]
then save
>> mpc =loadcase('case33bw');
>> results = runpf(mpc);
befor add you have
loss Total: 0.276 0.21
generator Total: 3.92 2.44 3.72 2.30
after add
loss Total Total: 0.276 0.21:
[image: image.png]
[image: image.png]
in bus 32 change value
have nice timeOn Tue, Feb 12, 2019 at 6:40 PM Ray Zimmerman <[email protected]> wrote: > With a power flow (as opposed to OPF), the dispatch of each generator > (except slack, which is typically the substation in a distribution system), > including DGs is specified as an input. So if you want the DG dispatch to > change as load changes you will have to specify the dispatch changes > explicitly. > > Ray > > > On Feb 9, 2019, at 5:36 AM, Aamir Nawaz <[email protected]> wrote: > > Dear Amir al hosseni, > Thanks for your kind response. But i am sorry that you didnt understand my > question. Please see distribution system cases like case33bw.m and try to > add DGs to them. Most of load is take up by first generator while doing > runpf. This makes other DGs to have static output power and only 1st > generator output is changing to satisfy demand. You can change load to see > change in 1st generator output. Please study this and i hope you will > understand what i wanted to ask. Thanks. > > > > *Regards,Aamir Nawaz* > > > On Saturday, February 2, 2019, 10:53:04 AM GMT+8, amir ali Hosseini < > [email protected]> wrote: > > > hi > you shold read document MATPOWER > but so > Are you Mathpower add path to the Matlab?!if yes?! So! > frist you shold chose the case . for example case 9 that means it has 9bus > In command window typeing > mpc=loadcase('case9'); > Results = runpf(mpc); > It was simple isn't it?! > > > On Fri, Feb 1, 2019, 19:07 Ray Zimmerman <[email protected] wrote: > > If you have islands, each island must have it’s own slack bus. > > Ray > > > On Jan 27, 2019, at 1:12 AM, Aamir Nawaz <[email protected]> wrote: > > Dear Dr. Ray, > Thanks for your kind response. I am still unable to understand how to > execute opf or pf for distribution system while adding some DGs on other > feeders than slack bus. Please share some example where DGs connected > within the distribution system is supplying power to load, particularly in > case of islanding. I hope you understood my problem and help me solve this. > Thanks again. > > > > *Regards,Aamir Nawaz* > On Friday, January 11, 2019, 6:49:00 AM GMT+8, Ray Zimmerman < > [email protected]> wrote: > > > If you are running an OPF, it will take the least expensive generation it > can. Maybe check the relative costs? > > Ray > > On Jan 3, 2019, at 10:46 PM, Aamir Nawaz <[email protected]> wrote: > > Dear Dr. Ray, > I want to execute IEEE 13 bus distribution system with distributed > generations (DG, wind farm, pv etc). I have added generators but it always > take power from generator at slack bus but not others. Please guide me how > to add DG in distribution system at different nodes. > > > > *Regards,Aamir Nawaz.* > <case13bw.m> > > > > >
case33bw.m
Description: Binary data