In this example, it seems you have added a 0 MW generator to bus 32 and changed 
the bus type from PQ to PV. The only change should be that there is now a Q 
injection at bus 32 in order to keep the voltage at the specified 1 p.u.

Is that not what you intended?

   Ray

> On Feb 14, 2019, at 1:21 AM, amir ali Hosseini <[email protected]> wrote:
> 
> Hello ! sorry ! I try again!
> you  most change type of bus
> <image.png>
> then add GEN for example
> <image.png>
> and
> <image.png>
> then save 
> >> mpc =loadcase('case33bw');
> >> results = runpf(mpc);
> befor add you have 
> loss Total:     0.276      0.21
> generator   Total:      3.92      2.44      3.72      2.30
> after add
> loss Total  Total:     0.276      0.21:
> <image.png>
> <image.png>
> in bus 32 change value 
> have nice time
> 
> On Tue, Feb 12, 2019 at 6:40 PM Ray Zimmerman <[email protected] 
> <mailto:[email protected]>> wrote:
> With a power flow (as opposed to OPF), the dispatch of each generator (except 
> slack, which is typically the substation in a distribution system), including 
> DGs is specified as an input. So if you want the DG dispatch to change as 
> load changes you will have to specify the dispatch changes explicitly.
> 
>     Ray
> 
> 
>> On Feb 9, 2019, at 5:36 AM, Aamir Nawaz <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>> Dear Amir al hosseni,
>> Thanks for your kind response. But i am sorry that you didnt understand my 
>> question. Please see distribution system cases like case33bw.m and try to 
>> add DGs to them. Most of load is take up by first generator while doing 
>> runpf. This makes other DGs to have static output power and only 1st 
>> generator output is changing to satisfy demand. You can change load to see 
>> change in 1st generator output. Please study this and i hope you will 
>> understand what i wanted to ask. Thanks.
>> 
>> 
>> Regards,
>> Aamir Nawaz
>> 
>> 
>> On Saturday, February 2, 2019, 10:53:04 AM GMT+8, amir ali Hosseini 
>> <[email protected] <mailto:[email protected]>> wrote:
>> 
>> 
>> hi 
>> you shold read document MATPOWER
>> but so 
>> Are you  Mathpower add path to the Matlab?!if yes?! So!
>> frist you shold chose the case . for example case 9 that means it has 9bus
>> In command window typeing 
>> mpc=loadcase('case9');
>> Results = runpf(mpc);
>> It was simple isn't it?!
>> 
>> 
>> On Fri, Feb 1, 2019, 19:07 Ray Zimmerman <[email protected] 
>> <mailto:[email protected]> wrote:
>> If you have islands, each island must have it’s own slack bus.
>> 
>>     Ray
>> 
>> 
>>> On Jan 27, 2019, at 1:12 AM, Aamir Nawaz <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> 
>>> Dear Dr. Ray, 
>>> Thanks for your kind response. I am still unable to understand how to 
>>> execute opf or pf for distribution system while adding some DGs on other 
>>> feeders than slack bus. Please share some example where DGs connected 
>>> within the distribution system is supplying power to load, particularly in 
>>> case of islanding. I hope you understood my problem and help me solve this. 
>>> Thanks again.
>>> 
>>> 
>>> Regards,
>>> Aamir Nawaz
>>> On Friday, January 11, 2019, 6:49:00 AM GMT+8, Ray Zimmerman 
>>> <[email protected] <mailto:[email protected]>> wrote:
>>> 
>>> 
>>> If you are running an OPF, it will take the least expensive generation it 
>>> can. Maybe check the relative costs?
>>> 
>>>    Ray
>>> 
>>>> On Jan 3, 2019, at 10:46 PM, Aamir Nawaz <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>> 
>>>> Dear Dr. Ray,
>>>> I want to execute IEEE 13 bus distribution system with distributed 
>>>> generations (DG, wind farm, pv etc). I have added generators  but it 
>>>> always take power from generator at slack bus but not others. Please guide 
>>>> me how to add DG in distribution system at different nodes.
>>>> 
>>>> Regards,
>>>> Aamir Nawaz.