[email protected] (Joe Gidi), 2014.11.23 (Sun) 01:22 (CET):
> I'm running OpenBSD 5.6/amd64 on my fileserver. It has an APC UPS that was
> previously managed with apcupsd. Since I upgraded to 5.6, the UPS now
> attaches as a upd device:
> 
> $ dmesg | grep uhidev3
> uhidev3 at uhub3 port 5 configuration 1 interface 0 "APC Back-UPS ES 450
> FW:844.K2 .D USB FW:K2" rev 1.10/1.06 addr 2
> uhidev3: iclass 3/0, 123 report ids
> upd0 at uhidev3
> 
> And it reports sensible values in hw.sensors:
> $ sysctl hw.sensors.upd0
> hw.sensors.upd0.indicator0=On (Charging), OK
> hw.sensors.upd0.indicator1=Off (Discharging), OK
> hw.sensors.upd0.indicator2=On (ACPresent), OK
> hw.sensors.upd0.indicator3=On (BatteryPresent), OK
> hw.sensors.upd0.indicator4=Off (ShutdownImminent), OK
> hw.sensors.upd0.percent0=79.00% (RemainingCapacity), OK
> hw.sensors.upd0.percent1=100.00% (FullChargeCapacity), OK
> 
> So far, so good. Now, I'd like to configure sensorsd to monitor the device
> and invoke a script when the power goes out. I have this line in
> sensorsd.conf:
> 
> hw.sensors.upd0.indicator2:command=/etc/sensorsd/ups.sh %s %2
> 
> The ups.sh script currently just echoes the token values that it's passed
> to a log file.
> 
> The issue I'm running into is this: the status of the sensors seems to
> always be "OK", even when their state changes. I can unplug the UPS from
> the wall and then I see this:
> 
> hw.sensors.upd0.indicator0=Off (Charging), OK
> hw.sensors.upd0.indicator1=On (Discharging), OK
> hw.sensors.upd0.indicator2=Off (ACPresent), OK
> hw.sensors.upd0.indicator3=On (BatteryPresent), OK
> hw.sensors.upd0.indicator4=Off (ShutdownImminent), OK
> hw.sensors.upd0.percent0=76.00% (RemainingCapacity), OK
> hw.sensors.upd0.percent1=100.00% (FullChargeCapacity), OK
> 
> We're not charging, we're discharging, AC power is not present, but none
> of the status indicators (the %s token) ever leaves the "OK" state. As I
> understand it, that lack of state change results in sensorsd doing
> nothing, even though the sensor's value (the %2 token, On/Off) changes.
> 
> Can anyone clue me in? I feel like I must be missing something silly and
> obvious here.

see here: http://undeadly.org/cgi?action=article&sid=20140320093943

``hw.sensors.upd0.indicator0:low=1:high=2:command=echo "who turned %2 \
  the lights?" | mail -s "power sensors" root''

the trick seems to be to specify "low=1:high=2". I suppose that works
for indicator2, too. 