Hi Charles,

I've added 3 more files to github.
https://github.com/mattwire/powercool-ups/blob/master/wireshark-UPSmart-startup.pcapng
- captures startup of UPSmart software and continues for about 5 minutes.
https://github.com/mattwire/powercool-ups/blob/master/wireshark-UPSmart-ups_off-on.pcapng
- UPSmart software is running, UPS is OFF. UPS is switched on and connects
to software.
https://github.com/mattwire/powercool-ups/blob/master/UPSmart_connected.png
- is a screenshot of the UPSmart software when connected (shows some values
from UPS).

Cheers,
Matthew

On 16 October 2016 at 22:49, [email protected] <[email protected]> wrote:

> Thanks for the log - apparently we always get valid (apart from
> 0.191312) but empty replies, not only for index 0x03, but also for the
> other queried index (0x0c).
> I've re-looked at the logs you posted on GitHub, but I don't see
> anything exotic going on there.
> Maybe we're missing some sort of handshaking or the like: can you post
> the whole captures/logs, right from when you plug the cable till the
> communication is established with UPSmart1.5?
>
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to