Citeren Kevin <bakd...@gmail.com>:

On the Smart-UPS 1000, all the instant commands do more or less what you would
expect. Looking at the timers using "upsc apc1500" I now see that:

 shutdown.
   load.off/load.off.delay both set the shutdown timer to 90, shuts down
     after 90 seconds

It looks like this is the minimum time the UPS allows. On almost every other HID PDC UPS we know of, the granularity is much finer than that (usually one to ten seconds). It is quite possible that your UPS was originally designed with a serial interface (possibly even a dumb one) and that the USB interface was added later on. So this may be all the underlying hardware supports.

   reboot sets the reboot timer to 90, sleeps after 90 seconds

Same here.

   return immediately switches to battery for a moment, sets both shutdown
     and startup to 90 seconds, sleeps after 90 seconds

That is very odd. You could try what happens if you change the 'ondelay' and 'offdelay' values in 'ups.conf'. Set offdelay to 1 second and ondelay to 100/200/400 seconds and run the shutdown.return command again (while monitoring the 'ups.timer.shutdown' and 'ups.timer.start' through upslog or upsc.

 test.panel and beeper commands also work as expected.

So you are right, it does seem to be working on this model. I don't know why I didn't see this when I was testing originally. Also I don't understand why the shutdown.return, which seems to be translated to "load.on.delay, load.off.delay"
is used in preference to the "shutdown.reboot" command.

According to the USB HID PDC specifications, the 'reboot n' command will kill the power immediately and return after 'n' seconds if power is present or will wait until the power returns if it wasn't. We prefer to have a little grace period, so that's why we do the two step approach of setting both the shutdown and (re)start timers.

By setting a restart timer longer than the shutdown timer, this effectively allows for a grace period until the UPS switches off. From then it behaves like a reboot command. You need this grace period if you want your system to hibernate instead of shutdown, since the Linux kernel doesn't allow calling hooks just before it powers off the system.

Apparently, due to the dreadful granularity of your UPS hardware timers the commands we send

    load.on.delay 30
    load.off.delay 20

are interpreted as setting both to 90 seconds. Worse, since the ups.timer.start elapses before the ups.timer.shutdown, this effectively puts the UPS to sleep.

On the CS 500 the load.off switches it off immediately, the load.off delay,
shutdown.return and shutdown.stayoff all switch to battery, and set the shutdown
timer to 20 seconds and then shuts down after that time. (Never restarts) The
beeper commands work, as does the shutdown.stop (sets the shutdown timer to -1)

This probably requires some remapping of variables. I'll see if I can find a solution for that.

Best regards, Arjen
--