Citeren Kevin <bakd...@gmail.com>:
[apc1500]
driver=usbhid-ups
port=auto
ondelay=200
offdelay=1
Yes.
After restarting the driver, and running shutdown.return, the timers
are set to
90 and 200. (the values of ups.delay.shutdown and ups.delay.start)
REBOOT:-1 SHUT:-1 START:-1
REBOOT:-1 SHUT:-1 START:-1
REBOOT:-1 SHUT:89 START:199
REBOOT:-1 SHUT:89 START:199
REBOOT:-1 SHUT:89 START:199
REBOOT:-1 SHUT:85 START:195
REBOOT:-1 SHUT:85 START:195
REBOOT:-1 SHUT:83 START:193
REBOOT:-1 SHUT:83 START:193
Using values of 250 and 1 gives:
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:-1 START:-1
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:-1 START:-1
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:89 START:249
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:89 START:249
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:89 START:249
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:86 START:246
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:86 START:246
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:84 START:244
delay.start:250 delay.shutdown:1 REBOOT:-1 SHUT:84 START:244
This looks actually pretty promising. It looks like the UPS sets a
lower limit to the shutdown timer. I would not be surprised if this is
caused by the value that is set in the
"UPS.Output.APCShutdownAfterDelay" HID path, which is currently set at
"90".
Could you try the attached patch on the nut-2.6.0 sources, compile it
again and run the driver again? If all is well, I expect the
'ups.delay.shutdown' to be a modifiable value after that. You could
try if setting it to "20" works. If the above is the case, I expect
there might be a mapping for the 'ups.delay.start' and
'ups.delay.reboot' as well.
If the variable seems to be modifiable, try to run 'shutdown.return'
again while logging as the above.
[...]
Ok, this makes sense now. The Smart-UPS 1000 apparently has some
variations on the 'standard'.
Well, it is not the only UPS (nor vendor) that has. These so called
vendor specific HID paths are allowed by the PDC standard. The problem
is that every vendor can choose what to put in them. So you can't
refer to a standard to find the meaning of them. This is not a problem
if we have full access to the specifications (like Eaton for
instance). But if the vendor is not willing to share them with us
(like APC for instance), we need to reverse engineer them. The latter
is a long, tedious process, which requires lots of help from owners of
these devices.
[...]
Isn't putting the UPS to sleep the desired behaviour here, so that
it wakes up again when power returns?
It should wakeup if the power returns after a power outage. But if the
power happens to return between the moment NUT sees the battery is low
(and initiates the shutdown sequence on the server) and the moment it
sends the shutdown signal to the UPS, it should rather cycle the
outlet to prevent what is known as a power race (see the documentation
for more information). You don't want to see the happening when you're
not around to restart your servers by hand.
[...]
On the CS 500, the shutdown timer is the only one that changes at all. The
reboot and start timers stay at zero (not -1) all the time.
I guess this means that the existing mapping might be wrong. I suspect
that it only has 'shutdown.reboot' and that the other mappings allow
setting the delay values. Note that in the CS 500 these are all vendor
specific HID paths. I'll deal with that, after we fully understand the
operation on the Smart-UPS 1000.
Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)
Index: drivers/apc-hid.c
===================================================================
--- drivers/apc-hid.c (revision 2844)
+++ drivers/apc-hid.c (working copy)
@@ -259,6 +259,7 @@
{ "ups.timer.reboot", 0, 0, "UPS.PowerSummary.DelayBeforeReboot", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},
/* used by APC SmartUPS RM */
{ "ups.delay.start", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.Output.DelayBeforeStartup", NULL, DEFAULT_ONDELAY, HU_FLAG_ABSENT, NULL},
+ { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.Output.APCShutdownAfterDelay", NULL, "%.0f", HU_FLAG_SEMI_STATIC, NULL },
{ "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.Output.DelayBeforeShutdown", NULL, DEFAULT_OFFDELAY, HU_FLAG_ABSENT, NULL},
{ "ups.timer.start", 0, 0, "UPS.Output.DelayBeforeStartup", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},
{ "ups.timer.shutdown", 0, 0, "UPS.Output.DelayBeforeShutdown", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser