I didn't have any issues with my old ES 725 and 2.6.4 for Windows
(7x64). I better make sure this new driver doesn't cause any issue for
its particular firmware. I can't look at it at the moment, but I'll try
and check it out today.
[email protected] wrote, On 9/10/2012 7:58 AM:
With Arnaud Quette's help, I have tried to fix the regression concerning the
APC Back UPS ES unit.
This regression is related to an issue in this UPS firmware. It cannot be
reverted to previous version because the current code fixes communication issue
with others UPS (which behave correctly, but are not very permissive).
So we (Arnaud and I) have decided to add a tweak (call it a hack if you wish)
for this APC UPS.
I need your help to test it on real hardware.
For UNIX users, you will need to compile NUT from revision 3723.
For Windows users, it is here : http://fbohe.free.fr/usbhid-ups.exe
For Denis: It is NOT the same binary you have already tested. You should use
this one now.
Please let us know if this new driver fix your issue.
Thanks to all reporter.
Regards,
Fred
--
Eaton Opensource Team - http://opensource.eaton.com
-----------------------------
-----------------------------