2012/9/11 Kris Jordan <[email protected]> > Arnaud Quette wrote, On 9/11/2012 1:39 AM: > >> >> 2012/9/11 Kris Jordan <[email protected] >> <mailto:nut.kj@**sagebrushnetworks.com <[email protected]>>> >> >> >> Seems to be working as far as reporting data w/o staleness. >> >> driver.version: 2.6.5-3691:3709M >> device.model: Back-UPS ES 725 >> ups.firmware: 802.n2.D >> ups.firmware.aux: n2 >> ups.productid: 0002 >> ups.vendorid: 051d >> >> >> is battery.charge reported on both units now? >> I'd also be interested in seeing a driver debug trace (-DDDDD, during a >> minute or so) and a complete upsc output, in compressed form please, to >> counter validate on my side. >> > > Both units? battery.charge was always reported on this ES725 (NUT > 2.6.4-2.6.5 and the new driver). > > Do you normally want upsd, upsmon, and upsc ran during the 1min debug > trace? Otherwise, here's the logs from the driver ran by itself for 1min. >
only the driver and upsd are required to get the data, so it's fine. you should also do a quick discharge (a couple of minutes) to see battery.charge decreasing well. > The only difference in the upsc output is the driver version. > > --- > > I'd like to thank you guys for the Windows pid and fsd fixes, 2.6.5 has > been working great. Thank you! > Fred will appreciate a lot, as usual. I'm forcing him to work on the Windows port for ~ 2 years (is a pure Linux fan!) So thanks again Fred for all your excellent work on the Windows port, and making NUT more widely available. I'm eager to see it finally entering the mainstream (we have still a lot of work before). cheers, Arnaud
_______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser