On 3/2/2017 9:57 AM, Charles Lepple wrote:
> On Dec 9, 2016, at 11:14 AM, Mike <the.li...@mgm51.com> wrote:
>>
>> On 12/8/2016 10:37 PM, Charles Lepple wrote:
>>> On Dec 8, 2016, at 1:34 PM, Mike wrote:
>>>> The result of the command
>>>>
>>>> upscmd -u user -p password myups load.off.delay 300
>>>>
>>>> is an immediate power-off, no delay.
>>>
>>> Hmm. Certainly possible that we are sending the delay to the wrong spot. 
>>> Hopefully the 300 is overriding the 20-second delay specified by 
>>> ups.delay.shutdown.
>>>
>>> You can try restarting just the driver with debug flags - something like 
>>> the following, depending on your distribution's paths:
>>>
>>> /lib/nut/usbhid-ups -a <name> -DDD 2>&1 | tee CPS-EC750G.log
>>>
>>> Let it run for 45-60 seconds and then stop it with Ctrl-C. Please compress 
>>> the log with gzip before posting.
>>>
>>
>> Hi Charles,
>>
>> Command, run on FreeBSD 11.0 (amd64)
>>
>> /usr/local/libexec/nut/usbhid-ups -a myups -DDD 2>&1 | tee CPS-EC750G.log
>>
>> 70 seconds of output attached.
>>
>>
>> Let me know if you need anything else.  This is an 'on the shelf' spare
>> UPS for me, so there is some flexibility in playing with it...
>>
>> thx.
> 
>    0.207421   Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 
> 0x15, Offset: 0, Size: 16, Value: -60
> 
> I haven't been able to find any information on what a "-60" would signify. 
> The value "-1" is used to cancel a timer, so maybe the internal timer is set 
> in minutes, and read back with a times-60 scale factor?
> 
> In that case, I would start by setting the "ups.delay.shutdown" and 
> "ups.delay.start" variables to multiples of 60 seconds, and try the shutdown 
> command without an argument. Using e.g. 120 and 180 will tell you whether the 
> start timer is measured from the beginning or end of the shutdown timer. 
> (Should be the latter, but no need to confuse the microcontroller any more 
> than necessary.) If that works, we can figure out why the load.off.delay 
> argument is being ignored.
> 
> You should be able to read the timer for UPS.Output.DelayBeforeShutdown via 
> the "ups.timer.shutdown" NUT variable.
> 
> Also, when testing, you may want to make sure that you have some sort of 
> dummy load on the UPS, such that "ups.load" is not zero. I am only vaguely 
> familiar with the MGE power saving features - so I am extrapolating to CPS 
> here - but I would not be surprised if the UPS ignored the shutdown delay if 
> it doesn't think there is a load attached.
> 


OK, I'll run your suggested changes and report back in a few days.

thanks.