On Wed, 17 May 2017, Dinow Hsieh wrote:

----------------------------------------------------------------------------------------
CC. Does a Ubuntu user with no xterm window open see the message as part of
the

==> The root and remote user(ssh-putty) get the broadcasting message all
from terminal-window

Since all the users have xterm access, there's no problem.

To get back to your original problem that the delayed shutdown of the UPS did not happen, and that the power outlets were not disconnected.

NUT 2.7.4 includes file .../scripts/systemd/nutshutdown . Does Ubunti
install this?

==> Yes. Ubuntu haved installed this as below contents

dinow-All-Series:/lib/systemd/system-shutdown$ cat nutshutdown
#!/bin/sh
/sbin/upsmon -K >/dev/null 2>&1 && /sbin/upsdrvctl shutdown

It would be interesting to know if this script is really executed on a system shutdown. Try adding line

   logger -t upsdrvctl "Calling for delated UPS shutdown"

The difficulty is that the NUT script is called very late when logging is probably no longer possible. For this reason, I don't use the NUT nutshutdown script. I prefer a systemd service unit

  # nut-delayed-ups-shutdown.service

  [Unit]
  Description=Initiate delayed UPS shutdown
  Before=umount.target
  DefaultDependencies=no

  [Service]
  Type=oneshot
  ExecStart=/usr/bin/logger -t upsdrvctl "nut-delayed-ups-shutdown.service
                                          calling upsdrvctl to shut down
                                          UPS unit"
  ExecStart=/usr/lib/ups/driver/upsdrvctl shutdown

  [Install]
  WantedBy=final.target

This service unit needs to be enabled with a command such as

  systemctl --system reenable
            /etc/systemd/system/nut-delayed-ups-shutdown.service

Roger