Unh - hunh, but it will run on the generator. If it didn't, I would go for the 
bad starter or motor, but it "seems" like the PF could be an issue??

Matt T
---- boB Gudgel <b...@midnitesolar.com> wrote: 
> Matt wrote:
> > Possibly a PF question, or maybe one for Magnum - boB,
> >
> > One of the guys at work is (almost) running a 3/4 hp sub pump with a Magna 
> > AE 48. Or rather, he isn't. According to him when he first fired it up, it 
> > operated the pump just fine. The next time he tried, though. he couldn't 
> > even get a buzz out of the starter. No workee.
> >   
> Sounds kind of like a "pump is broken or worn out" problem, doesn't it ?
> 
> If there is enough ac voltage applied to the pump, the it should do 
> ~something~, or lights should dim or some
> kind of sign should show itself, wouldn't you think ?   Otherwise, I 
> would suspect it might be a surge problem.
> 
> Is there a pilot light or something ?   Maybe a fuse blew or breaker 
> tripped somewhere ?   (when the pump went off?)
> 
> Doesn't sound like a PF problem though... However,  since you mention 
> it, with loads that are not a 1.0 power factor,
> at least for displacement power factor, when reactive phase shift is 
> involved, the inverter must be able to "sink" current
> from the stored reactive energy as well as be a source to the motor.   
> The Magnum does that just fine, as does any other
> decent inverter.
> 
> Maybe Tony, Eldon or Gary at Magnum has seen this before ?    425-353-8833
> 
> boB
> 
> 
> 
> 
> 
> 
> > The inverter runs all the other loads in the house fine, just not the pump. 
> > He can run the pump directly from a 7 kW generator with no issues.
> > So, do you think we're looking at a power factor deficit,(I think not), a 
> > motor starter problem or an inverter issue? I have to admit to being 
> > somewhat baffled by this one because it ran the pump once, but not after.
> >
> > Matt T
> >
> >
> > ---- boB Gudgel <b...@midnitesolar.com> wrote: 
> >   
> >> boB Gudgel wrote:
> >>
> >>  >>So, because of the different ways of specifying PF, it is always best 
> >> to think of Power Factor as being the ratio of real (in phase) power, or 
> >> VA to reactive power >>(VARS or "Volt Ampere Reactive").   That will 
> >> work in all cases.
> >>
> >>
> >> OOOps !   See, this can get confusing.   Reverse what I just said  Power 
> >> Factor... " Definition: The ratio of true power to apparent power"  as 
> >> David Brearley had just posted.  Otherwise, that calculation can give 
> >> you an answer that is GREATER than 1.0 and you don't want that !
> >>
> >> Had to eat some of my words.  I just wanted to point out that the phase 
> >> shift method was called DPF.   Didn't Ian Woodenden do an article on PF
> >> recently too ?  If not, he or someone probably should in one of the two 
> >> HP magazines.
> >>
> >> boB
> >>
> >>     
> >>> R. Walters wrote:
> >>>       
> >>>> Power factor expresses the time difference  between voltage peak and 
> >>>> current peak on each of their sine waves. If both current and voltage 
> >>>> waves are "in time", (their wave peaks match up) power factor is 1. 
> >>>> If one is ahead or behind the other, it's not. Think about an 
> >>>> electric motor: we hit it with a voltage wave, and a fraction of a 
> >>>> second later, it actually moves, and the current wave happens. There 
> >>>> is a little lag there. Resistive loads like lights have very little 
> >>>> lag, and big electric motors coming up to speed can have horrible PF.
> >>>>         
> >>> This definition of power factor only applies for linear loads with 
> >>> only inductance or capacitance (with resistance) and is called 
> >>> "Displacement Power Factor (DPF) and you will  see that on some power 
> >>> meters.
> >>>
> >>> For non-linear loads, like battery chargers or computer power supplies 
> >>> without PF Correction,  the current waveform (on an O-scope) looks 
> >>> nothing like a sine or cosine wave.   The current "spikes up" at the 
> >>> AC voltage peaks.  It actually *looks like* it might be in phase, BUT 
> >>> the current and the voltage do NOT look the same.  It's non-linear.  
> >>> Lower than 1.0 power factor for sure.
> >>>
> >>> For a grid tie inverter, resistive heater or any load that has a PF of 
> >>> 1.0,  the current and voltage waveform will both look exactly the same 
> >>> AND there will be no phase shift.   They are both linear and all 
> >>> current and voltage is in phase at every point in the AC cycle.
> >>>
> >>> So, because of the different ways of specifying PF, it is always best 
> >>> to think of Power Factor as being the ratio of real (in phase) power, 
> >>> or VA to reactive power (VARS or "Volt Ampere Reactive").   That will 
> >>> work in all cases. (Real Vs. Apparent power is the same thing).   
> >>> Apparent power is what you get when you multiply
> >>> your RMS meter's Voltage by the RMS current and is called VA Volt 
> >>> Amperes)   V x A will be the highest measured number, that is unless 
> >>> the PF = 1.0 in which
> >>> case both will measure the same.
> >>>
> >>> Some of that measured VA, or apparent power will be "in phase" and is 
> >>> the "real" or "true" power.  Some of that VA may be reactive, 
> >>> (inductive or capacitive that is) and is the "out of phase" portion.  
> >>> Capacitive and inductive reactance is ALWAYS 90 degrees out of phase 
> >>> in current and voltage.... It's just a matter of how MUCH of your 
> >>> power is 0 degrees phase shift and how MUCH of that VA is  + or - 90 
> >>> degrees out of phase.  If  ALL of the current is in phase with the 
> >>> voltage, then
> >>> the power factor is 1.0.   That is, if you lay them on top of each 
> >>> other, they will look the same on an oscilloscope if power factor = 1.0
> >>>
> >>> It can get way more complicated that this too, but that's basically 
> >>> it.  Feel free to add to this.
> >>>
> >>> boB
> >>>
> >>>
> >>>
> >>> power meters.
> >>>
> >>>
> >>>       
> >>>> There is much more to it, with reactance, "real" and "imaginary" 
> >>>> numbers?!, etc. but basically, we wrenches need to know that 
> >>>> everybody wants  Power factor to be close to 1.
> >>>> Obviously there isn't PF on DC, and it is my understanding that most 
> >>>> inverters can operate at most power factors. Not 100% sure, but I 
> >>>> think GT inverters would help not hurt the PF problem in most 
> >>>> situations.
> >>>>
> >>>> Correct me on any and all of this, Oh fellow wrenches,
> >>>>
> >>>> R. Walters
> >>>> Solarray.com
> >>>> NABCEP # 04170442
> >>>>
> >>>>         
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>       
> >>>> On Jul 30, 2009, at 9:19 AM, boB Gudgel wrote:
> >>>>
> >>>>         
> >>>>> Ron Young wrote:
> >>>>>           
> >>>>>> Ok, so all seem to be in agreement more or less. How do I break it 
> >>>>>> to British Columbia Hydro? :-|
> >>>>>>
> >>>>>> I think they must be misunderstanding what they are asking for but 
> >>>>>> the question is in the section for PV and on the same line as the 
> >>>>>> total output in Kwh of the PV. Power Factor %
> >>>>>>             
> >>>>> It was most likely just  a trick question.
> >>>>>
> >>>>> You're gonna fool them, though !   :)
> >>>>>
> >>>>>
> >>>>> boB
> >>>>>
> >>>>>
> >>>>>
> >>>>>           
> >>>>>> I'll contact them and see where this goes but I don't fully 
> >>>>>> understand what power factor is which will make it hard to argue my 
> >>>>>> case. My understanding is that it is the difference between what 
> >>>>>> the utility supplies to a residence vs. the actual loads being used 
> >>>>>> by that residence expressed as a percentage. I came across the 
> >>>>>> following course offering by SEI that discusses Power Factor with 
> >>>>>> reference to PV:
> >>>>>>
> >>>>>> POWER FACTOR AS IT RELATES TO SOLAR INSTALLATIONS Presented By: 
> >>>>>> Michael Smith of Alpine Management Systems  
> >>>>>> This session will deal with power factor: What is power factor?  
> >>>>>> What causes low power factor?  Why improve your power factor? This 
> >>>>>> session will explain the role of power factor correction as it 
> >>>>>> applies to solar installations. There are currently over 67,000 
> >>>>>> KVAR installations in 26 countries resulting in phenomenal energy 
> >>>>>> savings with a corresponding reduction in greenhouse gas emissions. 
> >>>>>> Session includes several KVAR installations and the resultant 
> >>>>>> savings. 
> >>>>>> http://www.solarenergy.org/workshops/docs/industry08_trainingdetails.pdf
> >>>>>>  
> >>>>>>
> >>>>>>
> >>>>>> Ron
> >>>>>>
> >>>>>> On 30-Jul-09, at 7:43 AM, Wind-sun.com wrote:
> >>>>>>
> >>>>>>             
> >>>>>>> There is no such thing as a power factor for DC or for panels.
> >>>>>>>  
> >>>>>>> ..................................................................................................
> >>>>>>>  
> >>>>>>>
> >>>>>>> Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
> >>>>>>> Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
> >>>>>>> ..................................................................................................
> >>>>>>>  
> >>>>>>>
> >>>>>>>
> >>>>>>>     ----- Original Message -----
> >>>>>>>     *From:* Ron Young <mailto:solarea...@solareagle.com>
> >>>>>>>     *To:* RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
> >>>>>>>     *Sent:* Wednesday, July 29, 2009 5:45 PM
> >>>>>>>     *Subject:* [RE-wrenches] Power Factor
> >>>>>>>
> >>>>>>>     Can anyone point me in the direction to find the power factor for
> >>>>>>>     Sanyo HIT N 205 panels? The utility is requesting it on a net
> >>>>>>>     metering interconnection application.      Ron Young
> >>>>>>>     earthRight Products - Solareagle.com
> >>>>>>>
> >>>>>>>
> >>>>>>>     
> >>>>>>> ------------------------------------------------------------------------
> >>>>>>>  
> >>>>>>>
> >>>>>>>
> >>>>>>>     _______________________________________________
> >>>>>>>     List sponsored by Home Power magazine
> >>>>>>>
> >>>>>>>     List Address: RE-wrenches@lists.re-wrenches.org 
> >>>>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
> >>>>>>>     <mailto:RE-wrenches@lists.re-wrenches.org>
> >>>>>>>
> >>>>>>>     Options & settings:
> >>>>>>>     
> >>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>>>>>>
> >>>>>>>     List-Archive: 
> >>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>>>>>>
> >>>>>>>     List rules & etiquette:
> >>>>>>>     www.re-wrenches.org/etiquette.htm
> >>>>>>>     <http://www.re-wrenches.org/etiquette.htm>
> >>>>>>>
> >>>>>>>     Check out participant bios:
> >>>>>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
> >>>>>>>
> >>>>>>> _______________________________________________
> >>>>>>> List sponsored by Home Power magazine
> >>>>>>>
> >>>>>>> List Address: RE-wrenches@lists.re-wrenches.org 
> >>>>>>> <mailto:RE-wrenches@lists.re-wrenches.org> 
> >>>>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
> >>>>>>>
> >>>>>>> Options & settings:
> >>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>>>>>>
> >>>>>>> List-Archive: 
> >>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>>>>>>
> >>>>>>> List rules & etiquette:
> >>>>>>> www.re-wrenches.org/etiquette.htm 
> >>>>>>> <http://www.re-wrenches.org/etiquette.htm>
> >>>>>>>
> >>>>>>> Check out participant bios:
> >>>>>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
> >>>>>>>
> >>>>>>>               
> >>>>>> ------------------------------------------------------------------------
> >>>>>>  
> >>>>>>
> >>>>>>
> >>>>>> _______________________________________________
> >>>>>> List sponsored by Home Power magazine
> >>>>>>
> >>>>>> List Address: RE-wrenches@lists.re-wrenches.org 
> >>>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
> >>>>>>
> >>>>>> Options & settings:
> >>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>>>>>
> >>>>>> List-Archive: 
> >>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>>>>>
> >>>>>> List rules & etiquette:
> >>>>>> www.re-wrenches.org/etiquette.htm
> >>>>>>
> >>>>>> Check out participant bios:
> >>>>>> www.members.re-wrenches.org
> >>>>>>
> >>>>>>   
> >>>>>>             
> >>>>> _______________________________________________
> >>>>> List sponsored by Home Power magazine
> >>>>>
> >>>>> List Address: RE-wrenches@lists.re-wrenches.org 
> >>>>> <mailto:RE-wrenches@lists.re-wrenches.org>
> >>>>>
> >>>>> Options & settings:
> >>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>>>>
> >>>>> List-Archive: 
> >>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>>>>
> >>>>> List rules & etiquette:
> >>>>> www.re-wrenches.org/etiquette.htm
> >>>>>
> >>>>> Check out participant bios:
> >>>>> www.members.re-wrenches.org
> >>>>>
> >>>>>           
> >>>> ------------------------------------------------------------------------
> >>>>
> >>>> _______________________________________________
> >>>> List sponsored by Home Power magazine
> >>>>
> >>>> List Address: RE-wrenches@lists.re-wrenches.org
> >>>>
> >>>> Options & settings:
> >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>>>
> >>>> List-Archive: 
> >>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>>>
> >>>> List rules & etiquette:
> >>>> www.re-wrenches.org/etiquette.htm
> >>>>
> >>>> Check out participant bios:
> >>>> www.members.re-wrenches.org
> >>>>
> >>>>   
> >>>>         
> >>> _______________________________________________
> >>> List sponsored by Home Power magazine
> >>>
> >>> List Address: RE-wrenches@lists.re-wrenches.org
> >>>
> >>> Options & settings:
> >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>>
> >>> List-Archive: 
> >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>>
> >>> List rules & etiquette:
> >>> www.re-wrenches.org/etiquette.htm
> >>>
> >>> Check out participant bios:
> >>> www.members.re-wrenches.org
> >>>
> >>>
> >>>       
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches@lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive: 
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >>     
> >
> >
> >   
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to