HI Steve,

Is there a logic to the change  between < 75 and 76> regarding loss of temp 
comp for Sell RE?

thanks,

jay

peltz power
On Apr 5, 2010, at 2:11 PM, Steve Higgins wrote:

> Sell RE and Refloat are not Temp Compensated,
> Absorb, Float Voltages and EQ are temp Compensated.
>  
> Older Grid tie inverters using firmware revision 75 utilized temperature 
> compensated voltage with the Sell RE, but new versions such as 76 and above 
> don’t.
>  
> “2)What is the difference between refloat and rebulk?”
>  
> For the purpose of the GT units, it’s really the same.  Just when Refloat, is 
> triggered it’s basically going into a Re-bulk mode.
>  
> Steve Higgins.